Cisco MLS SUP720 issue
Mar 17th, 2010
In our network intially we had 800mb of traffic flow between our site1 to site2 with point to point 1 gig connectivty in the cat 6500 with SUP 2 on both the site
on 1 site we upgraded the SUP2 to SUP720 last night and we din see any issues but when 600mb traffic flow started in mid day we had a issue that from site 1 to site 2 no connectvity isssues but icmp from site2 to site1 is giving issue
the interface traffic size
5 minute input rate 637419000 bits/sec, 464796 packets/sec  site2 to site1
5 minute output rate 630223000 bits/sec, 465577 packets/sec site1 to site 2
we suspecting some interface traffic ratelimit issue since we din face the issue in the morning when we have 500mb of traffic
we have the below config on our new SUP720 catalayst whether this will be rootcause
no mls acl tcam share-global
mls aging long 64
mls aging normal 32
mls netflow interface
mls rate-limit unicast cef glean 20000 60
mls rate-limit unicast ip rpf-failure 500 10
mls rate-limit unicast ip icmp redirect 0
mls rate-limit unicast ip icmp unreachable no-route 500 10
mls rate-limit unicast ip icmp unreachable acl-drop 500 10
mls rate-limit unicast ip errors 500 10
mls rate-limit all ttl-failure 10 1
mls verify ip length minimum
mls cef error action reset
thanks
Vinu
Jan Nejman Wed, 03/17/2010 - 08:18
  • Bronze, 100 points or more
could you check your switch processor utilization?
show module        # select supervisor module id
attach 2               # 2 is module id
show proc cpu     # check load on switch processor
exit
Kind regards
Jan Nejman
Caligare, Co.
http://www.caligare.com/
vinoth.kumar Wed, 03/17/2010 - 08:31
Hi ,
we are having normal cpu
-DIST65-#sh processes cpu
CPU utilization for five seconds: 3%/1%; one minute: 3%; five minutes: 4%
Mod Ports Card Type Model Serial
No.
Jan Nejman Wed, 03/17/2010 - 08:41
your "proc cpu" is from route processor or from switch processor? I saw usually
higher utilization on swich processor. Did you run attach command?
Kind regards,
Jan
Giuseppe Larosa Wed, 03/17/2010 - 09:02
  • Hall of Fame,
    Founding Member
Hello Vinoth,
Jan has already provided the sequence of commands
in your case sup720 should be installed in slot 5 or 6 if this is a 6506 or 6509 chassis
sh module can tell you this
with attach you get a session to switch processor
example:
attach 5
Trying Switch ...
Entering CONSOLE for Switch
Type "^C^C^C" to end this session
Switch-sp#sh proc cpu
CPU utilization for five seconds: 17%/0%; one minute: 15%; five minutes: 15%
PID Runtime(ms)   Invoked      uSecs   5Sec   1Min   5Min TTY Process
   1           0         1          0  0.00%  0.00%  0.00%   0 Chunk Manager
   2         720     32227         22  0.00%  0.00%  0.00%   0 Load Meter
   3       29368    242945        120  0.00%  0.01%  0.00%   0 CEF: IPv4 pro
Switch-sp#exit
[Connection to Switch closed by foreign host]
Switch#
you type exit to go back to standard telnet session that is on the route processor
Hope to help
Giuseppe
vinoth.kumar Wed, 03/17/2010 - 09:10
please find the attach command results
-DIST65-01.TC1#attach 5
Trying Switch ...
Type "CC^C" to end this session
DIST65-01.TC1-sp#sh proc cpu
CPU utilization for five seconds: 11%/0%; one minute: 15%; five minutes: 15%
1 4 5 800 0.00% 0.00% 0.00% 0 Chunk Manager
2 2616 328219 7 0.00% 0.00% 0.00% 0 Load Meter
3 36559756 33873626 1079 1.75% 2.25% 2.21% 0 DiagCard1/-1
4 0 51 0 0.00% 0.00% 0.00% 0
Retransmission o
5 4 3 1333 0.00% 0.00% 0.00% 0 IPC ISSU
Dispatc
6 0 1 0 0.00% 0.00% 0.00% 0 PF Redun ICC
Req
7 0 19 0 0.00% 0.00% 0.00% 0 PF Redun ICC
Req
8 0 2 0 0.00% 0.00% 0.00% 0 LC Registry
Expo
9 5402320 348104 15519 0.00% 0.34% 0.31% 0 Check heaps
10 0 1 0 0.00% 0.00% 0.00% 0 Pool Manager
11 0 2 0 0.00% 0.00% 0.00% 0 Timers
12 76 28017 2 0.00% 0.00% 0.00% 0 ARP Input
13 0 1 0 0.00% 0.00% 0.00% 0
AAA_SERVER_DEADT
14 0 2 0 0.00% 0.00% 0.00% 0 AAA
high-capacit
15 0 1 0 0.00% 0.00% 0.00% 0 Policy
Manager
16 0 2 0 0.00% 0.00% 0.00% 0 DDR Timers
17 0 2 0 0.00% 0.00% 0.00% 0 Dialer event
18 168 27342 6 0.00% 0.00% 0.00% 0 IPC Dynamic
Cach
19 0 1 0 0.00% 0.00% 0.00% 0 IPC Zone
Manager
20 2996 1630745 1 0.00% 0.00% 0.00% 0 IPC Periodic
Tim
21 2168 1630744 1 0.00% 0.00% 0.00% 0 IPC Deferred
Por
22 0 1 0 0.00% 0.00% 0.00% 0 IPC Process
