01-19-2010 12:18 AM - edited 03-06-2019 09:21 AM
hi all,
I have a question about power redundancy mode in cat6500-AC3000watt
cat6500#sh power
system power redundancy mode = restricted power mode
i know about combined mode and redundant mode,
but unfamiliar with restricted power mode
is there anyone knows about this?
Solved! Go to Solution.
01-29-2010 12:28 AM
Hi Sanghee Han,
So “show power” is actually given you
“system power redundancy mode = redundant” and
restricted shown in the “show env” cooling section for fan-tray 1:
---
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: Restricted-power
fan-tray 1 fan-fail: OK
---
The "restricted" power is the default for the E-chassis.
The WS-C6506/9-E-FAN has two modes - Restricted-Power and High Power.
Restricted-power mode means that the Fan-Tray operates at lower rotating speed
and it is enough for system’s per slots cooling (to keep temperature under thr).
Usually the fans in fan-tray will speed up if a fan has failed in the fan-tray or
if there are a linecards in the chassis that requires higher cooling.
For example, in case of WS-X6708-10G modules in some slots,
the chassis/fans will be running high-power mode.
The “show env [cooling]” will give you this info,
with details on required fans CFM capacity for chassis and for each module.
Like in you case with 4 modules:
1 7600-SIP-400 265.02 6.31 265.02 6.31 on on
2 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
5 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
6 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
The cooling at 70 cfm fans rotating looks enough for setup,
so fan-tray 1 is in default mode Restricted-power:
----------------- show environment ------------------
…
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: Restricted-power
fan-tray 1 fan-fail: OK
… snip…
chassis per slot cooling capacity: 70 cfm ambient temperature: < 55C
module 1 cooling requirement: 35 cfm
module 2 cooling requirement: 70 cfm
module 5 cooling requirement: 35 cfm
module 6 cooling requirement: 35 cfm
And for example in case of the chassis w two WS-X6708-10G-3C in slots 1 and 2
the fans will be running at high speed and
the output would looks similar to follow:
#show env cool
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: high-power <--
fan-tray 1 fan-fail: OK
chassis per slot cooling capacity: 94 cfm ambient temperature: < 55C
module 1 cooling requirement: 84 cfm <<<<<
module 2 cooling requirement: 84 cfm <<<<<
module 3 cooling requirement: 70 cfm
module 4 cooling requirement: 70 cfm
module 5 cooling requirement: 35 cfm
module 6 cooling requirement: 35 cfm
module 7 cooling requirement: 70 cfm
module 8 cooling requirement: 70 cfm
Thanks,
Sergey
01-26-2010 10:54 PM
Hello!
Is it a newer C6500-E series chassis ?
If yes, than "restricted" power could be the default for E-series, but normally it is
shown in show end, show power for FAN-tray part only, like "fan-tray 1 mode: Restricted-power".
Thanks,
Sergey
01-27-2010 04:14 PM
Thanks for your answer.
then, i wonder how the cat65k-E operates power resource in restricted-power mode.
do you know about this?
01-28-2010 07:45 AM
Hi,
Could you post the full output of "show power", "show env" and clarify which ios version is it.
Thanks,
Sergey
01-28-2010 03:48 PM
hi Sergey
i post the relative log...show power/env/ver/module.
