Dear friends,

Does anyone know of the cause of this message "PS2 capacity is limited to 2940.00"?. I am seeing that the power supply LED's are green but i am still getting this message.

The switch in question is WS-C6509 (not the E chassis) running IOS 12.2(33)SXH3.

H-6509-Dist1#sh power

system power redundancy mode = redundant

system power total = 3780.00 Watts (90.00 Amps @ 42V)

system power used = 2003.40 Watts (47.70 Amps @ 42V)

system power available = 1776.60 Watts (42.30 Amps @ 42V)

Power-Capacity PS-Fan Output Oper

PS Type Watts A @42V Status Status State

---- ------------------ ------- ------ ------ ------ -----

1 WS-CAC-6000W 5771.64 137.42 OK OK on

2 WS-CAC-6000W 5771.64 137.42 OK OK on

Note: PS2 capacity is limited to 2940.00 Watts (70.00 Amps @ 42V)

when PS1 is not present

Pwr-Requested Pwr-Allocated Admin Oper

Slot Card-Type Watts A @42V Watts A @42V State State

---- ------------------ ------- ------ ------- ------ ----- -----

1 WS-X6704-10GE 295.26 7.03 295.26 7.03 on on

2 WS-X6708-10GE 444.36 10.58 444.36 10.58 on on

3 WS-X6708-10GE 444.36 10.58 444.36 10.58 on on

5 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on

6 (Redundant Sup) - - 282.24 6.72 - -

9 WS-X6748-SFP 254.94 6.07 254.94 6.07 on on

Thanks a lot

Gautam

1 Accepted Solution

Accepted Solutions

Guatam - check this out:

http://www.cisco.com/en/US/docs/switches/lan/catalyst6500/hardware/Chassis_Installation/Cat6500/0apwsply.html#wp1071292

This gives you the details you need. The 6000W PS is limited to 4000W in the 6509 non-e chassis.

To address the note, you can find that info on the same page, at the foot of table A-27:

http://www.cisco.com/en/US/docs/switches/lan/catalyst6500/hardware/Chassis_Installation/Cat6500/0apwsply.html#wp1030075

"When running redundant 4000 W, 6000 W, or 8700 W power supplies in Catalyst 6506 and Catalyst 6509 non-E series systems, if you remove the power supply in bay 1, the total system power will be reduced to 2940 W (70 A at 42 VDC) after 180 seconds (3 minutes). You can avoid this reduction in the total system power by leaving the power supply in bay 1, even in a powered down state."

HTH,

Geoff

View solution in original post

4 Replies 4

glen.grant
VIP Alumni
VIP Alumni

You are probably running 120 volt power versus 240 volt which would give you full wattage .

Dear Glen,

We are in Qatar and running 240V. Is this a limitation of the AC power being supplied or the power supply itself?

If its power supply itself, then what is the suggested step in this case?

Thanks a lot

Gautam

Guatam - check this out:

http://www.cisco.com/en/US/docs/switches/lan/catalyst6500/hardware/Chassis_Installation/Cat6500/0apwsply.html#wp1071292

This gives you the details you need. The 6000W PS is limited to 4000W in the 6509 non-e chassis.

To address the note, you can find that info on the same page, at the foot of table A-27:

http://www.cisco.com/en/US/docs/switches/lan/catalyst6500/hardware/Chassis_Installation/Cat6500/0apwsply.html#wp1030075

"When running redundant 4000 W, 6000 W, or 8700 W power supplies in Catalyst 6506 and Catalyst 6509 non-E series systems, if you remove the power supply in bay 1, the total system power will be reduced to 2940 W (70 A at 42 VDC) after 180 seconds (3 minutes). You can avoid this reduction in the total system power by leaving the power supply in bay 1, even in a powered down state."

HTH,

Geoff

Thanks a lot Geoff for your wonderful answer which was very helpful

Getting Started

Find answers to your questions by entering keywords or phrases in the Search bar above. New here? Use these resources to familiarize yourself with the community:

Review Cisco Networking products for a $25 gift card