leve
23 36 258 139 0.00% 0.00% 0.00% 0 IPC Seat
Manager
24 0 1 0 0.00% 0.00% 0.00% 0 IPC Session
Serv
25 0 1 0 0.00% 0.00% 0.00% 0 IPC Stdby
Update
26 0 2 0 0.00% 0.00% 0.00% 0 Serial
Backgroun
27 1472 9 163555 0.00% 0.00% 0.00% 0 PrstVbl
28 0 1 0 0.00% 0.00% 0.00% 0 Crash writer
29 0 7 0 0.00% 0.00% 0.00% 0 RPC
cygnus-oir
30 7916 1630657 4 0.00% 0.00% 0.00% 0 GraphIt
31 0 1 0 0.00% 0.00% 0.00% 0 SERIAL
A'detect
32 16 15 1066 0.00% 0.00% 0.00% 0
client_entity_se
33 0 2 0 0.00% 0.00% 0.00% 0 SMART
34 0 1 0 0.00% 0.00% 0.00% 0 Reset Process
35 0 4 0 0.00% 0.00% 0.00% 0 RPC
pf_media_lay
36 0 1 0 0.00% 0.00% 0.00% 0 Critical
Bkgnd
37 9728 235644 41 0.00% 0.00% 0.00% 0 Net
Background
38 0 14 0 0.00% 0.00% 0.00% 0 IDB Work
39 0 441 0 0.00% 0.00% 0.00% 0 Logger
40 4292 1630654 2 0.00% 0.00% 0.00% 0 TTY
Background
41 15020 1645655 9 0.00% 0.00% 0.00% 0 Per-Second
Jobs
42 794920 80497 9875 0.00% 0.03% 0.00% 0 Per-minute
Jobs
43 4 61 65 0.00% 0.00% 0.00% 0 Cat6k NTI ICC
pr
44 48 604 79 0.00% 0.00% 0.00% 0 rf proxy sp
agen
45 0 1 0 0.00% 0.00% 0.00% 0 ISSU PROCESS
IPC
46 0 1 0 0.00% 0.00% 0.00% 0 RF Messaging
Pro
47 0 1 0 0.00% 0.00% 0.00% 0 PrstVbl IPC
Msg
48 0 1 0 0.00% 0.00% 0.00% 0 VSLP ISSU
receiv
49 24 255 94 0.00% 0.00% 0.00% 0 Env action
50 0 11 0 0.00% 0.00% 0.00% 0 Module oper
stat
51 0 72 0 0.00% 0.00% 0.00% 0 SNMP Traps
52 0 72 0 0.00% 0.00% 0.00% 0 SNMP Traps
53 4 40 100 0.00% 0.00% 0.00% 0 Snmp ICC
Process
54 0 3 0 0.00% 0.00% 0.00% 0 DFC Command
Task
55 0 1 0 0.00% 0.00% 0.00% 0 VS Redirect
EOBC
56 0 1 0 0.00% 0.00% 0.00% 0 VSIBC process
57 0 1 0 0.00% 0.00% 0.00% 0 VS IBSCP ISSU
58 0 1 0 0.00% 0.00% 0.00% 0 VS IBSCP ISSU
BO
59 4 39 102 0.00% 0.00% 0.00% 0 ICC Nego
60 0 6 0 0.00% 0.00% 0.00% 0 ACE_REQUESTS
han
61 0 3 0 0.00% 0.00% 0.00% 0 ACE Process
Msg
62 20 270 74 0.00% 0.00% 0.00% 0 ACE SP Tunnel
Ta
63 0 1 0 0.00% 0.00% 0.00% 0 EOBC Monitor
Pro
64 0 9 0 0.00% 0.00% 0.00% 0 Net Input
65 0 1 0 0.00% 0.00% 0.00% 0 pclc_sp
66 0 36 0 0.00% 0.00% 0.00% 0 PF DB SCP ICC
pr
67 4 8 500 0.00% 0.00% 0.00% 0 PF IPC ICC
Init
68 20 298 67 0.00% 0.00% 0.00% 0 Logger SP
Proces
69 0 1 0 0.00% 0.00% 0.00% 0 PF SCP
process
70 420 39 10769 0.00% 0.00% 0.00% 0 PF Sync
process
71 0 7 0 0.00% 0.00% 0.00% 0 RPC
rf_set_debug
72 16 164 97 0.00% 0.00% 0.00% 0 RF Status
73 0 315 0 0.00% 0.00% 0.00% 0 RPC Sync
74 172 6174 27 0.00% 0.00% 0.00% 0 SCP Multicast
75 0 2 0 0.00% 0.00% 0.00% 0 SCP Generic
Unso
76 17203100 9335120 1842 0.00% 0.89% 0.97% 0 DiagCard3/-1
77 2686156 20976309 128 0.15% 0.18% 0.16% 0 SCP Download
Lis
78 0 1 0 0.00% 0.00% 0.00% 0 LCP Bootupg
proc
79 1906508 9761 195318 0.00% 0.01% 0.05% 0 TCAM Manager
pro
80 0 1 0 0.00% 0.00% 0.00% 0 VS CHASSIS
Info
81 0 3 0 0.00% 0.00% 0.00% 0 VS ICC
request p
82 0 2 0 0.00% 0.00% 0.00% 0
cpf_msg_holdq_pr
83 0 1 0 0.00% 0.00% 0.00% 0
cpf_msg_rcvq_pro
84 0 1 0 0.00% 0.00% 0.00% 0 CHKPT Test
clien
85 4523796 6767434 668 0.00% 0.28% 0.26% 0 DiagCard5/-1
86 0 1 0 0.00% 0.00% 0.00% 0 IVFS SP ICC
Proc
87 34728 1011569 34 0.07% 0.00% 0.00% 0 LACP Protocol
88 0 1 0 0.00% 0.00% 0.00% 0 LMP state
machin
89 0 1 0 0.00% 0.00% 0.00% 0 VSLP RRP
event g
90 29716 432846 68 0.00% 0.00% 0.00% 0 Compute load
avg
91 24848 1554986 15 0.00% 0.00% 0.00% 0 OIR Process
92 0 1 0 0.00% 0.00% 0.00% 0 Inode Table
Dest
93 744 109478 6 0.00% 0.00% 0.00% 0 Fabric
Manager
94 39512 2455359 16 0.00% 0.00% 0.00% 0 Heartbeat
Proces
95 4 260 15 0.00% 0.00% 0.00% 0 Const ICC
reques
96 0 1 0 0.00% 0.00% 0.00% 0 Const ICC
event
97 0 1 0 0.00% 0.00% 0.00% 0 Const ICC
except
98 0 1 0 0.00% 0.00% 0.00% 0 ICC Local
Reques
99 6516 413152 15 0.00% 0.00% 0.00% 0 ICC Async
mcast
100 0 1 0 0.00% 0.00% 0.00% 0 ICC_REQ Debug
Pr
101 0 1 0 0.00% 0.00% 0.00% 0 ICC FC
Process
102 0 1 0 0.00% 0.00% 0.00% 0 ICC FC Test
Send
103 0 1 0 0.00% 0.00% 0.00% 0 ICC FC Test
Low
104 0 1 0 0.00% 0.00% 0.00% 0 itasca_sp
105 0 1 0 0.00% 0.00% 0.00% 0
StandbyDiagDaemo
106 103745948 197860956 524 5.27% 6.34% 6.37% 0 slcp process
107 0 2 0 0.00% 0.00% 0.00% 0 VQM SP
Process
108 0 3 0 0.00% 0.00% 0.00% 0 RPC
vs_prov_lc-M
109 13364428 7258714 1841 0.00% 1.05% 1.00% 0 DiagCard2/-1
110 0 1 0 0.00% 0.00% 0.00% 0 Mistral Reset
Pr
111 0 1 0 0.00% 0.00% 0.00% 0 ECC
correctable
112 36 280 128 0.00% 0.00% 0.00% 0 rf task
113 0 1 0 0.00% 0.00% 0.00% 0 RF High
