Warning message
POE Module goes into shutdown
Jul 8th, 2014
I'm facing an issue with two 4500 switches. It gives the following error " %C4K_ETHPOE-4-SUPPLYFAULT: Module 8 POE controller has been shutdown because of excessive power usage.". First all the line cards will go into  shutdown mode then recover but one of the POE modules does not recover from the shutdown. Need to know what could be causing this issue.
Thanks !!!
Hatim Janjali
Leo Laohoo Tue, 07/08/2014 - 15:20
  • Hall of Fame,
    The Hall of Fame designation is a lifetime achievement award based on significant overall achievements in the community.
  • Cisco Designated VIP,
    2017 LAN, Wireless
Your PS does not have enough "juice" to supply PoE to the line cards.
Post the complete output to the command "sh power inline" and "sh environment".
hjanjali1 Wed, 07/09/2014 - 02:21
 Hi Leo,
Posting the output below.
EON_SEZ_F1_4510_AS02#sh environ
no temperature alarms
Module Sensor                     Temperature          Status
1      Air inlet                  30C (56C,68C,71C)              ok
1      Air inlet remote           21C (46C,59C,62C)              ok
1      Air outlet                 33C (66C,76C,79C)              ok
1      Air outlet remote          26C (60C,71C,74C)              ok
2      Air inlet                  29C (56C,68C,71C)              ok
2      Air inlet remote           21C (46C,59C,62C)              ok
2      Air outlet                 32C (66C,76C,79C)              ok
2      Air outlet remote          25C (60C,71C,74C)              ok
3      Air inlet                  28C (56C,68C,71C)              ok
3      Air inlet remote           20C (46C,59C,62C)              ok
3      Air outlet                 31C (66C,76C,79C)              ok
3      Air outlet remote          25C (60C,71C,74C)              ok
4      Air inlet                  29C (56C,68C,71C)              ok
4      Air inlet remote           21C (46C,59C,62C)              ok
4      Air outlet                 31C (66C,76C,79C)              ok
4      Air outlet remote          25C (60C,71C,74C)              ok
5      Stub A                     30C (58C,71C,74C)              ok
5      Stub B                     22C (54C,68C,71C)              ok
5      XPP                        43C (67C,81C,84C)              ok
5      VFE                        50C (79C,90C,93C)              ok
5      NFE                        38C (68C,80C,83C)              ok
5      CPU                        43C (69C,83C,86C)              ok
5      FPGA                       33C (57C,71C,74C)              ok
6      Stub A                     30C (58C,71C,74C)              ok
6      Stub B                     24C (54C,68C,71C)              ok
6      XPP                        44C (67C,81C,84C)              ok
6      VFE                        51C (79C,90C,93C)              ok
6      NFE                        39C (68C,80C,83C)              ok
6      CPU                        44C (69C,83C,86C)              ok
6      FPGA                       31C (57C,71C,74C)              ok
7      Air inlet                  29C (56C,68C,71C)              ok
7      Air inlet remote           20C (46C,59C,62C)              ok
7      Air outlet                 30C (66C,76C,79C)              ok
7      Air outlet remote          25C (60C,71C,74C)              ok
8      Air inlet                  27C (56C,68C,71C)              ok
8      Air inlet remote           18C (46C,59C,62C)              ok
8      Air outlet                 28C (66C,76C,79C)              ok
8      Air outlet remote          20C (60C,71C,74C)              ok
9      air inlet                  21C (41C,56C,66C)              ok
9      air outlet                 25C (50C,64C,74C)              ok
10     air inlet                  22C (41C,56C,66C)              ok
10     air outlet                 27C (50C,64C,74C)              ok
Power                                             Fan      Inline
Supply  Model No          Type       Status       Sensor   Status
PS1     PWR-C45-6000ACV   AC 6000W   good         good     good
PS1-1                         220V   good
PS1-2                         220V   good
PS2     PWR-C45-6000ACV   AC 6000W   good         good     good
PS2-1                         220V   good
PS2-2                         220V   good
Power supplies needed by system    : 1
Power supplies currently available : 2
Chassis Type : WS-C4510R+E
Power consumed by backplane : 40 Watts
Switch Bandwidth Utilization : 0%
Supervisor Led Color : Green
Module  1 Status Led Color  : Green           PoE Led Color : Green
Module  2 Status Led Color  : Green           PoE Led Color : Green
Module  3 Status Led Color  : Green           PoE Led Color : Green
Module  4 Status Led Color  : Green           PoE Led Color : Green
Module  5 Status Led Color  : Green
Module  6 Status Led Color  : Green
Module  7 Status Led Color  : Green           PoE Led Color : Green
Module  8 Status Led Color  : Green           PoE Led Color : Green
Module  9 Status Led Color  : Green
Module 10 Status Led Color  : Green
Fantray : Good
Fantray removal timeout : 30
Power consumed by Fantray : 255 Watts
EON_SEZ_F1_4510_AS02#sh power inlin
Available:4592(w)  Used:1075(w)  Remaining:3517(w)
Interface Admin  Oper            Power(Watts)     Device              Class
