catalyst 6513 power problem ?

lcd_shouldit
Level 1
Level 1

Hi, today I got these log:

2836604: Jul  4 14:52:21.793: %SNMP-5-CHASSISALARM: Chassis Alarm Trap: tmpAlarm(OFF), minorAlarm(OFF), and/or majorAlarm(OFF)

2836605: Jul  4 14:52:21.781: %C6KPWR-SP-4-INPUTCHANGE: Power supply 2 input has changed.  Power capacity adjusted to 5771.64W

2836606: Jul  4 14:52:21.785: %C6KPWR-SP-4-PSREDUNDANTBOTHSUPPLY: in power-redundancy mode, system is operating on both power supplies.

2836607: Jul  4 14:52:23.913: %SNMP-5-CHASSISALARM: Chassis Alarm Trap: tmpAlarm(OFF), minorAlarm(ON), and/or majorAlarm(OFF)

2836608: Jul  4 14:52:23.889: %C6KPWR-SP-4-INPUTCHANGE: Power supply 2 input has changed.  Power capacity adjusted to 2671.20W

2836609: Jul  4 14:52:23.889: %C6KPWR-SP-4-PSOUTPUTDROP: Power supply 2 output has dropped

2836610: Jul  4 14:52:23.889: %C6KPWR-SP-4-PSREDUNDANTMISMATCH: power supplies rated outputs do not match.

2836611: Jul  4 14:52:23.897: %C6KPWR-SP-4-PSNOREDUNDANCY: Power supplies are not in full redundancy, power usage exceeds lower capacity supply

------------------ show power ------------------

system power redundancy mode = redundant

system power redundancy operationally = non-redundant

system power total =     5771.64 Watts (137.42 Amps @ 42V)

system power used =      3788.40 Watts (90.20 Amps @ 42V)

system power available = 1983.24 Watts (47.22 Amps @ 42V)

                        Power-Capacity PS-Fan Output Oper

PS   Type               Watts   A @42V Status Status State

---- ------------------ ------- ------ ------ ------ -----

1    WS-CAC-6000W       5771.64 137.42 OK     OK     on

2    WS-CAC-6000W       2671.20 63.60  OK     OK     on

                        Pwr-Allocated  Oper

Fan  Type               Watts   A @42V State

---- ------------------ ------- ------ -----

1    WS-C6K-13SLT-FAN2   298.20  7.10  OK

------------------ show environment ------------------

environmental alarms:

system minor alarm on power-supply 2 power-output-mode (raised 00:21:37 ago)

backplane:

  operating clock count: 2

  operating VTT count: 3

fan-tray 1:

  fan-tray 1 type: WS-C6K-13SLT-FAN2

  fan-tray 1 version: 2

  fan-tray 1 fan-fail: OK

VTT 1:

  VTT 1 OK: OK

  VTT 1 outlet temperature: 29C

VTT 2:

  VTT 2 OK: OK

  VTT 2 outlet temperature: 26C

VTT 3:

  VTT 3 OK: OK

  VTT 3 outlet temperature: 30C

clock 1:

  clock 1 OK: OK, clock 1 clock-inuse: in-use

clock 2:

  clock 2 OK: OK, clock 2 clock-inuse: not-in-use

power-supply 1:

  power-supply 1 fan-fail: OK

  power-supply 1 power-input: AC high

  power-supply 1 power-output-mode: high

  power-supply 1 power-output-fail: OK

power-supply 2:

  power-supply 2 fan-fail: OK

  power-supply 2 power-input: AC low

  power-supply 2 power-output-mode: low

  power-supply 2 power-output-fail: OK

So, Is there some problem ?

1 Accepted Solution

Accepted Solutions

InayathUlla Sharieff
Cisco Employee
Cisco Employee
Problem Description:


%C6KPWR-SP-4-PSOUTPUTDROP: Power supply [dec] output has dropped
A drop in output power was detected in the specified power supply. The input power may be offline or has changed from 220V to 110V.

Recommended Action: Reseat the input power cable and verify that the input line voltage is adequate. Enter the show power command to display the power status.

http://www.cisco.com/cgi-bin/Support/Errordecoder/index.cgi?action=search&counter=0&paging=5&links=reference&index=all&query=C6KPWR-SP-4-PSOUTPUTDROP

In order to investigate the real problem and root cause, we need to check the input line outage issue first.
But show power command line outputs shows PSU 1 still fine at this time.

Action plan:
1. check the if there is any power outage.
2. if power system reports input power still ok at that time period, It indicated PSU operational fail. I need to be RMA.

View solution in original post

3 Replies 3

InayathUlla Sharieff
Cisco Employee
Cisco Employee
Problem Description:


%C6KPWR-SP-4-PSOUTPUTDROP: Power supply [dec] output has dropped
A drop in output power was detected in the specified power supply. The input power may be offline or has changed from 220V to 110V.

Recommended Action: Reseat the input power cable and verify that the input line voltage is adequate. Enter the show power command to display the power status.

http://www.cisco.com/cgi-bin/Support/Errordecoder/index.cgi?action=search&counter=0&paging=5&links=reference&index=all&query=C6KPWR-SP-4-PSOUTPUTDROP

In order to investigate the real problem and root cause, we need to check the input line outage issue first.
But show power command line outputs shows PSU 1 still fine at this time.

Action plan:
1. check the if there is any power outage.
2. if power system reports input power still ok at that time period, It indicated PSU operational fail. I need to be RMA.

Hi, Thank you so much.

It is power issue. We make a RMA.

I've seen this alarm before.  A lot of times.

Each PSU has two power input.  If one of the power input source is flakey or loose, you'll get errors like this.  Alternatively, if one of the power input connectors in the PSU is faulty, same thing.