Priority
114 6628 1630817 4 0.00% 0.00% 0.00% 0 PF_Init
Process
115 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
116 152268 3469420 43 0.00% 0.00% 0.00% 0 SCP async:
LCP#1
117 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
118 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
119 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
120 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
121 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
122 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
123 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
124 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
125 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
126 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
127 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
128 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
129 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
130 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
131 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
132 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
133 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
134 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
135 0 1 0 0.00% 0.00% 0.00% 0 RTTYS Process
136 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
137 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
138 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
139 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
140 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
141 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
142 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
143 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
144 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
145 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
146 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
147 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
148 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
149 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
150 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
151 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
152 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
153 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
154 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
155 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
156 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
157 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
158 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
159 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
160 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
161 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
162 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
163 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
164 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
165 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
166 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
167 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
168 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
169 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
170 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
171 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
172 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
173 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
174 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
175 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
176 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
177 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
178 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
179 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
180 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
181 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
182 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
183 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
184 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
185 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
186 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
187 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
188 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
189 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
190 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
191 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
192 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
193 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
194 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
195 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
196 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
197 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
198 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
199 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
200 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
201 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
202 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
203 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
204 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
205 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
206 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
207 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
208 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
209 0 1 0 0.00% 0.00% 0.00% 0 IPC ISSU
Version
210 0 1 0 0.00% 0.00% 0.00% 0 RPC
rpc-master
211 0 23 0 0.00% 0.00% 0.00% 0
fabm_ch_sync:0
212 8 23 347 0.00% 0.00% 0.00% 0
fabm_ch_sync:9
213 12 23 521 0.00% 0.00% 0.00% 0
fabm_ch_sync:4
214 4 5 800 0.00% 0.00% 0.00% 0 Fabman
Timeout P
215 40148 10625645 3 0.00% 0.00% 0.00% 0 Heartbeat
216 0 1 0 0.00% 0.00% 0.00% 0 PS HB
listener P
217 0 1 0 0.00% 0.00% 0.00% 0 IDPROM Msg
Proce
218 0 1 0 0.00% 0.00% 0.00% 0 VSHA Handle
Leg
219 0 1 0 0.00% 0.00% 0.00% 0 Notify peer
imag
220 0 1 0 0.00% 0.00% 0.00% 0 IPC RTTYC
Messag
221 0 7 0 0.00% 0.00% 0.00% 0 NTI agent
handle
222 0 1 0 0.00% 0.00% 0.00% 0 NTI Example
Proc
223 0 1 0 0.00% 0.00% 0.00% 0 Cat6k NTI SP
Exa
224 4 60 66 0.00% 0.00% 0.00% 0 PF_Split Sync
Pr
225 0 16 0 0.00% 0.00% 0.00% 0 RPC
pf-split-sp
226 0 2 0 0.00% 0.00% 0.00% 0 RPC idprom-SP
227 56 1027 54 0.00% 0.00% 0.00% 0 RFS server
proce
228 0 350 0 0.00% 0.00% 0.00% 0 BACK CHECK
229 12 405 29 0.00% 0.00% 0.00% 0 AggMgr
Process
230 0 1 0 0.00% 0.00% 0.00% 0
cpf_process_tpQ
231 0 1 0 0.00% 0.00% 0.00% 0 Transport
Port A
232 12184 19378362 0 0.00% 0.00% 0.00% 0 EARL Intr
Thrtl
233 0 1 0 0.00% 0.00% 0.00% 0
const_dump_info_
234 0 2 0 0.00% 0.00% 0.00% 0 EARL FIB
Manager
235 87548 5968 14669 0.00% 0.00% 0.00% 0 EARL CC Task
236 244 441 553 0.00% 0.00% 0.00% 0 Remote
Console P
237 0 1 0 0.00% 0.00% 0.00% 0
DiagErrorLogProc
238 0 1 0 0.00% 0.00% 0.00% 0 CFRW_OIR
Process
239 8 16 500 0.00% 0.00% 0.00% 0 DiagSNMPProc
240 0 2 0 0.00% 0.00% 0.00% 0 Protocol
Filteri
241 4 8 500 0.00% 0.00% 0.00% 0 OBFL ENV
obfl0
242 0 2 0 0.00% 0.00% 0.00% 0 SEA_SCP_PRC
243 0 1 0 0.00% 0.00% 0.00% 0 SPAN EARL
Task
244 0 1 0 0.00% 0.00% 0.00% 0 ADJ MGR
245 0 2 0 0.00% 0.00% 0.00% 0 ADJ_MGR
246 8008 428084 18 0.00% 0.00% 0.00% 0 L2 Control
Task
247 14656 1623008 9 0.00% 0.00% 0.00% 0 L2 Throttle
Task
248 4760 657733 7 0.00% 0.00% 0.00% 0 L2 Aging Task
249 27680016 700077 39538 1.67% 1.67% 1.67% 0 Vlan
Statistics
250 20428 2487681 8 0.00% 0.00% 0.00% 0 L2 PI_E
consiste
251 2048 878238 2 0.00% 0.00% 0.00% 0 EARL7 monitor
ta
252 11304888 58030 194817 0.00% 0.71% 0.67% 0 TYFIB Table
Mana
253 948 34129 27 0.00% 0.00% 0.00% 0 CFIB-BGP Task
254 1056 1309 806 0.00% 0.00% 0.00% 0 CFIB LC QUEUE
BO
255 12228 1793059 6 0.00% 0.00% 0.00% 0 CFIB LC TIMER
Ta
256 676 164012 4 0.00% 0.00% 0.00% 0 CFIB LC STATS
Ta
257 0 2 0 0.00% 0.00% 0.00% 0 Gemini SP
proces
258 840 20191 41 0.00% 0.00% 0.00% 0 Online
Linecard
259 0 1 0 0.00% 0.00% 0.00% 0 DiagSatCtrl
Proc
260 1395444 5827031 239 0.00% 0.00% 0.02% 0 NF Exception
Tas
261 148 2519 58 0.00% 0.00% 0.00% 0 L3 Control
Task
262 64 1 64000 0.00% 0.00% 0.00% 0 Netflow NDE
Task
263 8436 795856 10 0.00% 0.00% 0.00% 0 Netflow Aging
Ta
264 576 166866 3 0.00% 0.00% 0.00% 0 Task for
pre-pro
265 12984 491907 26 0.00% 0.00% 0.00% 0 Netflow
Mgmt_Sta
266 0 1 0 0.00% 0.00% 0.00% 0 Netflow
Sampling
267 0 3 0 0.00% 0.00% 0.00% 0 MLS Stats
Hostor
268 0 1 0 0.00% 0.00% 0.00% 0 Async write
proc
269 0 1 0 0.00% 0.00% 0.00% 0 Async write
proc
270 0 1 0 0.00% 0.00% 0.00% 0 Async write
