JRM service is not coming up..plse find the atached error message.
regrds
Vaibhav
Correct Answer by Joe Clarke about 7 years 4 months ago
Check to make sure 172.28.100.10 is still the correct IP address for this server. If not, update the entries in gatekeeper.cfg, then restart Daemon Manager.
Overall Rating: 5 (1 ratings)
Joe Clarke Thu, 08/20/2009 - 21:53
You did not post the jrm.log. I'm also not sure why you're trying to reinitialize the cmf database. At this point, that seems to be overkill, and may not fix the underlying problem.
vaibhav-g Thu, 08/20/2009 - 22:20
Hi Clark
we will soon provide you the JRM.logs
Vaibhav
vaibhav-g Fri, 08/21/2009 - 06:58
Hi Clark
I have alredy attached the JRM.log file
plse help me..
Vaibhav
Joe Clarke Fri, 08/21/2009 - 07:05
Jrm appears to be working just fine. Was the hostname on this server changed? Post the output of the command:
pdreg -l CTMJrmServer
And the NMSROOT\lib\classpath\md.properties file. Additionally, it appears Daemon Manager has been up since 8/6. Simply restarting may get things back in sync.
Joe Clarke Sun, 08/23/2009 - 21:41
This looks good assuming the hostname of the server is ciscolms. Is this problem still occurring? Have you tried restarting Daemon Manager? It could simply be a timing issue.
vaibhav-g Mon, 08/24/2009 - 00:03
Hi Clark
we have tried to restart the daemon manger service but still we are facing same issue.Plse find the attached file for hostname.
Vaibhav
Joe Clarke Mon, 08/24/2009 - 07:08
Post the output of the DOS SET command, and the NMSROOT/MDC/tomcat/logs/stdout.log.
Joe Clarke Tue, 08/25/2009 - 08:23
Post screenshots of the Services control panel showing all of the CiscoWorks services. Additionally, the pdshow appears truncated. Run:
pdshow > pdshow.txt
Then post the pdshow.txt.
Joe Clarke Wed, 08/26/2009 - 07:54
The services look okay, but the pdshow is still truncated. Did you run:
pdshow > pdshow.txt
That will capture the entire output.
Joe Clarke Wed, 08/26/2009 - 23:03
The RmeGatekeeper is down. Post the output of netstat -a -n -o -b from the server as well as the RmeGatekeeper.log.
Joe Clarke Thu, 08/27/2009 - 08:50
Your netstat output is truncated. Run this command:
netstat -a -n -o -b > netstat.txt
Then post the netstat.txt. One of the ports required by RmeGatekeeper is in use by another process.
Joe Clarke Thu, 08/27/2009 - 22:08
There was something bound to one of the RmeGatekeeper ports, but all the ports appear to be free now. You should be able to restart the RmeGatekeeper, and have it stay up. Try running:
pdexec RmeGatekeeper
Then verify it stays in a running state. If so, restart Daemon Manager, and that should allow all of the daemons to resync.
vaibhav-g Fri, 08/28/2009 - 00:09
Hi Clark
Tried to start the RmeGatekeeper but it does not stay up and get down in few minutes.
Vaibhav
Correct Answer
Joe Clarke Mon, 08/31/2009 - 08:37
vaibhav-g Mon, 08/31/2009 - 09:18
Hi Clark
thanks for your response, i will check the same and upadte you,
If i found different Ip than i need to replace that IP address in Gatekeeper.cfg file, Plse confirm
Vaibhav
vaibhav-g Wed, 09/02/2009 - 07:24
Hi Clark
Thanks a ton..yes their was a IP conflict issue.Now issue was resolved by replacing the same..
Thanks again