                            From PS    To Device
Gi1/1     auto   off        0.0        0.0        n/a                 n/a
Gi1/2     auto   on         7.4        7.0        Ieee PD             2
Gi1/3     auto   on         6.3        6.0        IP Phone 6921       2
Gi1/4     auto   off        0.0        0.0        n/a                 n/a
Gi1/5     auto   off        0.0        0.0        n/a                 n/a
Gi1/6     auto   on         6.3        6.0        IP Phone 6921       2
Gi1/7     auto   on         6.3        6.0        IP Phone 6921       2
Gi1/8     auto   on         6.3        6.0        IP Phone 6921       2
Gi1/9     auto   on         6.3        6.0        IP Phone 6921       2
Gi1/10    auto   on         6.6        6.3        IP Phone 6921       2
Gi1/11    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/12    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/13    auto   off        0.0        0.0        n/a                 n/a
Gi1/14    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/15    auto   off        0.0        0.0        n/a                 n/a
Gi1/16    auto   off        0.0        0.0        n/a                 n/a
Gi1/17    auto   off        0.0        0.0        n/a                 n/a
Gi1/18    auto   on         6.3        6.0        IP Phone 6921       2
                            From PS    To Device
Gi1/19    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/20    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/21    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/22    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/23    auto   off        0.0        0.0        n/a                 n/a
Gi1/24    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/25    auto   off        0.0        0.0        n/a                 n/a
Gi1/26    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/27    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/28    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/29    auto   off        0.0        0.0        n/a                 n/a
Gi1/30    auto   off        0.0        0.0        n/a                 n/a
Gi1/31    auto   off        0.0        0.0        n/a                 n/a
Gi1/32    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/33    auto   off        0.0        0.0        n/a                 n/a
Gi1/34    auto   off        0.0        0.0        n/a                 n/a
Gi1/35    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/36    auto   off        0.0        0.0        n/a                 n/a
Gi1/37    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/38    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/39    auto   off        0.0        0.0        n/a                 n/a
Gi1/40    auto   off        0.0        0.0        n/a                 n/a
                            From PS    To Device
Gi1/41    auto   off        0.0        0.0        n/a                 n/a
Gi1/42    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/43    auto   off        0.0        0.0        n/a                 n/a
Gi1/44    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/45    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/46    auto   on         6.3        6.0        IP Phone 6921       2
Gi1/47    auto   on         16.2       15.4       AIR-CAP3502I-N-K9   3
Gi1/48    auto   on         15.8       15.0       AIR-LAP1141N-A-K9   3
Gi2/1     auto   on         6.3        6.0        IP Phone 6921       2
Gi2/2     auto   on         6.3        6.0        IP Phone 6921       2
Gi2/3     auto   on         6.3        6.0        IP Phone 6921       2
Gi2/4     auto   on         6.3        6.0        IP Phone 6921       2
Gi2/5     auto   on         6.3        6.0        IP Phone 6921       2
Gi2/6     auto   on         6.3        6.0        IP Phone 6921       2
Gi2/7     auto   off        0.0        0.0        n/a                 n/a
Gi2/8     auto   off        0.0        0.0        n/a                 n/a
Gi2/9     auto   off        0.0        0.0        n/a                 n/a
Gi2/10    auto   off        0.0        0.0        n/a                 n/a
Gi2/11    auto   off        0.0        0.0        n/a                 n/a
Gi2/12    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/13    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/14    auto   off        0.0        0.0        n/a                 n/a
                            From PS    To Device
Gi2/15    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/16    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/17    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/18    auto   off        0.0        0.0        n/a                 n/a
Gi2/19    auto   off        0.0        0.0        n/a                 n/a
Gi2/20    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/21    auto   off        0.0        0.0        n/a                 n/a
Gi2/22    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/23    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/24    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/25    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/26    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/27    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/28    auto   off        0.0        0.0        n/a                 n/a
