I have question about power redundancy mode specially restricted power mode.
hi all,
I have a question about power redundancy mode in cat6500-AC3000watt
cat6500#sh power
system power redundancy mode = restricted power mode
i know about combined mode and redundant mode,
but unfamiliar with restricted power mode
is there anyone knows about this?
1 ACCEPTED SOLUTION
Re: I have question about power redundancy mode specially restri
Hi Sanghee Han,
So “show power” is actually given you
“system power redundancy mode = redundant” and
restricted shown in the “show env” cooling section for fan-tray 1:
fan-tray 1:
   fan-tray 1 type: WS-C6509-E-FAN
   fan-tray 1 mode: Restricted-power
   fan-tray 1 fan-fail: OK
The "restricted" power is the default for the E-chassis.
The WS-C6506/9-E-FAN has two modes - Restricted-Power and High Power.
Restricted-power mode means that the Fan-Tray operates at lower rotating speed
and it is enough for system’s per slots cooling (to keep temperature under thr).
Usually the fans in fan-tray will speed up if a fan has failed in the fan-tray or
if there are a linecards in the chassis that requires higher cooling.
For example, in case of WS-X6708-10G modules in some slots,
the chassis/fans will be running high-power mode.
The “show env [cooling]” will give you this info,
with details on required fans CFM capacity for chassis and for each module.
Like in you case with 4 modules:
1    7600-SIP-400        265.02  6.31   265.02  6.31  on    on
2    WS-X6748-GE-TX      325.50  7.75   325.50  7.75  on    on
5    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
6    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
The cooling at 70 cfm fans rotating looks enough for setup,
so fan-tray 1 is in default mode Restricted-power:
----------------- show environment ------------------
fan-tray 1:
… snip…
chassis per slot cooling capacity: 70 cfm ambient temperature: < 55C
  module 1 cooling requirement: 35 cfm
  module 2 cooling requirement: 70 cfm
  module 5 cooling requirement: 35 cfm
  module 6 cooling requirement: 35 cfm
And for example in case of the chassis w two WS-X6708-10G-3C in slots 1 and 2
the fans will be running at high speed and
the output would looks similar to follow:
#show env cool
fan-tray 1:
 fan-tray 1 mode: high-power <--
chassis per slot cooling capacity: 94 cfm ambient temperature: < 55C
 module 1 cooling requirement: 84 cfm  <<<<<
 module 2 cooling requirement: 84 cfm  <<<<<
 module 3 cooling requirement: 70 cfm
 module 4 cooling requirement: 70 cfm
 module 7 cooling requirement: 70 cfm
 module 8 cooling requirement: 70 cfm
Sergey
Hello!
Is it a newer C6500-E series chassis ?
If yes, than "restricted" power could be the default for E-series, but normally it is
shown in show end, show power for FAN-tray part only, like "fan-tray 1 mode: Restricted-power".
Sergey
Thanks for your answer.
then, i wonder how the cat65k-E operates power resource in restricted-power mode.
do you know about this?
Could you post the full output of "show power", "show env" and clarify which ios version is it.
Sergey
hi Sergey
i post the relative log...show power/env/ver/module.