------------------ show power ------------------
system power redundancy mode = redundant
system power total = 2771.16 Watts (65.98 Amps @ 42V)
system power used = 1305.36 Watts (31.08 Amps @ 42V)
system power available = 1465.80 Watts (34.90 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-3000W 2771.16 65.98 OK OK on
2 WS-CAC-3000W 2771.16 65.98 OK OK on
Pwr-Allocated Oper
Fan Type Watts A @42V State
---- ------------------ ------- ------ -----
1 WS-C6509-E-FAN 150.36 3.58 OK
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 7600-SIP-400 265.02 6.31 265.02 6.31 on on
2 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
5 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
6 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
system auxiliary power mode = off
system auxiliary power redundancy operationally = non-redundant
system primary connector power limit = 10920.00 Watts (260.00 Amps @ 42V)
system auxiliary connector power limit = 10500.00 Watts (250.00 Amps @ 42V)
system primary power used = 1305.36 Watts (31.08 Amps @ 42V)
system auxiliary power used = 0 Watt
------------------ show environment ------------------
environmental alarms:
no alarms
backplane:
operating clock count: 2
operating VTT count: 3
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: Restricted-power
fan-tray 1 fan-fail: OK
VTT 1:
VTT 1 OK: OK
VTT 1 outlet temperature: 35C
VTT 2:
VTT 2 OK: OK
VTT 2 outlet temperature: 37C
VTT 3:
VTT 3 OK: OK
VTT 3 outlet temperature: 35C
clock 1:
clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
clock 2 OK: OK, clock 2 clock-inuse: not-in-use
power-supply 1:
power-supply 1 fan-fail: OK
power-supply 1 power-input: AC high
power-supply 1 power-output-mode: high
power-supply 1 power-output-fail: OK
power-supply 2:
power-supply 2 fan-fail: OK
power-supply 2 power-input: AC high
power-supply 2 power-output-mode: high
power-supply 2 power-output-fail: OK
module 1:
module 1 power-output-fail: OK
module 1 outlet temperature: 46C
module 1 inlet temperature: 38C
module 1 device-1 temperature: 44C
module 1 device-2 temperature: 43C
module 2:
module 2 power-output-fail: OK
module 2 outlet temperature: 49C
module 2 inlet temperature: 33C
module 5:
module 5 power-output-fail: OK
module 5 outlet temperature: 37C
module 5 inlet temperature: 32C
module 5 device-1 temperature: 42C
module 5 device-2 temperature: 42C
module 5 asic-1 temperature: 31C
module 5 asic-2 temperature: 31C
module 5 asic-3 temperature: 31C
module 5 asic-4 temperature: 32C
module 5 asic-5 temperature: 31C
module 5 asic-6 temperature: 32C
module 5 RP outlet temperature: 34C
module 5 RP inlet temperature: 35C
module 5 EARL outlet temperature: 43C
module 5 EARL inlet temperature: 34C
module 6:
module 6 power-output-fail: OK
module 6 outlet temperature: 37C
module 6 inlet temperature: 32C
module 6 device-1 temperature: 41C
module 6 device-2 temperature: 41C
module 6 asic-1 temperature: 31C
module 6 asic-2 temperature: 31C
module 6 asic-3 temperature: 31C
module 6 asic-4 temperature: 30C
module 6 asic-5 temperature: 31C
module 6 asic-6 temperature: 31C
module 6 RP outlet temperature: 34C
module 6 RP inlet temperature: 35C
module 6 EARL outlet temperature: 40C
module 6 EARL inlet temperature: 34C
SPA-4XT3/E3[1/0] temperature sensor 0, reading: 39C
SPA-4XT3/E3[1/0] temperature sensor 1, reading: 38C
SPA-4XT3/E3[1/0] temperature sensor 2, reading: 40C
SPA-4XT3/E3[1/0] temperature sensor 3, reading: 41C
SPA-4XT3/E3[1/0] temperature sensor 4, reading: 44C
SPA-4XT3/E3[1/0] nominal: 3.300V, reading: 3.290V
