6500 fantray cooling configuration
Oct 22nd, 2007
I have installed a new WS-6724-SFP line card in a WS-C6509 chassis and it will not come up due to the following error code:
%SYS-2-FAN_INSUFFICIENTCOOLING:Module 7 cannot be adequately cooled
HAVC6502> (enable) sh environment cooling
Chassis per slot cooling capacity : 37 cfm
Fan tray(s) cooling capacity :
Fan Model Ver Cooling Ambient FanStatus
capacity temp
1 WS-C6K-9SLOT-FAN 1 340 cfm - ok
Slot cooling requirement :
Slot CardType Cooling
1 WS-X6K-SUP2-2GE 30 cfm
3 WS-X6408A-GBIC 30 cfm
4 WS-X6516-GBIC 30 cfm
5 WS-X6516-GBIC 30 cfm
6 WS-X6516A-GBIC 30 cfm
7 Unknown 70 cfm
8 WS-X6148-RJ-45 30 cfm
9 WS-X6324-100FX-MM 30 cfm
It appears that the chassis only provides 37cfm per slot for cooling, regardless of the line card demands. There is ample cooling available, but the maximum of 37cfm is a hard set restriction. Can this be configured to be increased to the 70 required by the line card? Or does this require an enhanced 6500 chassis?
rgds
Phil
Overall Rating: 4 (1 ratings)
jerry.bonner Mon, 10/22/2007 - 14:13
Phil,
Ultimately your problem is that the 6700 series blades are only compatible with a sup720. More than that, a sup720 requires a high speed fan tray which is probably what the slot cards check for first.
You need a new sup and fan tray, but not necessarily an e-series chassis. CFM is not configurable to my knowledge.
Hope that helps.