Catalyst 6509 Ethernet Card Power Failures
Sep 10th, 2007
Over the last couple of months we have experienced about 5 Ethernet card failures, with another three happening late last year. The problem results in all Cisco IP phones on the card losing power (the phones are powered over Ethernet) and the PCs attached to the phones becoming disconnected from the network. More worryingly the most recent occurrence resulted in two components (capacitors??) on the card burning out when we tried reseating the card in the chassis.
In all but one of the occasions we have had to replace the cards as neither a hw-module reset or a physical reseating do not clear the problem
The only indication we get that there is a problem is when you examine the Show Logs:
%PM_SCP-SP-2-LCP_FW_ERR_INFORM: Module 3 is experiencing the following error: Inline Power Module - PS volatage bad
All our User Access Switches are Cisco WS-6509-E chassis, with 2 Supervisor Engine 32 cards. All of the installed Ethernet modules used are 48-port 10/100/1000 RJ45 EtherModule "WS-X6148A-GE-45AF". And we are currently running 12.2(18)SXF4 IOS (s3223-ipbasek9-mz.122-18.SXF4)
The fault has proven to be very random, on every occasion the fault has occurred in different module slots on different chassis located in different parts of the building.
I would be interested if anyone could comment on our problem as we are struggling to ascertain what the root cause is and we are becoming more and more concerned due to the frequency that this problem is happening.
Overall Rating: 3 (1 ratings)
JORGE RODRIGUEZ Mon, 09/10/2007 - 18:20
  • Green, 3000 points or more
Martin, have you opened a TAC case on this issue.. I would definatetly address this with TAC to rule out any hardware recalls.
Jorge
dany.datacraft Fri, 06/12/2009 - 03:16
did you resolve this problem? We had the same problem with the following modules and IOS:
System image file is "disk0:s72033-ipservicesk9-mz.122-18.SXF7.bin"
NAME: "1", DESCR: "WS-X6548-GE-TX SFM-capable 48 port 10/100/1000mb RJ45 Rev. 10
.1"
PID: WS-X6548-GE-TX , VID: , SN: SALXXXXXEXA
NAME: "sub-module of 1", DESCR: "WS-F6K-GE48-AF IEEE Voice Daughter Card Rev. 1.
2"
PID: WS-F6K-GE48-AF , VID: , SN: SALXXXXXEGZ
Jun 12 16:30:45: %PM_SCP-SP-2-LCP_FW_ERR_INFORM: Module 1 is experiencing the fo
Jun 12 16:30:50: %PM_SCP-SP-2-LCP_FW_ERR_INFORM: Module 1 is experiencing the fo
martinward1234 Mon, 06/15/2009 - 01:07
Hi Danny,
If my memory serves me correctly, this issue was due to the 6509 Chassis not being grounded properly.
You must ensure that you ground/earth the chassis correctly.
Hope this helps,
Martin
dany.datacraft Tue, 06/16/2009 - 19:57
Hi Martin,
Thanks for the pointers. Did you also remember such problem causes NIC cards that are connected to the line card to be damaged? Our customer has 3 X31 IBM notebook damaged (the NIC cards) when connected to the line card. They mentioned that they observed smoke coming out of the NIC card.
martinward1234 Wed, 06/17/2009 - 00:34
I don't recall any host devices becoming damaged, however on one occasion a faulty line card did "go bang" as it was being removed and was burnt a little in the process.
Leo Laohoo Fri, 06/12/2009 - 18:40
  • Hall of Fame,
    The Hall of Fame designation is a lifetime achievement award based on significant overall achievements in the community.
  • Cisco Designated VIP,
    2017 LAN, Wireless
I recommend you contact TAC to get your card RMA-ed. If this issue happens regularly, there could be a hardware fault with the chassis.
Hope this helps.