I have question about power redundancy mode specially restricted power mode.

Sanghee Han
Level 1
Level 1

hi all,

I have a question about power redundancy mode in cat6500-AC3000watt

cat6500#sh power
system power redundancy mode = restricted power mode

i know about combined mode and redundant mode,

but unfamiliar with restricted power mode

is there anyone knows about this?

1 Accepted Solution

Accepted Solutions

Hi Sanghee Han,

So “show power” is actually given you

“system power redundancy mode = redundant” and

restricted shown in the “show env” cooling section for fan-tray 1:

---

fan-tray 1:
   fan-tray 1 type: WS-C6509-E-FAN
   fan-tray 1 mode: Restricted-power
   fan-tray 1 fan-fail: OK

---

The "restricted" power is the default for the E-chassis.
The WS-C6506/9-E-FAN has two modes - Restricted-Power and High Power.
Restricted-power mode means that the Fan-Tray operates at lower rotating speed 
and it is enough for system’s per slots cooling (to keep temperature under thr).
 
Usually the fans in fan-tray will speed up if a fan has failed in the fan-tray or 
if there are a linecards in the chassis that requires higher cooling.
For example, in case of WS-X6708-10G modules in some slots, 
the chassis/fans will be running high-power mode.
 
The “show env [cooling]” will give you this info, 
with details on required fans CFM capacity for chassis and for each module.
 
Like in you case with 4 modules:
1    7600-SIP-400        265.02  6.31   265.02  6.31  on    on
2    WS-X6748-GE-TX      325.50  7.75   325.50  7.75  on    on
5    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
6    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
 
The cooling at 70 cfm fans rotating looks enough for setup, 
so fan-tray 1 is in default mode Restricted-power:
----------------- show environment ------------------
…  
fan-tray 1:
  fan-tray 1 type: WS-C6509-E-FAN
  fan-tray 1 mode: Restricted-power
  fan-tray 1 fan-fail: OK
… snip…
chassis per slot cooling capacity: 70 cfm ambient temperature: < 55C
  module 1 cooling requirement: 35 cfm
  module 2 cooling requirement: 70 cfm
  module 5 cooling requirement: 35 cfm
  module 6 cooling requirement: 35 cfm
 
And for example in case of the chassis w two WS-X6708-10G-3C in slots 1 and 2 
the fans will be running at high speed and
the output would looks similar to follow:
 
#show env cool    
fan-tray 1:
 fan-tray 1 type: WS-C6509-E-FAN
 fan-tray 1 mode: high-power <--
 fan-tray 1 fan-fail: OK
chassis per slot cooling capacity: 94 cfm ambient temperature: < 55C
 module 1 cooling requirement: 84 cfm  <<<<<
 module 2 cooling requirement: 84 cfm  <<<<<
 module 3 cooling requirement: 70 cfm
 module 4 cooling requirement: 70 cfm
 module 5 cooling requirement: 35 cfm
 module 6 cooling requirement: 35 cfm
 module 7 cooling requirement: 70 cfm
 module 8 cooling requirement: 70 cfm
 
 
 
Thanks,
Sergey

View solution in original post

6 Replies 6

Sergei Vasilenko
Cisco Employee
Cisco Employee

Hello!

Is it a newer C6500-E series chassis ?

If yes, than "restricted" power could be the default for E-series, but normally it is

shown in show end, show power for FAN-tray part only, like "fan-tray 1 mode: Restricted-power".

Thanks,

Sergey





Thanks for your answer.

then, i wonder how the cat65k-E operates power resource in restricted-power mode.

do you know about this?

Hi,

Could you post the full output of "show power", "show env" and clarify which ios version is it.


Thanks,
Sergey

hi Sergey

i post the relative log...show power/env/ver/module. 

