6509 PSU Query
Answered Question
Oct 27th, 2005
Hello All,
I got the following message when I did a SHOW POWER on our 6509:
"Note: PS2 capacity is limited to 2940.00 Watts (70.00 Amps @ 42V)
when PS1 is not present"
The PSUs are running in redundant mode.
Is this something I should worry about?
ukcap04-133-c65-ios#show power
system power redundancy mode = redundant
system power total = 3780.00 Watts (90.00 Amps @ 42V)
system power used = 1215.48 Watts (28.94 Amps @ 42V)
system power available = 2564.52 Watts (61.06 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
1 WS-CAC-4000W-INT 3795.12 90.36 OK OK on
2 WS-CAC-4000W-INT 3795.12 90.36 OK OK on
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
5 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
6 WS-SUP720-3B 282.24 6.72 282.24 6.72 on on
8 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
9 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
Correct Answer by szahid about 11 years 9 months ago
If you have 2 x 4000W and the power supply in bay #1 goes down, then the 4000W PSU in bay #2 will NOT be able to drive the full 4000W power - rather it will be limited to about 3000W. I dont know the exact
engineering reasons behind this but do know that this is not a bug and it is doing the right thing. Note the line in the output below which
highlights this...
2 WS-CAC-4000W-INT 3795.12 90.36 - - off
*Note: PS2 capacity is limited to 2940.00 Watts (70.00 Amps @ 42V)
when PS1 is not present*