Gi2/29    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/30    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/31    auto   off        0.0        0.0        n/a                 n/a
Gi2/32    auto   off        0.0        0.0        n/a                 n/a
Gi2/33    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/34    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/35    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/36    auto   on         6.3        6.0        IP Phone 6921       2
                            From PS    To Device
Gi2/37    auto   off        0.0        0.0        n/a                 n/a
Gi2/38    auto   off        0.0        0.0        n/a                 n/a
Gi2/39    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/40    auto   off        0.0        0.0        n/a                 n/a
Gi2/41    auto   off        0.0        0.0        n/a                 n/a
Gi2/42    auto   off        0.0        0.0        n/a                 n/a
Gi2/43    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/44    auto   off        0.0        0.0        n/a                 n/a
Gi2/45    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/46    auto   on         6.3        6.0        IP Phone 6921       2
Gi2/47    auto   on         15.8       15.0       AIR-LAP1141N-A-K9   3
Gi2/48    auto   on         15.8       15.0       AIR-LAP1141N-A-K9   3
Gi3/1     auto   on         6.3        6.0        IP Phone 6921       2
Gi3/2     auto   off        0.0        0.0        n/a                 n/a
Gi3/3     auto   on         6.3        6.0        IP Phone 6921       2
Gi3/4     auto   on         6.3        6.0        IP Phone 6921       2
Gi3/5     auto   off        0.0        0.0        n/a                 n/a
Gi3/6     auto   off        0.0        0.0        n/a                 n/a
Gi3/7     auto   on         6.3        6.0        IP Phone 6921       2
Gi3/8     auto   on         6.3        6.0        IP Phone 6921       2
Gi3/9     auto   on         6.3        6.0        IP Phone 6921       2
Gi3/10    auto   on         6.3        6.0        IP Phone 6921       2
                            From PS    To Device
Gi3/11    auto   off        0.0        0.0        n/a                 n/a
Gi3/12    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/13    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/14    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/15    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/16    auto   off        0.0        0.0        n/a                 n/a
Gi3/17    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/18    auto   off        0.0        0.0        n/a                 n/a
Gi3/19    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/20    auto   off        0.0        0.0        n/a                 n/a
Gi3/21    auto   off        0.0        0.0        n/a                 n/a
Gi3/22    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/23    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/24    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/25    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/26    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/27    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/28    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/29    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/30    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/31    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/32    auto   on         6.3        6.0        IP Phone 6921       2
                            From PS    To Device
Gi3/33    auto   on         7.4        7.0        Cisco/Ieee PD       2
Gi3/34    auto   off        0.0        0.0        n/a                 n/a
Gi3/35    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/36    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/37    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/38    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/39    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/40    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/41    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/42    auto   off        0.0        0.0        n/a                 n/a
Gi3/43    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/44    auto   on         6.3        6.0        IP Phone 6921       2
Gi3/45    auto   on         16.2       15.4       AIR-CAP2602E-N-K9   3
Gi3/46    auto   on         16.2       15.4       AIR-CAP3602E-N-K9   4
Gi3/47    auto   on         16.2       15.4       AIR-CAP3602E-N-K9   4
Gi3/48    auto   on         16.2       15.4       AIR-CAP2602E-N-K9   3
Gi4/1     auto   on         6.3        6.0        IP Phone 6921       2
Gi4/2     auto   off        0.0        0.0        n/a                 n/a
Gi4/3     auto   on         6.3        6.0        IP Phone 6921       2
Gi4/4     auto   off        0.0        0.0        n/a                 n/a
Gi4/5     auto   on         6.3        6.0        IP Phone 6921       2
Gi4/6     auto   on         6.3        6.0        IP Phone 6921       2
                            From PS    To Device