------------------ show power ------------------


system power redundancy mode = redundant
system power total =     2771.16 Watts (65.98 Amps @ 42V)
system power used =      1305.36 Watts (31.08 Amps @ 42V)
system power available = 1465.80 Watts (34.90 Amps @ 42V)
                        Power-Capacity PS-Fan Output Oper
PS   Type               Watts   A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1    WS-CAC-3000W       2771.16 65.98  OK     OK     on
2    WS-CAC-3000W       2771.16 65.98  OK     OK     on
                        Pwr-Allocated  Oper
Fan  Type               Watts   A @42V State
---- ------------------ ------- ------ -----
1    WS-C6509-E-FAN      150.36  3.58  OK
                        Pwr-Requested  Pwr-Allocated  Admin Oper
Slot Card-Type          Watts   A @42V Watts   A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1    7600-SIP-400        265.02  6.31   265.02  6.31  on    on
2    WS-X6748-GE-TX      325.50  7.75   325.50  7.75  on    on
5    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
6    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
system auxiliary power mode = off
system auxiliary power redundancy operationally = non-redundant
system primary connector power limit =   10920.00 Watts (260.00 Amps @ 42V)
system auxiliary connector power limit = 10500.00 Watts (250.00 Amps @ 42V)
system primary power used =              1305.36 Watts (31.08 Amps @ 42V)
system auxiliary power used =            0 Watt

------------------ show environment ------------------


environmental alarms:
  no alarms

backplane:
  operating clock count: 2
  operating VTT count: 3
 
fan-tray 1:
  fan-tray 1 type: WS-C6509-E-FAN
  fan-tray 1 mode: Restricted-power
  fan-tray 1 fan-fail: OK
VTT 1:
  VTT 1 OK: OK
  VTT 1 outlet temperature: 35C
VTT 2:
  VTT 2 OK: OK
  VTT 2 outlet temperature: 37C
VTT 3:
  VTT 3 OK: OK
  VTT 3 outlet temperature: 35C
clock 1:
  clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
  clock 2 OK: OK, clock 2 clock-inuse: not-in-use
power-supply 1:
  power-supply 1 fan-fail: OK
  power-supply 1 power-input: AC high
  power-supply 1 power-output-mode: high
  power-supply 1 power-output-fail: OK
power-supply 2:
  power-supply 2 fan-fail: OK
  power-supply 2 power-input: AC high
  power-supply 2 power-output-mode: high
  power-supply 2 power-output-fail: OK
module 1:
  module 1 power-output-fail: OK
  module 1 outlet temperature: 46C
  module 1 inlet temperature: 38C
  module 1 device-1 temperature: 44C
  module 1 device-2 temperature: 43C
module 2:
  module 2 power-output-fail: OK
  module 2 outlet temperature: 49C
  module 2 inlet temperature: 33C
module 5:
  module 5 power-output-fail: OK
  module 5 outlet temperature: 37C
  module 5 inlet temperature: 32C
  module 5 device-1 temperature: 42C
  module 5 device-2 temperature: 42C
  module 5 asic-1 temperature: 31C
  module 5 asic-2 temperature: 31C
  module 5 asic-3 temperature: 31C
  module 5 asic-4 temperature: 32C
  module 5 asic-5 temperature: 31C
  module 5 asic-6 temperature: 32C
  module 5 RP outlet temperature: 34C
  module 5 RP inlet temperature: 35C
  module 5 EARL outlet temperature: 43C
  module 5 EARL inlet temperature: 34C
module 6:
  module 6 power-output-fail: OK
  module 6 outlet temperature: 37C
  module 6 inlet temperature: 32C
  module 6 device-1 temperature: 41C
  module 6 device-2 temperature: 41C
  module 6 asic-1 temperature: 31C
  module 6 asic-2 temperature: 31C
  module 6 asic-3 temperature: 31C
  module 6 asic-4 temperature: 30C
  module 6 asic-5 temperature: 31C
  module 6 asic-6 temperature: 31C
  module 6 RP outlet temperature: 34C
  module 6 RP inlet temperature: 35C
  module 6 EARL outlet temperature: 40C
  module 6 EARL inlet temperature: 34C
  SPA-4XT3/E3[1/0] temperature sensor 0, reading: 39C
  SPA-4XT3/E3[1/0] temperature sensor 1, reading: 38C
  SPA-4XT3/E3[1/0] temperature sensor 2, reading: 40C
  SPA-4XT3/E3[1/0] temperature sensor 3, reading: 41C
  SPA-4XT3/E3[1/0] temperature sensor 4, reading: 44C
  SPA-4XT3/E3[1/0] nominal: 3.300V, reading: 3.290V
  SPA-4XT3/E3[1/0] nominal: 2.500V, reading: 2.510V
  SPA-4XT3/E3[1/0] nominal: 1.800V, reading: 1.796V
  SPA-4XT3/E3[1/0] nominal: 1.500V, reading: 1.499V
  SPA-8XCHT1/E1[1/1] temperature sensor 0, reading: 40C
  SPA-8XCHT1/E1[1/1] temperature sensor 1, reading: 41C
  SPA-8XCHT1/E1[1/1] temperature sensor 2, reading: 38C
  SPA-8XCHT1/E1[1/1] temperature sensor 3, reading: 35C
  SPA-8XCHT1/E1[1/1] temperature sensor 4, reading: 45C
  SPA-8XCHT1/E1[1/1] nominal: 3.300V, reading: 3.320V
  SPA-8XCHT1/E1[1/1] nominal: 2.500V, reading: 2.516V
  SPA-8XCHT1/E1[1/1] nominal: 1.800V, reading: 1.807V
  SPA-8XCHT1/E1[1/1] nominal: 1.500V, reading: 1.509V


