07-02-2013 12:35 AM - edited 03-01-2019 07:21 AM
Hi ,
We have two nexus switches working as the core of our network , we are facing a high temperature on both of them on the N7K-M224XP-23L module slot 3 . Eventhough we have the same module on slot 6 & 7 but we dont have this warning on them , the only different is that we are using the module on slot 3 for fiber connectivity but we are not using the modules on slot 6 & 7 for any thing yet .The cooling is fine in the data center and only this type of module on this slot is having a high temperature warnings . Please did any one face this problem before ?
Temperature:
--------------------------------------------------------------------
Module Sensor MajorThresh MinorThres CurTemp Status
(Celsius) (Celsius) (Celsius)
--------------------------------------------------------------------
3 MAC0Sn0(s2) 115 105 44 Ok
3 MAC0Sn1(s3) 115 105 45 Ok
3 MAC0-Buf0(s4) 115 105 53 Ok
3 MAC0-Buf1(s5) 115 105 62 Ok
3 MAC0-Buf2(s6) 115 105 70 Ok
3 MAC0-Buf3(s7) 115 105 69 Ok
3 MAC1Sn0(s8) 115 105 36 Ok
3 MAC1Sn1(s9) 115 105 39 Ok
3 MAC1-Buf0(s10) 115 105 40 Ok
3 MAC1-Buf1(s11) 115 105 57 Ok
3 MAC1-Buf2(s12) 115 105 47 Ok
3 MAC1-Buf3(s13) 115 105 40 Ok
3 Fwd0Sn0(s14) 115 105 103 Ok
3 Fwd0Sn1(s15) 115 105 103 Ok
3 Fwd1Sn0(s16) 115 105 84 Ok
3 Fwd1Sn1(s17) 115 105 84 Ok
3 Fwd2Sn0(s18) 115 105 94 Ok
3 Fwd2Sn1(s19) 115 105 94 Ok
3 Fwd3Sn0(s20) 115 105 61 Ok
3 Fwd3Sn1(s21) 115 105 61 Ok
3 QEng0Sn0(s22) 115 105 99 Ok
3 QEng0Sn1(s23) 115 105 99 Ok
3 QEng1Sn0(s24) 115 105 91 Ok
3 QEng1Sn1(s25) 115 105 91 Ok
3 QEng2Sn0(s26) 115 105 83 Ok
3 QEng2Sn1(s27) 115 105 83 Ok
3 QEng3Sn0(s28) 115 105 69 Ok
3 QEng3Sn1(s29) 115 105 69 Ok
3 Crossbar(s30) 115 105 52 Ok
Mod Ports Module-Type Model Status
--- ----- ----------------------------------- ------------------ ----------
1 0 Supervisor module-2 N7K-SUP2 active *
2 0 Supervisor module-2 N7K-SUP2 ha-standby
3 24 10 Gbps Ethernet Module N7K-M224XP-23L ok
4 48 10/100/1000 Mbps Ethernet XL Module N7K-M148GT-11L ok
5 48 10/100/1000 Mbps Ethernet XL Module N7K-M148GT-11L ok
6 24 10 Gbps Ethernet Module N7K-M224XP-23L ok
7 24 10 Gbps Ethernet Module N7K-M224XP-23L ok
Hardware
cisco Nexus7000 C7009 (9 Slot) Chassis ("Supervisor module-2")
Intel(R) Xeon(R) CPU with 12225160 kB of memory.
Processor Board ID JAF1646ALCH
Software
BIOS: version 2.8.0
kickstart: version 6.1(2)
system: version 6.1(2)
BIOS compile time: 06/09/12
kickstart image file is: bootflash:///n7000-s2-kickstart.6.1.2.bin
kickstart compile time: 12/25/2020 12:00:00 [10/26/2012 07:38:27]
system image file is: bootflash:///n7000-s2-dk9.6.1.2.bin
system compile time: 9/7/2012 13:00:00 [10/26/2012 08:44:25]
Solved! Go to Solution.
07-02-2013 04:26 AM
I would not take temperature within your data centre as the only measure.
It depends on what other switches and devices are next to your Nexus racks and how the air flow works.
Air flow on the N7K9s are side-to-side:
The same guide also makes recommendations as to how the switches should be mounted within the rack in order to allow for sufficient clearance.
I have seen a data centre where there were a number of N7Ks in the same row. So in effect hot air was being blown out of one switch and being sucked into the next.
Don't forget to rate all posts that are helpful.
07-03-2013 01:32 AM
Moahmmed,
Kindly check if there is any airblocking the module which is seeing high temperature issue.....
We have seen that airflow getting block to specific module i nthe data center the way they have been placed or someone just put somthing in front of it whic avoid the airflow.
Regards
Inayath
07-02-2013 12:41 AM
I forgot to post also that we have changed these modules with new ones but still the problem is appearing on slot 3 !!
07-02-2013 04:26 AM
I would not take temperature within your data centre as the only measure.
It depends on what other switches and devices are next to your Nexus racks and how the air flow works.
Air flow on the N7K9s are side-to-side:
The same guide also makes recommendations as to how the switches should be mounted within the rack in order to allow for sufficient clearance.
I have seen a data centre where there were a number of N7Ks in the same row. So in effect hot air was being blown out of one switch and being sucked into the next.
Don't forget to rate all posts that are helpful.
07-02-2013 09:16 PM
I agree with your recommendations but the strange thing is why it is happening only on slot3 and it is not showing on the rest of the slots !! If you see for example the temperature in slot 4 it seems fine
SWI700902# sh environment temperature module 4
Temperature:
--------------------------------------------------------------------
Module Sensor MajorThresh MinorThres CurTemp Status
(Celsius) (Celsius) (Celsius)
--------------------------------------------------------------------
4 CPU (s4) 115 95 47 Ok
4 Crossbar(s5) 105 95 49 Ok
4 CTSdev4 (s9) 115 105 61 Ok
4 CTSdev5 (s10) 115 105 60 Ok
4 CTSdev7 (s12) 115 105 57 Ok
4 CTSdev9 (s14) 115 105 54 Ok
4 CTSdev10(s15) 115 105 54 Ok
4 CTSdev11(s16) 115 105 50 Ok
4 CTSdev12(s17) 115 105 50 Ok
4 QEng1Sn1(s18) 115 105 55 Ok
4 QEng1Sn2(s19) 115 105 54 Ok
4 QEng1Sn3(s20) 115 105 52 Ok
4 QEng1Sn4(s21) 115 105 52 Ok
4 L2Lookup(s22) 120 110 53 Ok
4 L3Lookup(s23) 120 110 58 Ok
07-03-2013 01:32 AM
Moahmmed,
Kindly check if there is any airblocking the module which is seeing high temperature issue.....
We have seen that airflow getting block to specific module i nthe data center the way they have been placed or someone just put somthing in front of it whic avoid the airflow.
Regards
Inayath
07-03-2013 02:48 AM
Actually our nexus switches are mounted in server racks which means that the switch side and the server side are very close and according to cisco recommendations i think we need to keep some space in this area . Do you agree with me ?
07-03-2013 02:51 AM
There you go. Yes totally agree with you.
HTH
REgards
Inayath
*Plz rate all usefull posts /.
07-03-2013 03:22 AM
Have a look at the Cisco power calculator for the N7K at http://tools.cisco.com/cpc/
You will find that the N7K-M224XP-23L generates twice the heat and consumes twice the power of the N7K-M148GT-11L.
This will help to explain why this blade is so hot in comparison to the others.