FCoE Multihop Performance Issue
Answered Question
Dec 20th, 2012
  • Silver, 250 points or more
Has anyone out there implemented FCoE multihop on the new 2.1 firmware? I moved my lab UCS over to it and storage performance tanked. Here is what I have in my lab.
2 Nexus 5500s - used for both LAN and FC switching
EMC CX4-120 - connected to the 2 Nexus 5500s
UCS 6120/FEX 2104 - Pre-FCoE setup was a 2 port SAN port-channel in each fabric to the Nexus 5ks.
6 B200 M1 servers
ESXi 5
I cabled up an addition twinax on Fabric Interconnect A to Nexus 5548 in FC Fabric A
I cabled up an addition twinax on Fabric Interconnect B to Nexus 5548 in FC Fabric B
Configured the interfaces as FCoE uplink in UCS
Placed the FCoE interfaces in the appropriate VSAN
One fabric at a time I disabled the FC SAN port-channel to force the vHBAs to login over the FCoE uplink. Didn't have any issues with this and vHBAs showed up in the flogi table of the Nexus 5ks on the correct vfc interface.
Rebooted my ESXi hosts (boot from SAN) and the hosts rebooted fine using the FCoE uplinks to the Nexus 5ks.
When I powered on a VM it took over 20 minutes for it to boot and it never got to the point where it was usable.
No drops or errors on the FCoE or vfc interfaces of the Fabric Interconnects and Nexus 5ks.
As soon as I re-enabled the FC SAN port-channels using 4GB SFPs and disable the FCoE uplink performance was fine again.
I am hoping this is something to do with the older gen 1 hardware of 6100s and IOM 2100s and not a bug.
I have 2 other HP rack mount servers with Qlogic CNAs doing FCoE to the same VMFS LUNs with no issues.
Correct Answer by Adi Arslanagic about 4 years 4 months ago
Case ID: 624922297
Both Nexus switches and UCSM tech support are attached.
Endorsed by Robert Burns
Jeremy Waldrop about 4 years 2 months ago
I figured out my performance issue with using multi-hop FCoE from UCS to Nexus 5k.
We have our UCS QoS System Classes changed from the default of best effort 50 and FC 50. We are using the other classes to place some barriers around traffic like vMotion and to give VM network traffic and NFS traffic guaranteed percentages.
On the Nexus 5k side we had the default QoS of 50/50 configured.
To test I reset UCS back to the defaults and then my performance issue went away. The miss-match in QoS between UCS and Nexus 5k was causing the issue.
I then went back and enabled one QoS system class at a time to see which one was causing the issue. When I enabled the Platinum system class I immediatly started noticing a performance issue access storage. The platinum class was being used for IP storage and has no-drop configured.
I can't find anywhere that this is documented but it looks like having no-drop configured on 2 different qos groups at the same time it causes issues.
Here is a screen shot of the QoS system class configuration that works with FCoE
vMotion is mapped to Best Effort
ESXi Mgmt is mapped to Silver
VM traffic is mapped to Gold
I don't really need a QoS policy or vNICs for IP Storage but if I did I would enable packet drop on Platinum and map the NFS/iSCSI vNICs to Platinum.
Overall Rating: 5 (6 ratings)
vek64gware Thu, 12/20/2012 - 18:51
I see some perfomance degradation also, when i switch to FCoE path to Netapp.
But not that drastic as yours.
I have 3 years old chassis with 200 gen 1 and old adapter in it.
Then - 2104, 6120 and 5010 upstream.
Netapp with FCoe cards is connected to 5010.
Cables are twinax.
I have M200gen3 with VIC1280 to play with.
Will try to see if it's gioing to do better.
Jeremy Waldrop Fri, 12/21/2012 - 03:49
So it sounds like there could be an issue with GEN 1 hardware and FCoE multihop. Anyone out there have GEN 2 hardware they can test this with?
