Temparature - Cisco 6509-E
hello,
The VTT outlet temparature on my switch (Cisco 6509-E). What might be the cause? I often get this issue.
SWITCH>sh environment temperature
  VTT 1 outlet temperature: 25C
  VTT 2 outlet temperature: 34C
  VTT 3 outlet temperature: 40C
  module 1 outlet temperature: 42C
  module 1 inlet temperature: 24C
  module 1 EARL outlet temperature: 31C
  module 1 EARL inlet temperature: 30C
  module 2 outlet temperature: 42C
  module 2 inlet temperature: 26C
  module 2 EARL outlet temperature: 31C
  module 2 EARL inlet temperature: 33C
  module 3 outlet temperature: 42C
  module 3 inlet temperature: 26C
  module 3 EARL outlet temperature: 32C
  module 3 EARL inlet temperature: 34C
  module 4 outlet temperature: 37C
  module 4 inlet temperature: 28C
  module 4 device-1 temperature: 32C
  module 4 device-2 temperature: 36C
  module 5 outlet temperature: 30C
  module 5 inlet temperature: 25C
  module 5 device-1 temperature: 31C
  module 5 device-2 temperature: 32C
  module 5 asic-1 (SSO-1) temp: 25C
  module 5 asic-2 (SSO-1) temp: 25C
  module 5 asic-3 (SSO-1) temp: 25C
  module 5 asic-4 (SSO-1) temp: 25C
  module 5 asic-5 (SSA-1) temp: 25C
  module 5 asic-6 (HYPERION-1) temp: 25C
  module 5 RP outlet temperature: 27C
  module 5 RP inlet temperature: 28C
  module 5 EARL outlet temperature: 33C
  module 5 EARL inlet temperature: 24C
  module 7 outlet temperature: 34C
  module 7 inlet temperature: 24C
  module 7 device-1 temperature: 30C
  module 7 device-2 temperature: 34C
  module 8 outlet temperature: 32C
  module 8 inlet temperature: 24C
  module 8 device-1 temperature: 30C
  module 8 device-2 temperature: 33C
  module 9 outlet temperature: 31C
  module 9 inlet temperature: 26C
  module 9 device-1 temperature: 24C
  module 9 device-2 temperature: 27C
SWITCH>sh environment cooling
fan-tray 1:
  fan-tray 1 type: WS-C6509-E-FAN
  fan-tray 1 mode: restricted-power
  fan-tray 1 fan-fail: OK
chassis per slot cooling capacity: 70 cfm
  module 1 cooling requirement: 70 cfm
  module 2 cooling requirement: 70 cfm
  module 3 cooling requirement: 70 cfm
  module 4 cooling requirement: 35 cfm
  module 5 cooling requirement: 35 cfm
  module 7 cooling requirement: 35 cfm
  module 8 cooling requirement: 35 cfm
  module 9 cooling requirement: 30 cfm
1 REPLY
Re: Temparature - Cisco 6509-E
fan-tray 1:
Hi Deepa,
The current temparature for module 1,2 and 3  are showing 42 'C whch is at warining level, check out the following thisngs and parameters
To view the acceptable temperature and voltage parameters, use the 'show environment alarm thresholds' command. To return the current temperature to normal parameters make sure the device is installed in:
A site with a dry, clean, well-ventilated and air-conditioned area. Make sure   that the air conditioner is working correctly.
A site that maintains an ambient temperature of 32 to 104º F (0 to 40º C).
Install the system in an open rack whenever possible. If installation in an enclosed rack is unavoidable, ensure that the rack has adequate ventilation.
Maintain ambient airflow to ensure normal operation. If the airflow is blocked or restricted, or if the intake air is too warm, an overtemperature condition  can occur.
Allow at least 6 inches (15.24 cm) of clearance around the ventilation openings of the chassis.
Avoid placing the system in an overly congested rack or directly next to another equipment rack. Heat exhaust from other equipment can enter the inlet air vents and cause an overtemperature condition.
Equipment near the bottom of a rack might generate excessive heat that is drawn upward and into the intake ports of the equipment above. The warm air can cause an overtemperature condition in the equipment above.
Ensure that cables from other equipment do not obstruct the airflow through the   chassis or impair access to the power supplies or cards. Route cables away   from field-replaceable components to avoid disconnecting cables unnecessarily   for equipment maintenance or upgrades.
If the module temperature sensor does not recover by itself then plan a downtime and power cycle the module.
Hope this helps out your query !!
If helpful do rate the valaubale post.
Ganesh.H
2883
