06-09-2014 06:53 AM - edited 03-07-2019 07:40 PM
Getting Error on cisco WS-C3650-24PD switch
Jun 9 13:39:51.152: %ILPOWER-3-CONTROLLER_PORT_ERR: Controller port error, Interface Gi1/0/6: Power Controller reports Short detected
the problem is this port is connected to a UPS network management card, so this port should not be trying to engage PoE at all on this port. I turned off PoE on this port manually and this message stopped. is this possibly an issue with the switch hardware or do you think it might be more or a software bug?
Solved! Go to Solution.
06-10-2014 05:29 PM
Thanks for the output. VERY, VERY HELPFUL.
Pair "D" controls GigabitEthernet and Pair "C" controls PoE. Look at the "Staus" column. See the result? Ideally, you want the result to be NORMAL. A result of "Short" is no good.
Look at the distance of the fault. This means your patch cable connected to the switch port is faulty. Replace that. Just because your end-device is not PoE doesn't mean that all you need is turning off the port's PoE. The fault could potentially mean that the cable is so faulty/inferior you're potentially looking at cross-talk.
06-09-2014 06:25 PM
Do the following:
1. Command: test cable tdr interface G1/0/6;
2. Wait for approximately 5 to 7 seconds;
3. Command: sh cable tdr interface G1/0/6; and
4. Post the output to #3.
06-10-2014 07:25 AM
S-BAY-CORE1#sh cable tdr interface g1/0/6
TDR test last run on: June 10 09:24:18
Interface Speed Local pair Pair length Remote pair Pair status
Gi1/0/6 100M Pair A 0 +/- 1 meters Pair A Normal
Pair B 0 +/- 1 meters Pair B Normal
Pair C 2 +/- 1 meters N/A Short
Pair D 2 +/- 1 meters N/A Short
and the current port config
interface GigabitEthernet1/0/6
switchport mode access
power inline never
spanning-tree portfast
Like i said above i turned off power to that port becuse the device does not use PoE
06-10-2014 05:29 PM
06-11-2014 08:01 AM
i swapped out the cable and set the port back to auto for PoE. i have not received that error since the cable swap, however after reissuing the command i get the same output
S-BAY-CORE1#sh cable tdr interface G1/0/6
TDR test last run on: June 11 09:57:47
Gi1/0/6 100M Pair A 0 +/- 1 meters Pair B Normal
Pair B 0 +/- 1 meters Pair A Normal
Pair C 1 +/- 1 meters N/A Short
Now keep in mind the network interface connected to the port is only 10/100
06-11-2014 03:28 PM
Let me hazard a guess that your switch is running 15.0(2)SE?
06-30-2014 06:28 AM
no it is not this switch "3650" is running IOS-XE this is NOT a 3560