Hello Jeremy,
we are ready to test multihop FCoE with gen2 card (M81KR, VIC1240, IOM2104, FI 6248UP, Nexus5548UP, Win2008 on bare metal, NetApp storage, UCS2.11a).
But first, please, can you explain to me exactly where/how I can configure FCoE northbound ?
I have vPC from both FIs to a pair of N5Ks and of course separate native FC link between each pair of FI and N5K.
With Multihop FCoE feature introduced in 2.1 version – is there any way  to get rid of this native FC link and have FCoE northbound (FI to N5K)  USING ONE LINK OF THE EXISTING vPC?
From the nexus side, it allows me to have one more vlan in one link southbound of a vPC for vsan traffic. But it seems, that on FI I cannot have unified ports in portchannel (vPC) northbound to N5K (or exactly - one unified port straight from "left" FI to "left" N5K and uplink port from "left" FI to "right" N5K and both ports on FI in portchannel - vPC from N5Ks perspective).
Obviously, another way is to add separate ethernet links (between FI and  N5K) and make them unified northbound ... but I still believe I am doing some mistake and FCoE northbound should work in existing vPC to N5K.
Thank you for any comments.
Pavel
Jeremy Waldrop Thu, 01/24/2013 - 13:50
Yes, you can configure the existing uplink port as a Unified Port by also making it an FCoE uplink port. You could do this to one link on each FI and then map the appropriate VSAN. To migrate admin down the regular FC uplinks one fabric at a time and the server vHBA will perform a flogi across the FCoE uplink.
I have tested this and have tested it using a dedicate FCoE uplink, both tests resulted in very poor SAN peformance in my lab. Not sure if it is the gen 1 hardware or something else.
Adi Arslanagic Thu, 02/21/2013 - 01:29
I've run into the same problem and it is almost identical configuration:
2x Nexus 5548UP
2x UCS 6248UP
Cisco VIC1240 adapters
2x 8Gb native FC uplinks (storage also connected via 2x 8Gb native FC to both nexus switches)
After switching from native FC Uplinks to FCoE Uplinks (2x 10G twinax port-channeled) storage performance is severly degraded, unusable.
Also I see no errors or drops on fcoe ethernet or vfc interfaces, but there are packets discarded on input:
nexus-sw1# show queuing interface ethernet 1/5
Ethernet1/5 queuing information:
  TX Queuing
    qos-group  sched-type  oper-bandwidth
        0       WRR             50
        1       WRR             50
  RX Queuing
    qos-group 0
    q-size: 360960, HW MTU: 9216 (9216 configured)
    drop-type: drop, xon: 0, xoff: 360960
    Statistics:
        Pkts received over the port             : 0
        Ucast pkts sent to the cross-bar        : 0
        Mcast pkts sent to the cross-bar        : 0
        Ucast pkts received from the cross-bar  : 0
        Pkts sent to the port                   : 0
        Pkts discarded on ingress               : 0
        Per-priority-pause status               : Rx (Inactive), Tx (Inactive)
    qos-group 1
    q-size: 79360, HW MTU: 2158 (2158 configured)
    drop-type: no-drop, xon: 20480, xoff: 40320
    Statistics:
        Pkts received over the port             : 809739
        Ucast pkts sent to the cross-bar        : 743529
        Ucast pkts received from the cross-bar  : 67599
        Pkts sent to the port                   : 67599
        Pkts discarded on ingress               : 66210
  Total Multicast crossbar statistics:
    Mcast pkts received from the cross-bar      : 0
So I would rule out the gen 1 hardware problem.. have you managed to make it work?
Best Regards,
Adi
Jeremy Waldrop Thu, 02/21/2013 - 07:26
No, I haven't been able to make it work so that it is usable. I can get my ESXi host to boot from SAN over FCOE but when I power on a VM it takes 20 minutes to boot it.
dfilenko Fri, 02/22/2013 - 11:56
  • Cisco Employee,
When configuring FCoE from UCS to N5K, vPC can not be used for FCoE traffic. Also cos markings for FCoE traffic should match between N5K and UCS.