proc
271 0 1 0 0.00% 0.00% 0.00% 0 Async write
proc
272 1368 27339 50 0.00% 0.00% 0.00% 0 DFS flush
period
273 0 2 0 0.00% 0.00% 0.00% 0 AAA Server
274 0 1 0 0.00% 0.00% 0.00% 0 AAA ACCT Proc
275 0 1 0 0.00% 0.00% 0.00% 0 ACCT Periodic
Pr
276 0 1 0 0.00% 0.00% 0.00% 0 AAA System
Acct
277 0 2 0 0.00% 0.00% 0.00% 0 AAA
Dictionary R
278 0 2 0 0.00% 0.00% 0.00% 0 CEF switching
ba
279 20 27367 0 0.00% 0.00% 0.00% 0 IP Input
280 0 1 0 0.00% 0.00% 0.00% 0 ICMP event
handl
281 1896 328024 5 0.00% 0.00% 0.00% 0 SSM
connection m
282 627328 8004112 78 0.00% 0.04% 0.05% 0 Spanning Tree
283 20 318 62 0.00% 0.00% 0.00% 0 SpanTree Msg
284 10648 1641947 6 0.00% 0.00% 0.00% 0 UDLD
285 0 2 0 0.00% 0.00% 0.00% 0 REP Topology
cha
286 8 17 470 0.00% 0.00% 0.00% 0 Const Rate
Limit
287 0 1 0 0.00% 0.00% 0.00% 0 SP DHCP
Snooping
288 48 244 196 0.00% 0.00% 0.00% 0 802.1x switch
289 7792 98076 79 0.00% 0.00% 0.00% 0 DTP Protocol
290 60 51 1176 0.00% 0.00% 0.00% 0 BGP INT
291 896 51315 17 0.00% 0.00% 0.00% 0 L2 MAC oob
sync
292 8 1041 7 0.00% 0.00% 0.00% 0 L3 Manager SP
Co
293 112 1024 109 0.00% 0.00% 0.00% 0 L3 Manager SP
294 7832 1252193 6 0.00% 0.00% 0.00% 0 mls-hal
Process
295 152 91291 1 0.00% 0.00% 0.00% 0 mfib-const-lc
Pr
296 160324 16386617 9 0.00% 0.00% 0.00% 0 Mcast Hw
Agent6
297 0 2 0 0.00% 0.00% 0.00% 0 mls-msc-ha
proce
298 68 291 233 0.00% 0.00% 0.00% 0 mls-msc
Process
299 0 1 0 0.00% 0.00% 0.00% 0 mls-msc-cc
Proce
300 0 2 0 0.00% 0.00% 0.00% 0 MVRP Process
301 4 84 47 0.00% 0.00% 0.00% 0 PIM Snooping
Pro
302 0 1 0 0.00% 0.00% 0.00% 0 pm-sp-mat
303 48 27367 1 0.00% 0.00% 0.00% 0 Port-Security
304 0 1 0 0.00% 0.00% 0.00% 0 Private hosts
sp
305 2572 27104 94 0.00% 0.00% 0.00% 0 QoS SP
Process
306 0 1 0 0.00% 0.00% 0.00% 0 Switch Backup
In
307 1200 164011 7 0.00% 0.00% 0.00% 0 Ethchnl
308 2120 35689 59 0.00% 0.00% 0.00% 0 CEF
background p
309 59308 426493 139 0.00% 0.00% 0.00% 0 Hardware API
bac
310 0 2 0 0.00% 0.00% 0.00% 0 CEF LC IPC
Backg
311 16184 2012769 8 0.00% 0.00% 0.00% 0 CEF LC Stats
312 0 1 0 0.00% 0.00% 0.00% 0 TCP Timer
313 0 1 0 0.00% 0.00% 0.00% 0 TCP Protocols
314 0 1 0 0.00% 0.00% 0.00% 0 Socket Timers
315 0 5563 0 0.00% 0.00% 0.00% 0 HTTP CORE
316 0 1 0 0.00% 0.00% 0.00% 0 Probe Input
317 0 1 0 0.00% 0.00% 0.00% 0 XDR
background p
318 8716 434707 20 0.00% 0.00% 0.00% 0 XDR mcast
319 33204 1643792 20 0.00% 0.00% 0.00% 0 XDR LC PRIO
Back
320 2188 27372 79 0.00% 0.00% 0.00% 0 XDR LC PRIO
Crit
321 92 138 666 0.00% 0.00% 0.00% 0 XDR LC Pre
Sys_i
322 11364 26157 434 0.00% 0.00% 0.00% 0 XDR LC
Backgroun
323 0 1 0 0.00% 0.00% 0.00% 0 IP Traceroute
324 0 1 0 0.00% 0.00% 0.00% 0 RARP Input
325 0 1 0 0.00% 0.00% 0.00% 0 PPP IP Add
Route
326 0 1 0 0.00% 0.00% 0.00% 0 X.25 Encaps
Mana
327 0 2 0 0.00% 0.00% 0.00% 0 REP LSL Proc
328 0 2 0 0.00% 0.00% 0.00% 0 REP BPA/EPA
Proc
329 0 4 0 0.00% 0.00% 0.00% 0 MRIB LC IPC
Proc
330 752 597723 1 0.00% 0.00% 0.00% 0 CFMPAL
Process
331 8104 183442 44 0.00% 0.00% 0.00% 0 IP ACL XDR LC
Ba
332 257848 9662654 26 0.00% 0.00% 0.00% 0 mls-gc
Process
333 0 1 0 0.00% 0.00% 0.00% 0 mls-pimsn
Proces
334 3924 1634709 2 0.00% 0.00% 0.00% 0 MLTL Agent
335 0 1 0 0.00% 0.00% 0.00% 0 mld-mrouter
Proc
336 0 1 0 0.00% 0.00% 0.00% 0 mls-cgmp
Process
337 2636 109471 24 0.00% 0.00% 0.00% 0 mls-igmp
Process
338 28 113 247 0.00% 0.00% 0.00% 0
mcast-igmp-filte
339 4896 182462 26 0.00% 0.00% 0.00% 0 mls-mld
Process
340 0 1 0 0.00% 0.00% 0.00% 0 EM Background
Pr
341 0 2 0 0.00% 0.00% 0.00% 0 LOCAL AAA
342 0 2 0 0.00% 0.00% 0.00% 0 ENABLE AAA
343 0 2 0 0.00% 0.00% 0.00% 0 LINE AAA
344 0 2 0 0.00% 0.00% 0.00% 0 TPLUS
345 0 1 0 0.00% 0.00% 0.00% 0 Pre-download
RP
346 0 1 0 0.00% 0.00% 0.00% 0 Pre-dnld LC
to A
347 0 1 0 0.00% 0.00% 0.00% 0 Pre-download
pee
348 0 1 0 0.00% 0.00% 0.00% 0 router-guard
Pro
349 0 2 0 0.00% 0.00% 0.00% 0 MVRP SWITCH
Proc
350 0 2 0 0.00% 0.00% 0.00% 0 AAA SEND STOP
EV
351 4 7 571 0.00% 0.00% 0.00% 0 MCM IPC
Master
352 0 2 0 0.00% 0.00% 0.00% 0 RPC vslp_sp
353 60 19 3157 0.00% 0.00% 0.00% 0 OBFL MSG
obfl0
354 0 2 0 0.00% 0.00% 0.00% 0 Rommon
upgrade p
355 0 1 0 0.00% 0.00% 0.00% 0 CONST SMC
356 0 2 0 0.00% 0.00% 0.00% 0 RPC
c6k_autoshut
357 5072504 1550295 3271 0.00% 0.29% 0.29% 0 Env Poll
358 0 1 0 0.00% 0.00% 0.00% 0 Cat6k NTI SP
Exa
359 2240 328019 6 0.00% 0.00% 0.00% 0 Inline Power
