New Member

Getting PLATFORM-2-MOD_TEMPMINALRM error message in N7k

Dear Folkz,

I'm getting the below error continuously in N7K platform. Plz help here to resolve this problem.

2013 Jul 16 04:09:29  %PLATFORM-2-MOD_TEMPMINALRM: Xbar-3 reported minor temperature alarm. Sensor=2 Temperature=43 MinThreshold=42

2013 Jul 16 05:45:15 %PLATFORM-2-MOD_TEMPOK: Xbar-3 recovered from minor temperature alarm. Sensor=2 Temperature=41 MinThreshold=42

2013 Jul 16 06:32:18  %PLATFORM-2-MOD_TEMPMINALRM: Xbar-4 reported minor temperature alarm. Sensor=2 Temperature=43 MinThreshold=42

2013 Jul 16 06:35:19  %PLATFORM-2-MOD_TEMPOK: Xbar-4 recovered from minor temperature alarm. Sensor=2 Temperature=41 MinThreshold=42

CORE2# sh environment temperature xbar 3

Temperature:

--------------------------------------------------------------------

Module   Sensor        MajorThresh   MinorThres   CurTemp     Status

                       (Celsius)     (Celsius)    (Celsius)

--------------------------------------------------------------------

xbar-3   Intake  (s2)    60              42          39         Ok

xbar-3   Crossbar(s3)    105             95          69         Ok

2 REPLIES
Cisco Employee

Getting PLATFORM-2-MOD_TEMPMINALRM error message in N7k

Kindly clear the air filter to resolve this high temperature issue.

Below are the steps to check and change air filter.

 http://www.cisco.com/en/US/docs/switches/datacenter/hw/nexus7000/install
ation/guide/n7k_replacing.html#wp1109683

HTH

Regards

Inayath

New Member

Getting PLATFORM-2-MOD_TEMPMINALRM error message in N7k

Dear Shariff,

Thanks For your response !

I'll do the same and update the result shortly :-)