Power Supply OID 6500 Running CatOS
May 28th, 2008
Hi, does anyone have the OID so that I can monitor the online status of my 6500 Chassis Power Supplies. I'd like to be able to see if one of the power supplies is /becomes faulty
GRAEME DANIELSON Thu, 05/29/2008 - 01:10
Walk this from the envmon mib .1.3.6.1.4.1.9.9.13.1.5.1.3 and make sure they're all 1
The current state of the power supply(s)
CISCO-ENVMON-MIB::ciscoEnvMonSupplyState
Valid values are:
normal(1): the environment is good, such as low
temperature.
warning(2): the environment is bad, such as temperature
above normal operation range but not too
high.
critical(3): the environment is very bad, such as
temperature much higher than normal
operation limit.
shutdown(4): the environment is the worst, the system
should be shutdown immediately.
notPresent(5): the environmental monitor is not present,
such as temperature sensors do not exist.
notFunctioning(6): the environmental monitor does not
function properly, such as a temperature
sensor generates a abnormal data like
1000 C.
The envmon mib can be used to monitor just about all environmentals if the device supports it e.g. temperature, fan etc. not just on 6500s
GRAEME DANIELSON Thu, 05/29/2008 - 01:13
Valid values are:
temperature.
high.
operation limit.
1000 C.
GRAEME DANIELSON Thu, 05/29/2008 - 01:38
Sorry, missed the CatOS bit. Not entirely sure but these in the stackMIB look like the ones you're after (can't confirm I don't have access to any live CatOS any more)
chassisPs1Status .1.3.6.1.4.1.9.5.1.2.4
chassisPs2Status .1.3.6.1.4.1.9.5.1.2.7