SNMP configs....

Unanswered Question

Hi all,

Kindly let me know what all SNMP commands are useful for typical 6500 series swicth used in datacenter. I wish to configure this switch for sendinig SNMP alerts in case of 'module down' or 'module power down', but I do not want to monitor the link down/up of each and every switchport (just want to monitor modules). Kindly let me know how can it be done?

thanks and regards,

--Gaurav

I have this problem too.
0 votes
  • 1
  • 2
  • 3
  • 4
  • 5
Overall Rating: 4 (1 ratings)
Loading.
adamclarkuk_2 Sat, 02/28/2009 - 00:52

Try these

snmp-server enable traps snmp authentication coldstart warmstart

snmp-server enable traps chassis

snmp-server enable traps module

snmp-server enable traps event-manager

snmp-server enable traps hsrp

snmp-server enable traps rtr

snmp-server enable traps entity

snmp-server enable traps envmon fan shutdown supply temperature status

snmp-server host xxx.xxx.xxx.xxx

snmp-server host xxx.xxx.xxx.xxx

These cover you module up and down

Leo Laohoo Sun, 03/15/2009 - 14:49

May I be allowed to add the following:

snmp-server enable traps cpu

snmp-server enable traps transceiver

snmp-server enable traps power-ethernet

To disable logging of links going down/up, go to each interface and configure the following:

no logging event link-status

no snmp trap link-status