Hi, today I got these log:
2836604: Jul 4 14:52:21.793: %SNMP-5-CHASSISALARM: Chassis Alarm Trap: tmpAlarm(OFF), minorAlarm(OFF), and/or majorAlarm(OFF)
2836605: Jul 4 14:52:21.781: %C6KPWR-SP-4-INPUTCHANGE: Power supply 2 input has changed. Power capacity adjusted to 5771.64W
2836606: Jul 4 14:52:21.785: %C6KPWR-SP-4-PSREDUNDANTBOTHSUPPLY: in power-redundancy mode, system is operating on both power supplies.
2836607: Jul 4 14:52:23.913: %SNMP-5-CHASSISALARM: Chassis Alarm Trap: tmpAlarm(OFF), minorAlarm(ON), and/or majorAlarm(OFF)
2836608: Jul 4 14:52:23.889: %C6KPWR-SP-4-INPUTCHANGE: Power supply 2 input has changed. Power capacity adjusted to 2671.20W
2836609: Jul 4 14:52:23.889: %C6KPWR-SP-4-PSOUTPUTDROP: Power supply 2 output has dropped
2836610: Jul 4 14:52:23.889: %C6KPWR-SP-4-PSREDUNDANTMISMATCH: power supplies rated outputs do not match.
2836611: Jul 4 14:52:23.897: %C6KPWR-SP-4-PSNOREDUNDANCY: Power supplies are not in full redundancy, power usage exceeds lower capacity supply
------------------ show power ------------------
system power redundancy mode = redundant
system power redundancy operationally = non-redundant
system power total = 5771.64 Watts (137.42 Amps @ 42V)
system power used = 3788.40 Watts (90.20 Amps @ 42V)
system power available = 1983.24 Watts (47.22 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-6000W 5771.64 137.42 OK OK on
2 WS-CAC-6000W 2671.20 63.60 OK OK on
Pwr-Allocated Oper
Fan Type Watts A @42V State
---- ------------------ ------- ------ -----
1 WS-C6K-13SLT-FAN2 298.20 7.10 OK
------------------ show environment ------------------
environmental alarms:
system minor alarm on power-supply 2 power-output-mode (raised 00:21:37 ago)
backplane:
operating clock count: 2
operating VTT count: 3
fan-tray 1:
fan-tray 1 type: WS-C6K-13SLT-FAN2
fan-tray 1 version: 2
fan-tray 1 fan-fail: OK
VTT 1:
VTT 1 OK: OK
VTT 1 outlet temperature: 29C
VTT 2:
VTT 2 OK: OK
VTT 2 outlet temperature: 26C
VTT 3:
VTT 3 OK: OK
VTT 3 outlet temperature: 30C
clock 1:
clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
clock 2 OK: OK, clock 2 clock-inuse: not-in-use
power-supply 1:
power-supply 1 fan-fail: OK
power-supply 1 power-input: AC high
power-supply 1 power-output-mode: high
power-supply 1 power-output-fail: OK
power-supply 2:
power-supply 2 fan-fail: OK
power-supply 2 power-input: AC low
power-supply 2 power-output-mode: low
power-supply 2 power-output-fail: OK
So, Is there some problem ?
Solved! Go to Solution.
07-04-2013 06:20 AM
Problem Description: %C6KPWR-SP-4-PSOUTPUTDROP: Power supply [dec] output has dropped A drop in output power was detected in the specified power supply. The input power may be offline or has changed from 220V to 110V. Recommended Action: Reseat the input power cable and verify that the input line voltage is adequate. Enter the show power command to display the power status. http://www.cisco.com/cgi-bin/Support/Errordecoder/index.cgi?action=search&counter=0&paging=5&links=reference&index=all&query=C6KPWR-SP-4-PSOUTPUTDROP In order to investigate the real problem and root cause, we need to check the input line outage issue first. But show power command line outputs shows PSU 1 still fine at this time. Action plan: 1. check the if there is any power outage. 2. if power system reports input power still ok at that time period, It indicated PSU operational fail. I need to be RMA.
07-04-2013 06:20 AM
Problem Description: %C6KPWR-SP-4-PSOUTPUTDROP: Power supply [dec] output has dropped A drop in output power was detected in the specified power supply. The input power may be offline or has changed from 220V to 110V. Recommended Action: Reseat the input power cable and verify that the input line voltage is adequate. Enter the show power command to display the power status. http://www.cisco.com/cgi-bin/Support/Errordecoder/index.cgi?action=search&counter=0&paging=5&links=reference&index=all&query=C6KPWR-SP-4-PSOUTPUTDROP In order to investigate the real problem and root cause, we need to check the input line outage issue first. But show power command line outputs shows PSU 1 still fine at this time. Action plan: 1. check the if there is any power outage. 2. if power system reports input power still ok at that time period, It indicated PSU operational fail. I need to be RMA.
07-05-2013 09:18 AM
Hi, Thank you so much.
It is power issue. We make a RMA.
07-05-2013 04:07 PM
I've seen this alarm before. A lot of times.
Each PSU has two power input. If one of the power input source is flakey or loose, you'll get errors like this. Alternatively, if one of the power input connectors in the PSU is faulty, same thing.