SPA-4XT3/E3[1/0] nominal: 2.500V, reading: 2.510V
SPA-4XT3/E3[1/0] nominal: 1.800V, reading: 1.796V
SPA-4XT3/E3[1/0] nominal: 1.500V, reading: 1.499V
SPA-8XCHT1/E1[1/1] temperature sensor 0, reading: 40C
SPA-8XCHT1/E1[1/1] temperature sensor 1, reading: 41C
SPA-8XCHT1/E1[1/1] temperature sensor 2, reading: 38C
SPA-8XCHT1/E1[1/1] temperature sensor 3, reading: 35C
SPA-8XCHT1/E1[1/1] temperature sensor 4, reading: 45C
SPA-8XCHT1/E1[1/1] nominal: 3.300V, reading: 3.320V
SPA-8XCHT1/E1[1/1] nominal: 2.500V, reading: 2.516V
SPA-8XCHT1/E1[1/1] nominal: 1.800V, reading: 1.807V
SPA-8XCHT1/E1[1/1] nominal: 1.500V, reading: 1.509V
chassis connector rating: 1302.00 Watts (31.00 Amps @ 42V)
chassis auxiliary connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 1
module 1 connector rating: 1512.00 Watts (36.00 Amps @ 42V)
module 1 power consumption: 265.02 Watts ( 6.31 Amps @ 42V)
module 2
module 2 connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 2 power consumption: 325.50 Watts ( 7.75 Amps @ 42V)
module 5
module 5 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 5 power consumption: 282.24 Watts ( 6.72 Amps @ 42V)
module 6
module 6 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 6 power consumption: 282.24 Watts ( 6.72 Amps @ 42V)
chassis per slot cooling capacity: 70 cfm
ambient temperature: < 55C
module 1 cooling requirement: 35 cfm
module 2 cooling requirement: 70 cfm
module 5 cooling requirement: 35 cfm
module 6 cooling requirement: 35 cfm
------------------ show version ------------------
Cisco IOS Software, s72033_rp Software (s72033_rp-ADVIPSERVICESK9_WAN-M), Version 12.2(33)SXI3, RELEASE SOFTWARE (fc2)
Technical Support: http://www.cisco.com/techsupport
Copyright (c) 1986-2009 by Cisco Systems, Inc.
Compiled Tue 27-Oct-09 11:11 by prod_rel_team
ROM: System Bootstrap, Version 12.2(17r)SX5, RELEASE SOFTWARE (fc1)
PE007 uptime is 9 minutes
Uptime for this control processor is 9 minutes
Time since PE007 switched to active is 8 minutes
System returned to ROM by reload at 10:45:12 UTC Mon Jan 4 2010 (SP by reload)
System image file is "sup-bootflash:s72033-advipservicesk9_wan-mz.122-33.SXI3.bin"
Last reload reason: Reload Command
This product contains cryptographic features and is subject to United
States and local country laws governing import, export, transfer and
use. Delivery of Cisco cryptographic products does not imply
third-party authority to import, export, distribute or use encryption.
Importers, exporters, distributors and users are responsible for
compliance with U.S. and local country laws. By using this product you
agree to comply with applicable laws and regulations. If you are unable
to comply with U.S. and local laws, return this product immediately.
A summary of U.S. laws governing Cisco cryptographic products may be found at:
http://www.cisco.com/wwl/export/crypto/tool/stqrg.html
If you require further assistance please contact us by sending email to
export@cisco.com.
cisco WS-C6509-E (R7000) processor (revision 1.5) with 458720K/65536K bytes of memory.
Processor board ID SMC1346005X
SR71000 CPU at 600Mhz, Implementation 0x504, Rev 1.2, 512KB L2 Cache
Last reset from s/w reset
1 SIP-400 controller (4 Serial)(8 E1).
1 Virtual Ethernet interface
52 Gigabit Ethernet interfaces
7 Serial interfaces
8 Channelized E1 ports
1917K bytes of non-volatile configuration memory.
8192K bytes of packet buffer memory.
65536K bytes of Flash internal SIMM (Sector size 512K).
Configuration register is 0x2102
------------------ show module ------------------
Mod Ports Card Type Model Serial No.