Adi Arslanagic Fri, 02/22/2013 - 12:44
Hi Dmitri,
in my case vPC is used, but only for LAN traffic. There is a separate port-channel between nexus and FI only for FCoE SAN traffic, and only allowed vlan on the link (on the nexus) is 981 which maps to vsan 10 (SAN A).
Adi
dfilenko Fri, 02/22/2013 - 12:47
  • Cisco Employee,
In this case, are you using uplink manager to create disjoined L2 configuration on UCS side? By default, all UCS uplinks allowing all vlans, so it's possible for vfc to get mapped to vPC port channel.
Adi Arslanagic Fri, 02/22/2013 - 13:21
I have configured Ethernet 1/5-6 on both FIs as FCoE uplink interfaces, then on the SAN tab added them to FCoE Port Channel and assigned to VSAN 10 and 20 respectfully.
Here is the show run int po201 from FI-A nxos:
!Command: show running-config interface port-channel201
!Time: Fri Feb 22 21:57:34 2013
version 5.0(3)N2(2.11a)
  description C: FcoeUplink
  shutdown
  switchport mode trunk
  pinning border
  switchport trunk native vlan 4049
  switchport trunk allowed vlan 981-982,4048-4049
  speed 10000
dfilenko Fri, 02/22/2013 - 13:55
  • Cisco Employee,
Adi,
Can you please provide output of:
From UCS:
(nxos)# show vifs interface port-channel201
(nxos)# show running-config interface vfc
(nxos)# show int vfc
From UCS and Nexus:
(nxos)# show class-map type qos
(nxos)# show policy-map type qos
(nxos)# show class-map type queuing
(nxos)# show class-map type network-qos
(nxos)# show policy-map type network-qos
Adi Arslanagic Fri, 02/22/2013 - 14:18
Dmitri,
here is the output
UCS show commands output:
DC-eVlada-A(nxos)# show vifs interface port-channel 201
Interface      MAX-VIFS VIFS
Po201          0        vfc821,
DC-eVlada-A(nxos)# show running-config interface vfc821
!Command: show running-config interface vfc821
!Time: Fri Feb 22 22:51:21 2013
interface vfc821
  bind interface port-channel201
  switchport mode NP
DC-eVlada-A(nxos)# sh int vfc821
vfc821 is down (Administratively down)
    Bound interface is port-channel201
    Hardware is Virtual Fibre Channel
    Port WWN is 23:34:54:7f:ee:ab:d1:3f
    Admin port mode is NP, trunk mode is on
    snmp link state traps are enabled
    Port vsan is 10
    1 minute input rate 0 bits/sec, 0 bytes/sec, 0 frames/sec
    1 minute output rate 0 bits/sec, 0 bytes/sec, 0 frames/sec
      20995367 frames input, 34899127788 bytes
        0 discards, 0 errors
      9188891 frames output, 14893075816 bytes
    last clearing of "show interface" counters never
    Interface last changed at Wed Feb 20 19:42:34 2013
DC-eVlada-A(nxos)# show class-map type qos
  Type qos class-maps
    class-map type qos match-any class-fcoe
      match cos 3
    class-map type qos match-any class-default
      match any
    class-map type qos match-any class-all-flood
      match all flood
    class-map type qos match-any class-ip-multicast
      match ip multicast
DC-eVlada-A(nxos)# show policy-map type qos
  Type qos policy-maps
  policy-map type qos default-in-policy
    class type qos class-default
      set qos-group 0
  policy-map type qos system_qos_policy
    class type qos class-fcoe
      set qos-group 1
      set qos-group 0
  policy-map type qos fcoe-default-in-policy
      set qos-group 1
      set qos-group 0
DC-eVlada-A(nxos)#
DC-eVlada-A(nxos)# show class-map type queuing
  Type queuing class-maps
    class-map type queuing class-fcoe
      match qos-group 1
    class-map type queuing class-default
      match qos-group 0
    class-map type queuing class-all-flood
      match qos-group 2
    class-map type queuing class-ip-multicast