Gi4/7     auto   off        0.0        0.0        n/a                 n/a
Gi4/8     auto   on         6.3        6.0        IP Phone 6921       2
Gi4/9     auto   on         6.3        6.0        IP Phone 6921       2
Gi4/10    auto   on         6.3        6.0        IP Phone 6921       2
Gi4/11    auto   off        0.0        0.0        n/a                 n/a
Gi4/12    auto   on         6.3        6.0        IP Phone 6921       2
Gi4/13    auto   off        0.0        0.0        n/a                 n/a
Gi4/14    auto   off        0.0        0.0        n/a                 n/a
Gi4/15    auto   off        0.0        0.0        n/a                 n/a
Gi4/16    auto   off        0.0        0.0        n/a                 n/a
Gi4/17    auto   off        0.0        0.0        n/a                 n/a
Gi4/18    auto   off        0.0        0.0        n/a                 n/a
Gi4/19    auto   off        0.0        0.0        n/a                 n/a
Gi4/20    auto   on         16.2       15.4       Ieee PD             0
Gi4/21    auto   on         7.4        7.0        Ieee PD             2
Gi4/22    auto   on         7.4        7.0        Ieee PD             2
Gi4/23    auto   off        0.0        0.0        n/a                 n/a
Gi4/24    auto   on         16.2       15.4       Ieee PD             0
Gi4/25    auto   off        0.0        0.0        n/a                 n/a
Gi4/26    auto   on         7.4        7.0        Ieee PD             2
Gi4/27    auto   on         7.4        7.0        Ieee PD             2
Gi4/28    auto   on         7.4        7.0        Ieee PD             2
                            From PS    To Device
Gi4/29    auto   on         16.2       15.4       Ieee PD             0
Gi4/30    auto   off        0.0        0.0        n/a                 n/a
Gi4/31    auto   on         6.3        6.0        IP Phone 6921       2
Gi4/32    auto   on         16.2       15.4       Ieee PD             0
Gi4/33    auto   off        0.0        0.0        n/a                 n/a
Gi4/34    auto   off        0.0        0.0        n/a                 n/a
Gi4/35    auto   off        0.0        0.0        n/a                 n/a
Gi4/36    auto   off        0.0        0.0        n/a                 n/a
Gi4/37    auto   off        0.0        0.0        n/a                 n/a
Gi4/38    auto   off        0.0        0.0        n/a                 n/a
Gi4/39    auto   off        0.0        0.0        n/a                 n/a
Gi4/40    auto   off        0.0        0.0        n/a                 n/a
Gi4/41    auto   off        0.0        0.0        n/a                 n/a
Gi4/42    auto   on         6.3        6.0        IP Phone 6921       2
Gi4/43    auto   on         6.3        6.0        IP Phone 6921       2
Gi4/44    auto   off        0.0        0.0        n/a                 n/a
Gi4/45    auto   on         6.3        6.0        IP Phone 6921       2
Gi4/46    auto   on         6.3        6.0        IP Phone 6921       2
Gi4/47    auto   on         16.2       15.4       AIR-CAP3502I-N-K9   3
Gi4/48    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/1     auto   off        0.0        0.0        n/a                 n/a
Gi7/2     auto   off        0.0        0.0        n/a                 n/a
                            From PS    To Device
Gi7/3     auto   on         6.3        6.0        IP Phone 6921       2
Gi7/4     auto   off        0.0        0.0        n/a                 n/a
Gi7/5     auto   off        0.0        0.0        n/a                 n/a
Gi7/6     auto   off        0.0        0.0        n/a                 n/a
Gi7/7     auto   on         6.3        6.0        IP Phone 6921       2
Gi7/8     auto   off        0.0        0.0        n/a                 n/a
Gi7/9     auto   on         6.3        6.0        IP Phone 6921       2
Gi7/10    auto   off        0.0        0.0        n/a                 n/a
Gi7/11    auto   off        0.0        0.0        n/a                 n/a
Gi7/12    auto   off        0.0        0.0        n/a                 n/a
Gi7/13    auto   off        0.0        0.0        n/a                 n/a
Gi7/14    auto   on         7.4        7.0        IP Phone 6921       2
Gi7/15    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/16    auto   off        0.0        0.0        n/a                 n/a
Gi7/17    auto   off        0.0        0.0        n/a                 n/a
Gi7/18    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/19    auto   off        0.0        0.0        n/a                 n/a
Gi7/20    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/21    auto   off        0.0        0.0        n/a                 n/a
Gi7/22    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/23    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/24    auto   on         6.3        6.0        IP Phone 6921       2
                            From PS    To Device
Gi7/25    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/26    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/27    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/28    auto   off        0.0        0.0        n/a                 n/a
Gi7/29    auto   off        0.0        0.0        n/a                 n/a