Por
360 2767124 26521297 104 0.31% 0.06% 0.05% 0 C6K PROCMIB
SP P
361 0 2 0 0.00% 0.00% 0.00% 0 RPC
c6k_schedule
362 0 4 0 0.00% 0.00% 0.00% 0 RPC c6k_ubl
363 0 1 0 0.00% 0.00% 0.00% 0 capture
process
364 0 2 0 0.00% 0.00% 0.00% 0 RPC
cdump_rp_req
365 0 2 0 0.00% 0.00% 0.00% 0 RPC
cfmpal_rpc_r
366 0 2 0 0.00% 0.00% 0.00% 0 Const FIB
excep
367 0 2 0 0.00% 0.00% 0.00% 0 RPC
const_ifs_rp
368 0 2 0 0.00% 0.00% 0.00% 0 RPC cts_rp
369 0 2 0 0.00% 0.00% 0.00% 0 RPC
dhcp_snoopin
370 8 4 2000 0.00% 0.00% 0.00% 0 OBFL INTR
obfl0
371 224 16575 13 0.00% 0.00% 0.00% 0 OBFL TEMP
obfl0
372 512 39 13128 0.00% 0.00% 0.00% 0 HW Capacity
ICC
373 0 2 0 0.00% 0.00% 0.00% 0 RPC intacc_rp
374 0 2 0 0.00% 0.00% 0.00% 0 RPC itasca_sp
375 6144 2415 2544 0.00% 0.00% 0.00% 0 L2
Application T
376 0 2 0 0.00% 0.00% 0.00% 0 RPC
l2_macmove_r
377 0 1 0 0.00% 0.00% 0.00% 0 L2 Macn Task
378 0 4 0 0.00% 0.00% 0.00% 0 RPC
c6k_ltl_rp
379 0 2 0 0.00% 0.00% 0.00% 0 RPC
mvrp_rp2sp
380 5152 1632531 3 0.00% 0.00% 0.00% 0 NV Health
Monito
381 1256 546691 2 0.00% 0.00% 0.00% 0
DiagInbandRatePr
382 0 2 0 0.00% 0.00% 0.00% 0 RPC
c6k_oversubs
383 0 2 0 0.00% 0.00% 0.00% 0 RPC
pclc_g2_fw_s
384 0 2 0 0.00% 0.00% 0.00% 0 RPC
pclc_g2_ids_
385 120 1190 100 0.00% 0.00% 0.00% 0 RPC
issu_cli_rp2
386 32 261 122 0.00% 0.00% 0.00% 0 RPC
pf_issu_rp2s
387 0 20 0 0.00% 0.00% 0.00% 0 RPC
pf_prst_vbl_
388 0 2 0 0.00% 0.00% 0.00% 0 RPC
pf_redun_rp2
389 3804 56535 67 0.00% 0.00% 0.00% 0 RPC
c6k_power_sp
390 134552 1331856 101 0.00% 0.00% 0.00% 0 RPC
c6k_sp_envir
391 0 19 0 0.00% 0.00% 0.00% 0 PM Vlan Timer
Pr
392 0 1 0 0.00% 0.00% 0.00% 0 pm icc
process
393 12256 85921 142 0.00% 0.00% 0.00% 0 pm scp
process
394 296 1012 292 0.00% 0.00% 0.00% 0 PM CP Process
395 1176 1244 945 0.00% 0.00% 0.00% 0 RPC pm-cp
396 7428 5560564 1 0.00% 0.00% 0.00% 0 PM Callback
397 276 132 2090 0.00% 0.00% 0.00% 0 VLAN Manager
398 0 1 0 0.00% 0.00% 0.00% 0 PM FEC LOAD
SHAR
399 3020 164010 18 0.00% 0.00% 0.00% 0 Port manager
per
400 780 328019 2 0.00% 0.00% 0.00% 0 Max CPU
utilizat
401 0 2 0 0.00% 0.00% 0.00% 0 RPC
pvt_hosts_sw
402 0 2 0 0.00% 0.00% 0.00% 0 RPC
rep_rp2sp_ap
403 8 2 4000 0.00% 0.00% 0.00% 0 SEA main
process
404 0 1 0 0.00% 0.00% 0.00% 0
SeaErrorLogProc
405 1536 164013 9 0.00% 0.00% 0.00% 0 SP Error
Detecti
406 0 2 0 0.00% 0.00% 0.00% 0 RPC
error_detect
407 0 1 0 0.00% 0.00% 0.00% 0
vs_error_detecti
408 0 10 0 0.00% 0.00% 0.00% 0 RPC lcc_rp
409 260 3938 66 0.00% 0.00% 0.00% 0 RPC fabman_rp
410 0 1 0 0.00% 0.00% 0.00% 0 vs_fabman_rp
ICC
411 0 1 0 0.00% 0.00% 0.00% 0
vs_sp_environmen
412 0 2 0 0.00% 0.00% 0.00% 0 RPC
epld_isp_rpc
413 52 604 86 0.00% 0.00% 0.00% 0 RPC
c6k_stack_mi
414 0 2 0 0.00% 0.00% 0.00% 0 RPC chapi_sp
415 0 2 0 0.00% 0.00% 0.00% 0 RPC
const_ehsa_r
416 16 76 210 0.00% 0.00% 0.00% 0 RPC
const_nv_cfg
417 0 2 0 0.00% 0.00% 0.00% 0 RPC
const_platfo
418 28 154 181 0.00% 0.00% 0.00% 0 RPC dot1x_sp
419 4 24 166 0.00% 0.00% 0.00% 0 RPC
gbic_seprom_
420 0 2 0 0.00% 0.00% 0.00% 0 RPC l2_bridge
421 4 20 200 0.00% 0.00% 0.00% 0 RPC
lacp_switch_
422 8 259 30 0.00% 0.00% 0.00% 0 RPC
logging_even
423 12 364 32 0.00% 0.00% 0.00% 0 RPC
mapping_sp
424 0 2 0 0.00% 0.00% 0.00% 0 RPC
online_diag_
425 1984 8429 235 0.00% 0.00% 0.00% 0 RPC
online_diag_
426 0 2 0 0.00% 0.00% 0.00% 0 RPC
online_wan_d
427 868 11689 74 0.00% 0.00% 0.00% 0 RPC
pagp_switch_
428 12 295 40 0.00% 0.00% 0.00% 0 RPC
pikachu_sp
429 0 2 0 0.00% 0.00% 0.00% 0 RPC
pm_mat_mp2sp
430 792 8415 94 0.00% 0.00% 0.00% 0 RPC
pm_switch_rp
431 0 2 0 0.00% 0.00% 0.00% 0 RPC
psecure_sp
432 0 2 0 0.00% 0.00% 0.00% 0 RPC
pt_switch_mp
433 0 2 0 0.00% 0.00% 0.00% 0 RPC
qnq_switch_m
434 328 3068 106 0.00% 0.00% 0.00% 0 RPC
rf_cli_rp2sp
435 0 10 0 0.00% 0.00% 0.00% 0 RPC
span_switch_
436 0 2 0 0.00% 0.00% 0.00% 0 RPC
storm_contro
437 40 518 77 0.00% 0.00% 0.00% 0 RPC
stp_switch_a
438 0 2 0 0.00% 0.00% 0.00% 0 RPC
sw_backup_in
439 1235444 16362525 75 0.31% 0.05% 0.05% 0 RPC
sw_vlan_sp
440 0 2 0 0.00% 0.00% 0.00% 0 RPC
switch_engin
441 0 2 0 0.00% 0.00% 0.00% 0 RPC
ether_oam_rp
442 0 2 0 0.00% 0.00% 0.00% 0 RPC pf_rp_rpc
443 1884 23320 80 0.00% 0.00% 0.00% 0 RPC udld_sp
444 36 522 68 0.00% 0.00% 0.00% 0 RPC
sea_rp_cli_r
445 996 2418 411 0.00% 0.00% 0.00% 0 RPC
sea_console_
446 0 2 0 0.00% 0.00% 0.00% 0 RPC
cap_rpcs_req
447 0 2 0 0.00% 0.00% 0.00% 0 RPC