      match qos-group 2
DC-eVlada-A(nxos)#
DC-eVlada-A(nxos)# show class-map type network-qos
  Type network-qos class-maps
    class-map type network-qos class-fcoe
      match qos-group 1
    class-map type network-qos class-default
      match qos-group 0
    class-map type network-qos class-all-flood
      match qos-group 2
    class-map type network-qos class-ip-multicast
      match qos-group 2
DC-eVlada-A(nxos)# show policy-map type network-qos
  Type network-qos policy-maps
  policy-map type network-qos system_nq_policy
    class type network-qos class-fcoe
      pause no-drop
      mtu 2158
    class type network-qos class-default
      pause drop
      mtu 9000
  policy-map type network-qos default-nq-policy
      pause drop
      mtu 1500
      multicast-optimize
  policy-map type network-qos fcoe-default-nq-policy
      pause no-drop
      mtu 2158
      pause drop
      mtu 1500
      multicast-optimize
DC-eVlada-A(nxos)#
Nexus show commands output:
DC-nexus-sw1# show class-map type qos
  Type qos class-maps
      match cos 3
      match any
      match all flood
      match ip multicast
DC-nexus-sw1# show policy-map type qos
      set qos-group 0
      set qos-group 1
      set qos-group 0
DC-nexus-sw1#
DC-nexus-sw1# show class-map type queuing
      match qos-group 1
      match qos-group 0
      match qos-group 2
      match qos-group 2
DC-nexus-sw1#
DC-nexus-sw1# show class-map type network-qos
      match qos-group 1
      match qos-group 0
      match qos-group 2
      match qos-group 2
DC-nexus-sw1# show policy-map type network-qos
  policy-map type network-qos jumbo-frames
      pause no-drop
      mtu 2158
      mtu 9216
      multicast-optimize
      mtu 1500
      multicast-optimize
      pause no-drop
      mtu 2158
      mtu 1500
      multicast-optimize
DC-nexus-sw1#
dfilenko Fri, 02/22/2013 - 14:32
  • Cisco Employee,
This looks correct. Please open case with TAC to find out reason for packet drops on N5K interfaces.
dfilenko Fri, 02/22/2013 - 14:36
  • Cisco Employee,
Do you have case number handy? Does it have N5K and UCSM techsupports attached?
Correct Answer
Adi Arslanagic Fri, 02/22/2013 - 14:38
Case ID: 624922297
dfilenko Fri, 02/22/2013 - 15:01
  • Cisco Employee,
Thank Adi. I will take a look if I have time.
Can you please also provide output of the following from N5K ?
show platform fwm info asic-errors 0
this output shows reasons for drops, and it would be good to see what number is incrementing when fcoe uplink is enabled.
Adi Arslanagic Sat, 02/23/2013 - 01:00
Thanks for help.
Here is the output:
DC-nexus-sw1# show platform fwm info asic-errors 0
Printing non zero Carmel error registers:
DROP_SRC_VLAN_MBR: res0 = 2845053 res1 = 0 [12]
DROP_INVALID_FCF_BYPASS: res0 = 22 res1 = 0 [24]
DROP_FCF_SW_TBL_MISS: res0 = 470 res1 = 0 [25]
DROP_FCF_FC_SW_SHOULD_NOT_BE_ME: res0 = 80 res1 = 0 [27]
DROP_SHOULD_HAVE_INT_MULTICAST: res0 = 226 res1 = 0 [36]
DROP_VLAN_MASK_TO_NULL: res0 = 488 res1 = 0 [39]
DROP_SRC_MASK_TO_NULL: res0 = 93135 res1 = 0 [44]
DROP_INGRESS_ACL: res0 = 910 res1 = 0 [46]
DC-nexus-sw2# show platform fwm info asic-errors 0
DROP_SRC_VLAN_MBR: res0 = 2915122 res1 = 0 [12]
DROP_INVALID_FCF_BYPASS: res0 = 21 res1 = 0 [24]
DROP_FCF_SW_TBL_MISS: res0 = 376 res1 = 0 [25]
DROP_FCF_FC_SW_SHOULD_NOT_BE_ME: res0 = 81 res1 = 0 [27]
DROP_SHOULD_HAVE_INT_MULTICAST: res0 = 15 res1 = 0 [36]
DROP_VLAN_MASK_TO_NULL: res0 = 487 res1 = 0 [39]
DROP_SRC_MASK_TO_NULL: res0 = 99962 res1 = 0 [44]
DROP_INGRESS_ACL: res0 = 16 res1 = 0 [46]
I can not activate FCoE uplinks since this is production enviroment.