chassis connector rating: 1302.00 Watts (31.00 Amps @ 42V)
chassis auxiliary connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 1
  module 1 connector rating: 1512.00 Watts (36.00 Amps @ 42V)
  module 1 power consumption:  265.02 Watts ( 6.31 Amps @ 42V)
module 2
  module 2 connector rating: 2016.00 Watts (48.00 Amps @ 42V)
  module 2 power consumption:  325.50 Watts ( 7.75 Amps @ 42V)
module 5
  module 5 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
  module 5 power consumption:  282.24 Watts ( 6.72 Amps @ 42V)
module 6
  module 6 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
  module 6 power consumption:  282.24 Watts ( 6.72 Amps @ 42V)

chassis per slot cooling capacity: 70 cfm
ambient temperature: < 55C
  module 1 cooling requirement: 35 cfm
  module 2 cooling requirement: 70 cfm
  module 5 cooling requirement: 35 cfm
  module 6 cooling requirement: 35 cfm

------------------ show version ------------------

Cisco IOS Software, s72033_rp Software (s72033_rp-ADVIPSERVICESK9_WAN-M), Version 12.2(33)SXI3, RELEASE SOFTWARE (fc2)
Technical Support: http://www.cisco.com/techsupport
Copyright (c) 1986-2009 by Cisco Systems, Inc.
Compiled Tue 27-Oct-09 11:11 by prod_rel_team

ROM: System Bootstrap, Version 12.2(17r)SX5, RELEASE SOFTWARE (fc1)

PE007 uptime is 9 minutes
Uptime for this control processor is 9 minutes
Time since PE007 switched to active is 8 minutes
System returned to ROM by reload at 10:45:12 UTC Mon Jan 4 2010 (SP by reload)
System image file is "sup-bootflash:s72033-advipservicesk9_wan-mz.122-33.SXI3.bin"
Last reload reason: Reload Command

This product contains cryptographic features and is subject to United
States and local country laws governing import, export, transfer and
use. Delivery of Cisco cryptographic products does not imply
third-party authority to import, export, distribute or use encryption.
Importers, exporters, distributors and users are responsible for
compliance with U.S. and local country laws. By using this product you
agree to comply with applicable laws and regulations. If you are unable
to comply with U.S. and local laws, return this product immediately.

A summary of U.S. laws governing Cisco cryptographic products may be found at:
http://www.cisco.com/wwl/export/crypto/tool/stqrg.html

If you require further assistance please contact us by sending email to
export@cisco.com.

cisco WS-C6509-E (R7000) processor (revision 1.5) with 458720K/65536K bytes of memory.
Processor board ID SMC1346005X
SR71000 CPU at 600Mhz, Implementation 0x504, Rev 1.2, 512KB L2 Cache
Last reset from s/w reset
1 SIP-400 controller (4 Serial)(8 E1).
1 Virtual Ethernet interface
52 Gigabit Ethernet interfaces
7 Serial interfaces
8 Channelized E1 ports
1917K bytes of non-volatile configuration memory.
8192K bytes of packet buffer memory.

65536K bytes of Flash internal SIMM (Sector size 512K).
Configuration register is 0x2102

------------------ show module ------------------


Mod Ports Card Type                              Model              Serial No.
--- ----- -------------------------------------- ------------------ -----------
  1    0  4-subslot SPA Interface Processor-400  7600-SIP-400       JAE1333GT05
  2   48  CEF720 48 port 10/100/1000mb Ethernet  WS-X6748-GE-TX     SAL13463UG3
  5    2  Supervisor Engine 720 (Active)         WS-SUP720-3B       SAL135069CC
  6    2  Supervisor Engine 720 (Hot)            WS-SUP720-3B       SAL1350665E