Gi7/30    auto   off        0.0        0.0        n/a                 n/a
Gi7/31    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/32    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/33    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/34    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/35    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/36    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/37    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/38    auto   off        0.0        0.0        n/a                 n/a
Gi7/39    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/40    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/41    auto   off        0.0        0.0        n/a                 n/a
Gi7/42    auto   off        0.0        0.0        n/a                 n/a
Gi7/43    auto   on         7.4        7.0        Ieee PD             2
Gi7/44    auto   off        0.0        0.0        n/a                 n/a
Gi7/45    auto   on         6.3        6.0        IP Phone 6921       2
Gi7/46    auto   on         16.2       15.4       Ieee PD             0
                            From PS    To Device
Gi7/47    auto   off        0.0        0.0        n/a                 n/a
Gi7/48    auto   on         6.3        6.0        IP Phone 6921       2
Gi8/1     auto   off        0.0        0.0        n/a                 n/a
Gi8/2     auto   off        0.0        0.0        n/a                 n/a
Gi8/3     auto   off        0.0        0.0        n/a                 n/a
Gi8/4     auto   off        0.0        0.0        n/a                 n/a
Gi8/5     auto   off        0.0        0.0        n/a                 n/a
Gi8/6     auto   off        0.0        0.0        n/a                 n/a
Gi8/7     auto   off        0.0        0.0        n/a                 n/a
Gi8/8     auto   off        0.0        0.0        n/a                 n/a
Gi8/9     auto   off        0.0        0.0        n/a                 n/a
Gi8/10    auto   off        0.0        0.0        n/a                 n/a
Gi8/11    auto   off        0.0        0.0        n/a                 n/a
Gi8/12    auto   off        0.0        0.0        n/a                 n/a
Gi8/13    auto   off        0.0        0.0        n/a                 n/a
Gi8/14    auto   off        0.0        0.0        n/a                 n/a
Gi8/15    auto   off        0.0        0.0        n/a                 n/a
Gi8/16    auto   off        0.0        0.0        n/a                 n/a
Gi8/17    auto   off        0.0        0.0        n/a                 n/a
Gi8/18    auto   off        0.0        0.0        n/a                 n/a
Gi8/19    auto   off        0.0        0.0        n/a                 n/a
Gi8/20    auto   off        0.0        0.0        n/a                 n/a
                            From PS    To Device
Gi8/21    auto   off        0.0        0.0        n/a                 n/a
Gi8/22    auto   off        0.0        0.0        n/a                 n/a
Gi8/23    auto   off        0.0        0.0        n/a                 n/a
Gi8/24    auto   off        0.0        0.0        n/a                 n/a
Gi8/25    auto   off        0.0        0.0        n/a                 n/a
Gi8/26    auto   off        0.0        0.0        n/a                 n/a
Gi8/27    auto   off        0.0        0.0        n/a                 n/a
Gi8/28    auto   off        0.0        0.0        n/a                 n/a
Gi8/29    auto   off        0.0        0.0        n/a                 n/a
Gi8/30    auto   off        0.0        0.0        n/a                 n/a
Gi8/31    auto   off        0.0        0.0        n/a                 n/a
Gi8/32    auto   off        0.0        0.0        n/a                 n/a
Gi8/33    auto   off        0.0        0.0        n/a                 n/a
Gi8/34    auto   off        0.0        0.0        n/a                 n/a
Gi8/35    auto   off        0.0        0.0        n/a                 n/a
Gi8/36    auto   off        0.0        0.0        n/a                 n/a
Gi8/37    auto   off        0.0        0.0        n/a                 n/a
Gi8/38    auto   off        0.0        0.0        n/a                 n/a
Gi8/39    auto   off        0.0        0.0        n/a                 n/a
Gi8/40    auto   off        0.0        0.0        n/a                 n/a
Gi8/41    auto   off        0.0        0.0        n/a                 n/a
Gi8/42    auto   off        0.0        0.0        n/a                 n/a
                            From PS    To Device
Gi8/43    auto   off        0.0        0.0        n/a                 n/a
Gi8/44    auto   off        0.0        0.0        n/a                 n/a
Gi8/45    auto   off        0.0        0.0        n/a                 n/a
Gi8/46    auto   off        0.0        0.0        n/a                 n/a
Gi8/47    auto   off        0.0        0.0        n/a                 n/a
Gi8/48    auto   off        0.0        0.0        n/a                 n/a
Totals:          147  on    1075.5     1021.7
EON_SEZ_F1_4510_AS02# ex
Leo Laohoo Wed, 07/09/2014 - 15:45
  • Hall of Fame,
    2017 LAN, Wireless
I am re-reading your initial post.  The error message means that the entire line card's PoE function has been disabled because there's been too much power draw.   Which is strange.