Jeremy Waldrop Wed, 02/27/2013 - 11:14
Adi, any updates on the TAC case you have open?
Adi Arslanagic Thu, 02/28/2013 - 00:55
Hi Jeremy,
TAC said that we need to turn on the FCoE Uplinks to do troubleshooting but we were unable to since this is now a production enviroment :\.
They also suggested that Cisco HBA driver on the Win2012 server is a bit out of date and we should try to update it and test again with disk performance monitoring but we haven't been able to schedule it yet.
Have you raised a TAC case about this issue?
Adi
Jeremy Waldrop Fri, 02/22/2013 - 13:46
I have 2 dedicated 10G uplinks for FCoE in a SAN Port-channel. Functionally it works fine and my ESXi hosts boot from SAN just fine over FCoE. When I power a single VM on it takes 20 minutes for it to boot and it is unusable, no errors on any interfaces. If I disable the FCoE port channel and enable the traditional FC san-port-channel performance is great.
I have a vPC setup but that is just for Ethernet LAN uplinks.
Here is my Nexus 5k side config for fabric A, Fabric B is simlar except for the VSAN/VLANVFC numbers
In UCS I have VSAN 20 mapped to FCOE VLAN 3020 on A and VSAN 40 is mapped to FCOE VLAN 3020 on Fabric B.
With this config all ESXi vhba initiators flogi over the vfc8 interface on Fabric A and vfc9 interface on Fabric B. I can access my VMFS LUNs and it is all functional just very poor performance.
vlan 3020
  fcoe vsan 20
interface port-channel8
  description UCS Fabric A fcoe e1/31-32
  switchport trunk allowed vlan 3020
  spanning-tree port type edge trunk
  speed 10000
interface Ethernet1/17
  channel-group 8 mode active
interface Ethernet1/18
  description UCS Fabric A fcoe e1/32
interface vfc8
   switchport description UCS Fabric FCOE
   bind interface port-channel8
dfilenko Fri, 02/22/2013 - 14:35
  • Cisco Employee,
Jeremy,
I would recommend to open support case with TAC to analyze config. If you have FCoE  drops in the path, it would explain slowness of connectivity.
Jeremy Waldrop Sun, 03/31/2013 - 13:58
Robert Burns Mon, 04/01/2013 - 04:59
  • Cisco Employee,
Thanks for the great follow up Jeremy.  Hopefully this helps someone down the road if they encounter a similar issue.
Keep up the great work!
Robert
Adi Arslanagic Tue, 04/02/2013 - 04:24
Great find, thanks for updating the thread Jeremy!
Now that I think about it we also had mismatch between UCS and Nexus qos weights, guess that could have been the problem. We went with the native FC uplinks but this is good to know!
Adi
Ivan Kovacevic Fri, 06/28/2013 - 13:14
  • Cisco Employee,
This explanation is actually a bit misleading.
The issue is actually caused by a miss-match between UCS FI and N5k QoS config. Enabling "Platinum" class on UCS which is by default configured d no-drop class and leaving default N5k QoS config will cause DCBX negotiation to fail on the 10G between FI and N5k. This means that PFC will become disabled on for the "Fibre Channel" class as well, which means FCoE frames will be dropped and pause-frames will not be honored.
The correct recommendation is to keep the QoS config consistent end-to-end on all datacenter switches along the FCoE path.
Related Content