dot1ad_mp2sp
448 0 1 0 0.00% 0.00% 0.00% 0 VPN_MAPPER
449 0 2 0 0.00% 0.00% 0.00% 0 RPC
vs_prov_lc_s
450 0 1 0 0.00% 0.00% 0.00% 0 vs_pikachu_sp
IC
451 0 1 0 0.00% 0.00% 0.00% 0 vs_power_sp
ICC
452 0 278 0 0.00% 0.00% 0.00% 0 Syslog
453 0 1 0 0.00% 0.00% 0.00% 0 Cap LcCtrl:
SUP
454 0 7 0 0.00% 0.00% 0.00% 0 CMFI
455 20 268 74 0.00% 0.00% 0.00% 0 CMFI Scanner
456 0 3 0 0.00% 0.00% 0.00% 0 CMFI Misc
457 980 165534 5 0.00% 0.00% 0.00% 0 CMFI
Background
458 4 14 285 0.00% 0.00% 0.00% 0 Const2 IPv6
Proc
459 0 1 0 0.00% 0.00% 0.00% 0 v6fib stat
colle
460 0 47 0 0.00% 0.00% 0.00% 0 L2 Manager
Task
461 0 2 0 0.00% 0.00% 0.00% 0 L2 Manager
Earl6
462 0 1 0 0.00% 0.00% 0.00% 0 FPOE DB cc
463 29252 1604602 18 0.00% 0.00% 0.00% 0 LTL MGR
464 774332 493489 1569 0.00% 0.04% 0.05% 0 LTL MGR cc
465 0 2 0 0.00% 0.00% 0.00% 0 REP SP Proc
466 4 52 76 0.00% 0.00% 0.00% 0 SPAN switch
467 0 2 0 0.00% 0.00% 0.00% 0 ERSPAN Switch
SP
468 4 21 190 0.00% 0.00% 0.00% 0 SPAN Switch
SP
469 4216 164007 25 0.00% 0.00% 0.00% 0 SPAN Switch
SP B
470 232 75766 3 0.00% 0.00% 0.00% 0 NDE - IPV4
471 0 1 0 0.00% 0.00% 0.00% 0 NDE - MPLS
472 0 1 0 0.00% 0.00% 0.00% 0 NDE - L2
473 176 61893 2 0.00% 0.00% 0.00% 0 NDE - IPV6
474 724 328019 2 0.00% 0.00% 0.00% 0 SEA write CF
pro
475 0 1 0 0.00% 0.00% 0.00% 0 SEA write
messag
476 0 1 0 0.00% 0.00% 0.00% 0 SEA receive
proc
477 18068 164012 110 0.00% 0.00% 0.00% 0 TM Stat Adj
Task
478 164 497 329 0.00% 0.00% 0.00% 0 OBFL UPTIME
obfl
479 2020 176498 11 0.00% 0.00% 0.00% 0 IP Flow XDR
LC B
480 106192 11464473 9 0.00% 0.00% 0.00% 0 SCP async:
LCP#5
481 448 5652 79 0.00% 0.00% 0.00% 0 Collection
proce
482 1024 109343 9 0.00% 0.00% 0.00% 0 OBFL I/O
Buffer
483 97028 2462619 39 0.07% 0.00% 0.00% 0 CEF: IPv4
proces
484 24 52 461 0.00% 0.00% 0.00% 0 ADJ
background
485 46500 3139966 14 0.00% 0.00% 0.00% 0 SCP async:
LCP#3
486 39980 2459818 16 0.00% 0.00% 0.00% 0 SCP async:
LCP#2
487 56 373 150 0.00% 0.00% 0.00% 0 SpanTree
Helper
488 324 1166 277 0.00% 0.00% 0.00% 0 SpanTree
Flush
489 84 101 831 0.47% 0.05% 0.01% 1 Virtual Exec
-DIST65-01.TC1-sp#sh proc cpu history
1111111222221111 1111122222 1111111111111111111111
6611111000008888999991111155555888888888855555666666666688
100
90
80
70
60
50
40
30 *****
20 ** ********* ***** **********************
10 **********************************************************
0....5....1....1....2....2....3....3....4....4....5....5....
0 5 0 5 0 5 0 5 0 5
CPU% per second (last 60 seconds)
2222223222222222222122222222322222222222222222222322223222
1488822275624423487988449665055553432852248556623085385821
100
90
80
70
60
50
40 *
30 *** * *** ** ** ********* ** ***** *** ***
20 ##############################################*###
10 ##########################################################
0 5 0 5 0 5 0 5 0 5
CPU% per minute (last 60 minutes)
  • = maximum CPU% # = average CPU%
3333333333335343333333333333343333333333333333333333333334345453334333
9443168692511174443553424749502421714421416525863461264254223309512555
100
90
80
70
60
50 * * * *
40 * **** * * * ** * *** * ** *** * * ** ****** ****
30 **********************************************************************
20 ######################################################################
10 ######################################################################
0....5....1....1....2....2....3....3....4....4....5....5....6....6....7.
0 5 0 5 0 5 0 5 0 5 0 5 0
CPU% per hour (last 72 hours)
-DIST65-01.TC1-sp#sh proc cpu | exclude 0.00
CPU utilization for five seconds: 8%/0%; one minute: 15%; five minutes: 15%
3 36560880 33874681 1079 2.39% 2.19% 2.20% 0 DiagCard1/-1
77 2686244 20976927 128 0.07% 0.17% 0.16% 0 SCP Download
Lis
106 103749056 197866803 524 3.91% 6.22% 6.35% 0 slcp process
109 13364996 7258998 1841 0.15% 1.18% 1.02% 0 DiagCard2/-1
249 27680796 700097 39538 1.67% 1.69% 1.68% 0 Vlan
Statistics
282 627372 8004433 78 0.07% 0.05% 0.05% 0 Spanning Tree
464 774344 493501 1569 0.07% 0.03% 0.05% 0 LTL MGR cc
489 120 160 750 0.07% 0.06% 0.02% 1 Virtual Exec
thanks
Vinu
On Wed, Mar 17, 2010 at 4:03 PM, giuslar
Jan Nejman Wed, 03/17/2010 - 09:17
Hello kumar,
  it looks that your switch processor is OK. The problem will be probably with rate limiters.
Could you send me "show mls statistics" and "show mls rate-limit usage"?