------------------ show power ------------------
system power total =     2771.16 Watts (65.98 Amps @ 42V)
system power used =      1305.36 Watts (31.08 Amps @ 42V)
system power available = 1465.80 Watts (34.90 Amps @ 42V)
                        Power-Capacity PS-Fan Output Oper
PS   Type               Watts   A @42V Status Status State
1    WS-CAC-3000W       2771.16 65.98  OK     OK     on
2    WS-CAC-3000W       2771.16 65.98  OK     OK     on
                        Pwr-Allocated  Oper
Fan  Type               Watts   A @42V State
1    WS-C6509-E-FAN      150.36  3.58  OK
                        Pwr-Requested  Pwr-Allocated  Admin Oper
Slot Card-Type          Watts   A @42V Watts   A @42V State State
system auxiliary power mode = off
system auxiliary power redundancy operationally = non-redundant
system primary connector power limit =   10920.00 Watts (260.00 Amps @ 42V)
system auxiliary connector power limit = 10500.00 Watts (250.00 Amps @ 42V)
system primary power used =              1305.36 Watts (31.08 Amps @ 42V)
system auxiliary power used =            0 Watt
------------------ show environment ------------------
environmental alarms:
  no alarms
backplane:
  operating clock count: 2
  operating VTT count: 3
fan-tray 1:
VTT 1:
  VTT 1 OK: OK
  VTT 1 outlet temperature: 35C
VTT 2:
  VTT 2 OK: OK
  VTT 2 outlet temperature: 37C
VTT 3:
  VTT 3 OK: OK
  VTT 3 outlet temperature: 35C
clock 1:
  clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
  clock 2 OK: OK, clock 2 clock-inuse: not-in-use
power-supply 1:
  power-supply 1 fan-fail: OK
  power-supply 1 power-input: AC high
  power-supply 1 power-output-mode: high
  power-supply 1 power-output-fail: OK
power-supply 2:
  power-supply 2 fan-fail: OK
  power-supply 2 power-input: AC high
  power-supply 2 power-output-mode: high
  power-supply 2 power-output-fail: OK
module 1:
  module 1 power-output-fail: OK
  module 1 outlet temperature: 46C
  module 1 inlet temperature: 38C
  module 1 device-1 temperature: 44C
  module 1 device-2 temperature: 43C
module 2:
  module 2 power-output-fail: OK
  module 2 outlet temperature: 49C
  module 2 inlet temperature: 33C
module 5:
  module 5 power-output-fail: OK
  module 5 outlet temperature: 37C
  module 5 inlet temperature: 32C
  module 5 device-1 temperature: 42C
  module 5 device-2 temperature: 42C
  module 5 asic-1 temperature: 31C
  module 5 asic-2 temperature: 31C
  module 5 asic-3 temperature: 31C
  module 5 asic-4 temperature: 32C
  module 5 asic-5 temperature: 31C
  module 5 asic-6 temperature: 32C
  module 5 RP outlet temperature: 34C
  module 5 RP inlet temperature: 35C
  module 5 EARL outlet temperature: 43C
  module 5 EARL inlet temperature: 34C
module 6:
  module 6 power-output-fail: OK
  module 6 outlet temperature: 37C
  module 6 inlet temperature: 32C
  module 6 device-1 temperature: 41C
  module 6 device-2 temperature: 41C
  module 6 asic-1 temperature: 31C
  module 6 asic-2 temperature: 31C
  module 6 asic-3 temperature: 31C
  module 6 asic-4 temperature: 30C
  module 6 asic-5 temperature: 31C
  module 6 asic-6 temperature: 31C
  module 6 RP outlet temperature: 34C
  module 6 RP inlet temperature: 35C
  module 6 EARL outlet temperature: 40C
  module 6 EARL inlet temperature: 34C
  SPA-4XT3/E3[1/0] temperature sensor 0, reading: 39C
  SPA-4XT3/E3[1/0] temperature sensor 1, reading: 38C
  SPA-4XT3/E3[1/0] temperature sensor 2, reading: 40C
  SPA-4XT3/E3[1/0] temperature sensor 3, reading: 41C
  SPA-4XT3/E3[1/0] temperature sensor 4, reading: 44C
  SPA-4XT3/E3[1/0] nominal: 3.300V, reading: 3.290V
  SPA-4XT3/E3[1/0] nominal: 2.500V, reading: 2.510V
  SPA-4XT3/E3[1/0] nominal: 1.800V, reading: 1.796V
  SPA-4XT3/E3[1/0] nominal: 1.500V, reading: 1.499V
  SPA-8XCHT1/E1[1/1] temperature sensor 0, reading: 40C
  SPA-8XCHT1/E1[1/1] temperature sensor 1, reading: 41C
  SPA-8XCHT1/E1[1/1] temperature sensor 2, reading: 38C
  SPA-8XCHT1/E1[1/1] temperature sensor 3, reading: 35C
  SPA-8XCHT1/E1[1/1] temperature sensor 4, reading: 45C
  SPA-8XCHT1/E1[1/1] nominal: 3.300V, reading: 3.320V
  SPA-8XCHT1/E1[1/1] nominal: 2.500V, reading: 2.516V
  SPA-8XCHT1/E1[1/1] nominal: 1.800V, reading: 1.807V
  SPA-8XCHT1/E1[1/1] nominal: 1.500V, reading: 1.509V
chassis connector rating: 1302.00 Watts (31.00 Amps @ 42V)
chassis auxiliary connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 1
  module 1 connector rating: 1512.00 Watts (36.00 Amps @ 42V)
  module 1 power consumption:  265.02 Watts ( 6.31 Amps @ 42V)
module 2
  module 2 connector rating: 2016.00 Watts (48.00 Amps @ 42V)
  module 2 power consumption:  325.50 Watts ( 7.75 Amps @ 42V)
module 5
  module 5 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
  module 5 power consumption:  282.24 Watts ( 6.72 Amps @ 42V)
module 6
  module 6 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
  module 6 power consumption:  282.24 Watts ( 6.72 Amps @ 42V)
------------------ show version ------------------
Cisco IOS Software, s72033_rp Software (s72033_rp-ADVIPSERVICESK9_WAN-M), Version 12.2(33)SXI3, RELEASE SOFTWARE (fc2)
Copyright (c) 1986-2009 by Cisco Systems, Inc.