Mod MAC addresses                       Hw    Fw           Sw           Status
--- ---------------------------------- ------ ------------ ------------ -------
  1  0026.cb02.d000 to 0026.cb02.d07f   2.7   12.2(33)SXI3 12.2(33)SXI3 Ok
  2  0026.9987.9278 to 0026.9987.92a7   3.4   12.2(18r)S1  12.2(33)SXI3 Ok
  5  000a.b86e.20a4 to 000a.b86e.20a7   5.9   8.5(3)       12.2(33)SXI3 Ok
  6  0024.1499.859c to 0024.1499.859f   5.9   8.5(3)       12.2(33)SXI3 Ok

Mod  Sub-Module                  Model              Serial       Hw     Status
---- --------------------------- ------------------ ----------- ------- -------
1/0 4xT3E3 SPA                  SPA-4XT3/E3        JAE1344MOIT  1.1    Ok
1/1 8xCHT1/E1 SPA               SPA-8XCHT1/E1      JAE1347OL0Z  1.5    Ok
  2  Centralized Forwarding Card WS-F6700-CFC       SAL13453G2S  4.1    Ok
  5  Policy Feature Card 3       WS-F6K-PFC3B       SAL13495HBA  2.6    Ok
  5  MSFC3 Daughterboard         WS-SUP720          SAL1350679T  4.0    Ok
  6  Policy Feature Card 3       WS-F6K-PFC3B       SAL1350689H  2.6    Ok
  6  MSFC3 Daughterboard         WS-SUP720          SAL135067E7  4.0    Ok

Mod  Online Diag Status
---- -------------------
  1  Pass
1/0 Unknown
1/1 Unknown
  2  Pass
  5  Pass
  6  Pass

thanks for your attention for this post.

and have a good time

Hi Sanghee Han,

So “show power” is actually given you

“system power redundancy mode = redundant” and

restricted shown in the “show env” cooling section for fan-tray 1:

---

fan-tray 1:
   fan-tray 1 type: WS-C6509-E-FAN
   fan-tray 1 mode: Restricted-power
   fan-tray 1 fan-fail: OK

---

The "restricted" power is the default for the E-chassis.
The WS-C6506/9-E-FAN has two modes - Restricted-Power and High Power.
Restricted-power mode means that the Fan-Tray operates at lower rotating speed 
and it is enough for system’s per slots cooling (to keep temperature under thr).
 
Usually the fans in fan-tray will speed up if a fan has failed in the fan-tray or 
if there are a linecards in the chassis that requires higher cooling.
For example, in case of WS-X6708-10G modules in some slots, 
the chassis/fans will be running high-power mode.
 
The “show env [cooling]” will give you this info, 
with details on required fans CFM capacity for chassis and for each module.
 
Like in you case with 4 modules:
1    7600-SIP-400        265.02  6.31   265.02  6.31  on    on
2    WS-X6748-GE-TX      325.50  7.75   325.50  7.75  on    on
5    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
6    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
 
The cooling at 70 cfm fans rotating looks enough for setup, 
so fan-tray 1 is in default mode Restricted-power:
----------------- show environment ------------------
…  
fan-tray 1:
  fan-tray 1 type: WS-C6509-E-FAN
  fan-tray 1 mode: Restricted-power
  fan-tray 1 fan-fail: OK
… snip…
chassis per slot cooling capacity: 70 cfm ambient temperature: < 55C
  module 1 cooling requirement: 35 cfm
  module 2 cooling requirement: 70 cfm
  module 5 cooling requirement: 35 cfm
  module 6 cooling requirement: 35 cfm
 
And for example in case of the chassis w two WS-X6708-10G-3C in slots 1 and 2 
the fans will be running at high speed and
the output would looks similar to follow:
 
#show env cool    
fan-tray 1:
 fan-tray 1 type: WS-C6509-E-FAN
 fan-tray 1 mode: high-power <--
 fan-tray 1 fan-fail: OK
chassis per slot cooling capacity: 94 cfm ambient temperature: < 55C
 module 1 cooling requirement: 84 cfm  <<<<<
 module 2 cooling requirement: 84 cfm  <<<<<
 module 3 cooling requirement: 70 cfm
 module 4 cooling requirement: 70 cfm
 module 5 cooling requirement: 35 cfm
 module 6 cooling requirement: 35 cfm
 module 7 cooling requirement: 70 cfm
 module 8 cooling requirement: 70 cfm
 
 
 
Thanks,
Sergey

thanks for your answer.

it's a good help for me.