cancel
Showing results for 
Search instead for 
Did you mean: 
cancel
953
Views
0
Helpful
1
Replies

Port-channel issue over Ciena DWDM

Antho_Balitrand
Level 1
Level 1

Hi all, 

 

I'm currently working on an issue encountered on a DC. 

We currently use 2 3750 stacks (1 in each DC), connected with a Po. 

We use dark fiber between each DC, so we have a Ciena DWDM transponder on each side. 

The problem is that, if we have an issue on the inter-DC fiber, the Ciena interface on the 3750 side is still up. Using LACP on the Po, the issue can be detected in about 3 X 30 sec = 90 sec. 

Before the issue is detected by LACP, the impacted port-channel interface is still used by the Po, which can cause big issues. 

I thought use an EEM applet in order to monitor the CDP neighbor on each interface, and exclude the interface from the Po till the CDP neighbor is down, but the CDP timers are even bigger (180 sec hold-time). 

Is there any way to address this problem, other than UDLD ? 

 

In our others DC, we have two NX7K on each side, and we are able to use LACP with fast-rate, but this is not available on 3750... 

 

Thank you very much ! 

1 Reply 1

Phil Bartlett
Level 1
Level 1

It maybe a problem with Ciena. We have some 10G port channels over diverse fibers using Sorrento Gigamux DWDM equipment.its operates in a totally transparent mode.

If there is an issue with the inter DC fiber or the equipment at the other  then the client side switch handles it as it was directly directly connected.

i suggest looking at the Ciena transponder