Compiled Tue 27-Oct-09 11:11 by prod_rel_team
ROM: System Bootstrap, Version 12.2(17r)SX5, RELEASE SOFTWARE (fc1)
PE007 uptime is 9 minutes
Uptime for this control processor is 9 minutes
Time since PE007 switched to active is 8 minutes
System returned to ROM by reload at 10:45:12 UTC Mon Jan 4 2010 (SP by reload)
System image file is "sup-bootflash:s72033-advipservicesk9_wan-mz.122-33.SXI3.bin"
Last reload reason: Reload Command
A summary of U.S. laws governing Cisco cryptographic products may be found at:
export@cisco.com.
cisco WS-C6509-E (R7000) processor (revision 1.5) with 458720K/65536K bytes of memory.
Processor board ID SMC1346005X
SR71000 CPU at 600Mhz, Implementation 0x504, Rev 1.2, 512KB L2 Cache
Last reset from s/w reset
1 SIP-400 controller (4 Serial)(8 E1).
1 Virtual Ethernet interface
52 Gigabit Ethernet interfaces
7 Serial interfaces
8 Channelized E1 ports
1917K bytes of non-volatile configuration memory.
8192K bytes of packet buffer memory.
65536K bytes of Flash internal SIMM (Sector size 512K).
------------------ show module ------------------
Mod Ports Card Type                              Model              Serial No.
  1    0  4-subslot SPA Interface Processor-400  7600-SIP-400       JAE1333GT05
  2   48  CEF720 48 port 10/100/1000mb Ethernet  WS-X6748-GE-TX     SAL13463UG3
  5    2  Supervisor Engine 720 (Active)         WS-SUP720-3B       SAL135069CC
  6    2  Supervisor Engine 720 (Hot)            WS-SUP720-3B       SAL1350665E
Mod MAC addresses                       Hw    Fw           Sw           Status
  1  0026.cb02.d000 to 0026.cb02.d07f   2.7   12.2(33)SXI3 12.2(33)SXI3 Ok
  2  0026.9987.9278 to 0026.9987.92a7   3.4   12.2(18r)S1  12.2(33)SXI3 Ok
  5  000a.b86e.20a4 to 000a.b86e.20a7   5.9   8.5(3)       12.2(33)SXI3 Ok
  6  0024.1499.859c to 0024.1499.859f   5.9   8.5(3)       12.2(33)SXI3 Ok
Mod  Sub-Module                  Model              Serial       Hw     Status
1/0 4xT3E3 SPA                  SPA-4XT3/E3        JAE1344MOIT  1.1    Ok
1/1 8xCHT1/E1 SPA               SPA-8XCHT1/E1      JAE1347OL0Z  1.5    Ok
  2  Centralized Forwarding Card WS-F6700-CFC       SAL13453G2S  4.1    Ok
  5  Policy Feature Card 3       WS-F6K-PFC3B       SAL13495HBA  2.6    Ok
  5  MSFC3 Daughterboard         WS-SUP720          SAL1350679T  4.0    Ok
  6  Policy Feature Card 3       WS-F6K-PFC3B       SAL1350689H  2.6    Ok
  6  MSFC3 Daughterboard         WS-SUP720          SAL135067E7  4.0    Ok
Mod  Online Diag Status
  1  Pass
1/0 Unknown
1/1 Unknown
  2  Pass
  5  Pass
  6  Pass
thanks for your attention for this post.
and have a good time
Hi Sanghee Han,
fan-tray 1:
fan-tray 1:
… snip…
#show env cool
fan-tray 1:
Sergey
thanks for your answer.
it's a good help for me.
thanks again~~
3854