Do not use ethernet cable. Please use only proper T1 cable, 100 Ohm impedence, with the correct pinout ans pair twisting, as per manual.



Rob Huffman Wed, 05/07/2008 - 04:19
User Badges:
  • Super Blue, 32500 points or more
  • Hall of Fame,

    Founding Member

  • Cisco Designated VIP,

    2017 IP Telephony, Unified Communications

Hi Jerry,


Hope all is well :) Just wanted to add a note to the good info from my friend Paolo. This doc has some good references for the RJ48 Pinouts;


http://www.cisco.com/en/US/docs/routers/access/hardware/notes/marcabl.html#wp38057


Hope this helps!

Rob

Zin.Karzazi Wed, 05/07/2008 - 04:26
User Badges:
  • Silver, 250 points or more

We use RJ45 for our PRIs without any Problems. If you just need a short Cable to connect to your E1, RJ45 would be fine.

rich_harris Wed, 05/07/2008 - 05:19
User Badges:

Sometimes the telco terminating box will only accept the keyed RJ48C but in most cases we use RJ45 straight through with no problems.

paolo bevilacqua Wed, 05/07/2008 - 05:55
User Badges:
  • Super Gold, 25000 points or more
  • Hall of Fame,

    Founding Member

Rj48C twisting is different from ethernet, hence no protection from interference, and bigger radiated interfences.


All is good until strange eproblems happens, at that time you will replace the cable anyway, so why don't do things rights since the beginning.

rich_harris Thu, 05/08/2008 - 01:12
User Badges:

Agreed, I'm all for doing things properly and if the telco kit does have the proper keyed socket you are safe.


Rich