Jan
vinoth.kumar Wed, 03/17/2010 - 09:24
Thanks for your reply
-DIST65-01.TC1#sh fabric utilization detail
Fabric utilization: Ingress Egress
Module Chanl Speed rate peak rate peak
1 0 20G 0% 0% 0% 1% @14:00
17Mar10
1 1 20G 0% 1% @13:11 05Mar10 0% 1% @12:36
17Mar10
5 0 20G 0% 1% @12:06 17Mar10 0% 1% @15:33
28Feb10
-DIST65-01.TC1#sh mls statistics
Statistics for Earl in Module 1
L2 Forwarding Engine
Total packets Switched : 60578204
L3 Forwarding Engine
Total packets Processed : 973227 @ 0 pps
Total packets L3 Switched : 22011 @ 0 pps
Total Packets Bridged : 17087
Total Packets FIB Switched : 22010
Total Packets ACL Routed : 0
Total Packets Netflow Switched : 1
Total Mcast Packets Switched/Routed : 376995
Total ip packets with TOS changed : 2
Total ip packets with COS changed : 2
Total non ip packets COS changed : 0
Total packets dropped by ACL : 0
Total packets dropped by Policing : 0
Total packets exceeding CIR : 0
Total packets exceeding PIR : 0
Errors
MAC/IP length inconsistencies : 0
Short IP packets received : 0
IP header checksum errors : 0
TTL failures : 0
MTU failures : 0
Statistics for Earl in Module 5
Total packets Switched : 24013162954
Total packets Processed : 24003699023 @ 20538 pps
Total packets L3 Switched : 23632264616 @ 20229 pps
Total Packets Bridged : 291999460
Total Packets FIB Switched : 23632264616
Total Packets Netflow Switched : 0
Total Mcast Packets Switched/Routed : 19911908
Total packets dropped by ACL : 154
Errors
TTL failures : 198758
MTU failures : 0
Total packets L3 Processed by all Modules: 24004672250 @ 20538 pps
-DIST65-01.TC1#sh mls rate-limit usage
Rate Limiter Type Packets/s Burst
Jan Nejman Wed, 03/17/2010 - 09:35
   the box is transfering only around 20k pps. I suppose that at this time is the box OK.
I have not any idea where is the problem at this moment. Try check the statistic as soon
as the problem occurs again. Did you tried to remove "rate-limiters" when you have troubles?
Jan
vinoth.kumar Thu, 03/18/2010 - 03:43
Since our traffic between sites are mostly 90 % pointed as unicast
for example
from site 1 - 10.109.2.3
to site 2 - 10.107.2.3
we suspecting the problem could be the configuration based on the mls
unicast
kindly find the interface details and advice me in case of any issue
Hardware is EtherSVI, address is 0014.1b44.5c0a (bia 0014.1b44.5c0a)
Description: VLAN-CONNtoWAN_S/W
Internet address is 10.207.2.1/29
MTU 1500 bytes, BW 1000000 Kbit, DLY 10 usec,
reliability 255/255, txload 128/255, rxload 138/255
Keepalive not supported
Last input 00:00:00, output 00:01:06, output hang never
Last clearing of "show interface" counters 2d20h
Input queue: 0/75/38/38 (size/max/drops/flushes); Total output drops: 0
Queueing strategy: fifo
Output queue: 0/40 (size/max)
5 minute input rate 544561000 bits/sec, 384371 packets/sec
5 minute output rate 576551000 bits/sec, 409327 packets/sec
L2 Switched: ucast: 489568 pkt, 32212571 bytes - mcast: 818 pkt, 66204
bytes
L3 in Switched: ucast: 70386284274 pkt, 12835184566001 bytes - mcast: 0
pkt, 0
bytes mcast
L3 out Switched: ucast: 72218893515 pkt, 12923218491182 bytes
70391256862 packets input, 12836057109266 bytes, 0 no buffer
Received 406 broadcasts (0 IP multicasts)
72220103421 packets output, 12923392656634 bytes, 0 underruns
0 output errors, 0 interface resets
but we experienced issue in the traffic connecting one way and another path
is fine which u can see the traffic packet difference in the interface
thanks
vinoth
On Wed, Mar 17, 2010 at 5:35 PM, vinoth kumar harikrishnan <
Jan Nejman Thu, 03/18/2010 - 08:08
Hi Vinoth,
  the interface status looks OK. There are no output drops, no corrupted packets.
I think that you can solve this problem only when the problem occurs again. I haven't
any idea how to solve the problem at this time. I recommend to check routing
information (OSPF, BGP, static?), logging, mls status as soon as the problem
occurs again. Maybe someone else can help you earlier, but your interface status
looks OK from my side.
Jan
vinoth.kumar Wed, 03/24/2010 - 12:31
Hi Thanks for reply
we some how found this could be the cause for belwo issue
currently we had 2 port channel group on the same switch port channel 1 and
port channel 1 is traffic coming IN around 650mb and module 4 port 13-20
port-channel 10 is traffic OUT to the other switch shared by 2 line card so
its 325 module 4 port 11 12 and module 3 port 11 and 12
at this point we are using 6148 line card which can only support up to 1 gig
of etherchannel throughput ASCI (by cisco refernce ) if we use the multiple
port-channel group also
if this true we might seen almost 975mb to 1Gig of traffic on that peak time
in Etherchannel ACSI which might leads to packet drop at that moment
what is mean by etherchannel ASCI ?
kindly need your advice
thanks
Vinoth kumar
On Thu, Mar 18, 2010 at 3:08 PM, [email protected] <
Giuseppe Larosa Wed, 03/24/2010 - 13:37
  • Hall of Fame,
    Founding Member
Hello Vinoth,
the 6148 linecard is oversubscribed 8:1 this means that 8 ports share a common 1 Gbps capable ASIC (custom chip).
This is not related to the use of port channels and can be the reason of the problems you see rather then the use of sup720.
see
http://www.cisco.com/en/US//products/hw/switches/ps700/products_tech_note09186a00801751d7.shtml#ASIC
Hope to help
Giuseppe
vinoth.kumar Wed, 03/24/2010 - 23:43
Thanks a lot for your information
Iam seeing some output drops
6506-SW-A#$ interface gigabitEthernet 4/11 | include qos3Outlost
53. qos3Outlost = 837682147
6506-SW-A#$ interface gigabitEthernet 4/12 | include qos3Outlost
6506-SW-A#$ interface gigabitEthernet 4/13 | include qos3Outlost
6506-SW-A#$ interface gigabitEthernet 4/14 | include qos3Outlost
6506-SW-A#$ interface gigabitEthernet 4/15 | include qos3Outlost
6506-SW-A#$ interface gigabitEthernet 4/16 | include qos3Outlost
6506-SW-A#$ interface gigabitEthernet 4/17 | include qos3Outlost
53. qos3Outlost = 14694
6506-SW-A#$ interface gigabitEthernet 4/18 | include qos3Outlost
6506-SW-A#$ interface gigabitEthernet 4/19 | include qos3Outlost
6506-SW-A#$ interface gigabitEthernet 4/20 | include qos3Outlost
vinu
On Wed, Mar 24, 2010 at 8:37 PM, giuslar