10-12-2010 07:43 AM - edited 03-06-2019 01:28 PM
We are replacing 2 6513's with 2 Nexus 7010's. The design is the 7010s linked together and all IDFs connecitng back.. The exact way we have it now. My question is where to configure the Vpc. Do you configure it on the trunk link between the 7010's? Or do you run another fiber/copper link and run if over that?
Solved! Go to Solution.
10-12-2010 08:54 AM
Yes, Po10 is the port-channel between two Nexus7010s. - Yogesh
10-12-2010 08:10 AM
Mike,
Once you have link/channel up between 7010s, you should identify it as "vPC peer-link".
7010(config)# interface port-channel 10
7010(config-if)# vpc peer-link
Under the port-channel to the access/distribution switch, we need to configure as "vPC".7010(config)# interface port-channel 25
7010(config-if)# vpc 25
Hope this helps.
vPC config guide:
http://www.cisco.com/en/US/docs/switches/datacenter/sw/5_x/nx-os/interfaces/configuration/guide/if_vPC.html
- Yogesh
10-12-2010 08:41 AM
So in your example Int Port-channel 10 is your trunk between the 7010's? If so i understand the concept.
10-12-2010 08:54 AM
Yes, Po10 is the port-channel between two Nexus7010s. - Yogesh
10-12-2010 09:06 AM
Thank You
10-12-2010 09:46 PM
You actually need two seperate linke between the two Nexus switches.
One is known as the "vpc peer-link", and carries the actual traffic between the two switches which allows them to present the same "virtual" host for terminating port-channels.
The second link is known as the "peer keepalive" link, and CANNOT be the same physical connection as the vpc peer-link as it needs to be a layer 3 link.
The recommendations also advise you should run the peer keepalive in a seperate VRF to maintain its route.
The relavent parts of my configuration looks like this
vrf context keepalive
vpc domain 1
role priority 1
peer-keepalive destination 10.255.254.2 source 10.255.254.1 vrf keepalive interval 400 timeout 3
peer-gateway
reload restore delay 300
interface Ethernet8/48
description Port for VPC Peer Keep-Alive
no switchport
vrf member keepalive
ip address 10.255.254.1/24
interface port-channel1
description Intra-switch link between Nexus core
switchport mode trunk
vpc peer-link
spanning-tree port type network
mtu 9216
interface Ethernet7/25
description Port one of two port channel group - link to secondary Nexus
switchport mode trunk
mtu 9216
channel-group 1 mode active
interface Ethernet7/26
description Port one of two port channel group - link to secondary Nexus
switchport mode trunk
mtu 9216
channel-group 1 mode active
The other side is similar, with changes only to ports (the keepalive port is in a different slot), IP addresses (the other end of the keepalive link needs a diferent IP address, obviously), and the secondary core switch doesn't need the "role priority" option in the vpc group.
Once this is up and running, a "show vpc brief' gives the following
nexus1# sh vpc brief
Legend:
(*) - local vPC is down, forwarding via vPC peer-link
vPC domain id : 1
Peer status : peer adjacency formed ok
vPC keep-alive status : peer is alive
Configuration consistency status: success
Type-2 consistency status : success
vPC role : primary, operational secondary
Number of vPCs configured : 14
Peer Gateway : Enabled
Dual-active excluded VLANs : -
vPC Peer-link status
---------------------------------------------------------------------
id Port Status Active vlans
-- ---- ------ --------------------------------------------------
1 Po1 up 1-2,20,30-31,40,50,60,70,80,90,110,120,140,150,160
,170,180,190,192,200-201,210-211,221,250,300,556,8
50,999,1601-1602,1610,1620,2000,4063,4065,4068,407
1
*ALL* your VLAN's should be in the peer-link unless you specifically don't want them available to be trunked via VPC.
nexus1# sh vpc peer-keepalive
vPC keep-alive status : peer is alive
--Peer is alive for : (5260233) seconds, (99) msec
--Send status : Success
--Last send at : 2010.10.13 15:40:06 735 ms
--Sent on interface : Eth8/48
--Receive status : Success
--Last receive at : 2010.10.13 15:40:06 736 ms
--Received on interface : Eth8/48
--Last update from peer : (0) seconds, (198) msec
vPC Keep-alive parameters
--Destination : 10.255.254.2
--Keepalive interval : 400 msec
--Keepalive timeout : 3 seconds
--Keepalive hold timeout : 3 seconds
--Keepalive vrf : keepalive
--Keepalive udp port : 3200
--Keepalive tos : 192
nexus1#
Without the functioning peer keepalive your VPC peer-link will not come up, and VPC's won't work. You need to get that right (including the VRF) before you can establish the peer link.
Cheers
10-13-2010 06:36 AM
"peer keepalive" link that is L3 is only for keepalive and it doesnt pass traffic?
All of the network traffic will go over your port-channel 1, and VPC will work assuming your peer keepalive link is working correctly?
10-13-2010 07:36 AM
>> "peer keepalive" link that is L3 is only for keepalive and it doesnt pass traffic?
That's right. It is recommended to have the vPC peer-keepalive link in a dedicated VRF.
>> All of the network traffic will go over your port-channel 1, and VPC will work assuming your peer keepalive link is working correctly?
Yes. All network traffic go through Port-ch 1.
Different failure scenarios:
(1) If the peer-keepalive goes down, peerlink stays up, both N7Ks know that peer-keepalive went down and operations will be normal.
(2) If the peerlink goes down but peer-keepalive is up, then N7Ks know both are active and peerlink went down. At this point, secondary switch suspends its local ports to avoid dual-active condition.
(3) If peerlink as well as peer-keepalive goes down at the same time, then dual-active scenario occurs.
- Yogesh
10-13-2010 07:40 AM
Thanks alot Yogesh!
-Mike
10-13-2010 03:31 PM
Absolutely correct.
The peer keepalive link will NOT pass traffic - that all goes across the peer link conenction - the keepalive is used for state updates and for synchronisation status - but your initial VPC establishment won't come up without it.
So you need a minimum of two ports linking your Nexus 7k's - one 10 gig for your peer link (from memory, peer link is not supported on 1 gig ports no matter how many you bundle, but I could be wrong), and a single one gig port in layer 3 mode for your peer keepalive link.
As shown, I use two x 10 gig ports between my Nexus 7k switches for more intra-switch bandwidth, but that's not strictly necesary, although Cisco's best practice recommends that not only do you use two x 10 gig ports, but that they be on seperate line cards - which isn't an option in my case as I only HAVE one 10 gig line card. :-)
Cheers
10-14-2010 05:07 AM
That is exaclty how i was going to do it too. new VRF for the l3 keepalive link and 2 10gig links inbeteen cores. Unfortunitally we only have 1 10 gb
blade in each core too. But that will change over time.
Thanks for the input.