RPS2300 stuck in "in use" status with CCME 2851

Hi,

My CCME power supply stuck in "in use" status after a power supply failure.

When I put again the CCME power supply, the supply stay provide by the RPS2300.

#sh environment

Main Power Supply is AC

Redundant Power Supply is attached

RPS status: in use

Fan 1 OK

Fan 2 OK

Fan 3 OK

System Temperature: 29 Celsius (normal)

Environmental information last updated 00:00:10 ago

#

I have performed the same with 3750E no problem.

Many thanks in advance for your return.

Olivier

1 REPLY
Anonymous
N/A

Re: RPS2300 stuck in "in use" status with CCME 2851

the RPS is designed to only support one such failure event at a time, meaning if six switches are cabled to the RPS

as failure protection and an attached switch has a ps that fails, then the RPS goes into the role of providing for that lost supply and therefore cannot provide for any other failures while the chassis with dead ps remains attached