--- ----- -------------------------------------- ------------------ -----------
1 0 4-subslot SPA Interface Processor-400 7600-SIP-400 JAE1333GT05
2 48 CEF720 48 port 10/100/1000mb Ethernet WS-X6748-GE-TX SAL13463UG3
5 2 Supervisor Engine 720 (Active) WS-SUP720-3B SAL135069CC
6 2 Supervisor Engine 720 (Hot) WS-SUP720-3B SAL1350665E
Mod MAC addresses Hw Fw Sw Status
--- ---------------------------------- ------ ------------ ------------ -------
1 0026.cb02.d000 to 0026.cb02.d07f 2.7 12.2(33)SXI3 12.2(33)SXI3 Ok
2 0026.9987.9278 to 0026.9987.92a7 3.4 12.2(18r)S1 12.2(33)SXI3 Ok
5 000a.b86e.20a4 to 000a.b86e.20a7 5.9 8.5(3) 12.2(33)SXI3 Ok
6 0024.1499.859c to 0024.1499.859f 5.9 8.5(3) 12.2(33)SXI3 Ok
Mod Sub-Module Model Serial Hw Status
---- --------------------------- ------------------ ----------- ------- -------
1/0 4xT3E3 SPA SPA-4XT3/E3 JAE1344MOIT 1.1 Ok
1/1 8xCHT1/E1 SPA SPA-8XCHT1/E1 JAE1347OL0Z 1.5 Ok
2 Centralized Forwarding Card WS-F6700-CFC SAL13453G2S 4.1 Ok
5 Policy Feature Card 3 WS-F6K-PFC3B SAL13495HBA 2.6 Ok
5 MSFC3 Daughterboard WS-SUP720 SAL1350679T 4.0 Ok
6 Policy Feature Card 3 WS-F6K-PFC3B SAL1350689H 2.6 Ok
6 MSFC3 Daughterboard WS-SUP720 SAL135067E7 4.0 Ok
Mod Online Diag Status
---- -------------------
1 Pass
1/0 Unknown
1/1 Unknown
2 Pass
5 Pass
6 Pass
thanks for your attention for this post.
and have a good time
01-29-2010 12:28 AM
Hi Sanghee Han,
So “show power” is actually given you
“system power redundancy mode = redundant” and
restricted shown in the “show env” cooling section for fan-tray 1:
---
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: Restricted-power
fan-tray 1 fan-fail: OK
---
The "restricted" power is the default for the E-chassis.
The WS-C6506/9-E-FAN has two modes - Restricted-Power and High Power.
Restricted-power mode means that the Fan-Tray operates at lower rotating speed
and it is enough for system’s per slots cooling (to keep temperature under thr).
Usually the fans in fan-tray will speed up if a fan has failed in the fan-tray or
if there are a linecards in the chassis that requires higher cooling.
For example, in case of WS-X6708-10G modules in some slots,
the chassis/fans will be running high-power mode.
The “show env [cooling]” will give you this info,
with details on required fans CFM capacity for chassis and for each module.
Like in you case with 4 modules:
1 7600-SIP-400 265.02 6.31 265.02 6.31 on on
2 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
5 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
6 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
The cooling at 70 cfm fans rotating looks enough for setup,
so fan-tray 1 is in default mode Restricted-power:
----------------- show environment ------------------
…
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: Restricted-power
fan-tray 1 fan-fail: OK
… snip…
chassis per slot cooling capacity: 70 cfm ambient temperature: < 55C
module 1 cooling requirement: 35 cfm
module 2 cooling requirement: 70 cfm
module 5 cooling requirement: 35 cfm
module 6 cooling requirement: 35 cfm
And for example in case of the chassis w two WS-X6708-10G-3C in slots 1 and 2
the fans will be running at high speed and
the output would looks similar to follow:
#show env cool
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: high-power <--
fan-tray 1 fan-fail: OK
chassis per slot cooling capacity: 94 cfm ambient temperature: < 55C
module 1 cooling requirement: 84 cfm <<<<<
module 2 cooling requirement: 84 cfm <<<<<
module 3 cooling requirement: 70 cfm
module 4 cooling requirement: 70 cfm
module 5 cooling requirement: 35 cfm
module 6 cooling requirement: 35 cfm
module 7 cooling requirement: 70 cfm
module 8 cooling requirement: 70 cfm
Thanks,
Sergey
01-31-2010 06:41 PM
thanks for your answer.
it's a good help for me.
thanks again~~