Your "sh environment" shows that you've got two large PS and they are more-than-enough to power the entire chassis' PoE.
Your "sh power inline" is showing slot 8 doesn't have any PoE.
So what I'd like to know is what PoE devices do you have connected to slot 8 line card?
Can I ask you to post the output to the command "sh module"?
hjanjali1 Thu, 07/10/2014 - 01:35
Hi Leo,
It is an RJ45 V+E Module. The reason you do not see any POE's connected is because the phones do not boot when connected on to the module. Only data connectivity works. When the phone is connected the port status is as "not connected".
Hatim Janjali
Leo Laohoo Thu, 07/10/2014 - 05:19
  • Hall of Fame,
    2017 LAN, Wireless
Kindly post the output to the command "sh module".
hjanjali1 Thu, 07/10/2014 - 22:42
Hi Leo,
EON_SEZ_F1_4510_AS02#sh module
Mod Ports Card Type                              Model              Serial No.
 1    48  10/100/1000BaseT Premium POE E Series  WS-X4748-RJ45V+E   CAT1512L0DB
 2    48  10/100/1000BaseT Premium POE E Series  WS-X4748-RJ45V+E   CAT1512L0B5
 3    48  10/100/1000BaseT Premium POE E Series  WS-X4748-RJ45V+E   CAT1802L66N
 4    48  10/100/1000BaseT Premium POE E Series  WS-X4748-RJ45V+E   CAT1512L0FB
 5     4  Sup 7-E 10GE (SFP+), 1000BaseX (SFP)   WS-X45-SUP7-E      CAT1510L2G1
 6     4  Sup 7-E 10GE (SFP+), 1000BaseX (SFP)   WS-X45-SUP7-E      CAT1510L2KV
 7    48  10/100/1000BaseT Premium POE E Series  WS-X4748-RJ45V+E   CAT1512L0CL
 8    48  10/100/1000BaseT Premium POE E Series  WS-X4748-RJ45V+E   CAT1512L0DP
 9    48  10/100/1000BaseT (RJ45)                WS-X4648-RJ45-E    JAE151208MX
10    48  10/100/1000BaseT (RJ45)                WS-X4648-RJ45-E    JAE151208S9
 M MAC addresses                    Hw  Fw           Sw               Status
 1 c89c.1de4.58f0 to c89c.1de4.591f 1.0                               Ok
 2 c89c.1de4.5f50 to c89c.1de4.5f7f 1.0                               Ok
 3 b838.6185.a7b0 to b838.6185.a7df 1.4                               Ok
 4 c89c.1de4.6310 to c89c.1de4.633f 1.0                               Ok
 5 6400.f159.c8c0 to 6400.f159.c8c3 1.0 15.0(1r)SG1  03.04.04.SG      Ok
 6 6400.f159.c8c4 to 6400.f159.c8c7 1.0 15.0(1r)SG1  03.04.04.SG      Ok
 7 c89c.1de4.5bf0 to c89c.1de4.5c1f 1.0                               Ok
 8 c89c.1de4.5fe0 to c89c.1de4.600f 1.0                               Ok
 9 6400.f12b.20d1 to 6400.f12b.2100 1.0                               Ok
10 6400.f12b.2731 to 6400.f12b.2760 1.0                               Ok
Mod  Redundancy role     Operating mode      Redundancy status
 5   Active Supervisor   SSO                 Active
 6   Standby Supervisor  SSO                 Standby hot
Leo Laohoo Fri, 07/11/2014 - 00:51
  • Hall of Fame,
    2017 LAN, Wireless
I am not sure.
Your IOS is good.  It could be a line card failure.  You might want to just open a TAC case with this thread.  Option is found on the upper-right-hand corner under "Action".
hjanjali1 Mon, 07/14/2014 - 02:40
Hi Leo,
Could there be a problem with the model of the line card as i have 3 LC's failed with the same reason in 3 different switches.
Hatim Janjali
Leo Laohoo Mon, 07/14/2014 - 15:34
  • Hall of Fame,
    2017 LAN, Wireless
There is a possibility that it could be a bad "batch" of line cards.  This is more true if you can compare the serial number of the three previous line cards that were RMA-ed and this one.
If they all have similar number between the fourth and seventh, then it could be.
