10-07-2010 08:10 AM - edited 03-09-2019 11:12 PM
I have configured 802.1x on a fas0/3 and works fine.
I'm testing to configure a restricted VLAN on that port and it does not work.
This is the configuration:
interface FastEthernet0/3
switchport access vlan 11
switchport mode access
dot1x pae authenticator
dot1x port-control auto
dot1x auth-fail vlan 30
dot1x auth-fail max-attempts 2
When PC connected to Fas0/3 failed the authentication two times it should switch to VLAN 30 but it's not happening (port fas0/3 remains in VLAN 11 in up/down state)
SHOW VLAN:
11 VLAN0011 active Fa0/2, Fa0/3, Fa0/4
30 RESTRICTED active
sw1#sh dot1x interface fas 0/3
Dot1x Info for FastEthernet0/3
PAE = AUTHENTICATOR
PortControl = AUTO
ControlDirection = Both
HostMode = SINGLE_HOST
ReAuthentication = Disabled
QuietPeriod = 60
ServerTimeout = 30
SuppTimeout = 30
ReAuthPeriod = 3600 (Locally configured)
ReAuthMax = 2
MaxReq = 2
TxPeriod = 30
RateLimitPeriod = 0
Auth-Fail-Vlan = 30
Auth-Fail-Max-attempts = 2
This is a 2960 running c2960-lanbase-mz.122-35.SE5, what I'm missing?
Federico.
Solved! Go to Solution.
10-07-2010 12:57 PM
Ferderico,
How are you testing the Auth-Fail VLAN? If you are testing with a bad password and using PEAP this is considerred a retriable error which may not cause an Access-Reject from the RADIUS server, instead the password can be retried without first tearing down the TLS tunnel via an Access-Reject. As configured it would take 3 Access-Rejects from the RADIUS server to be placed into the auth-fail VLAN. If I remember correctly a bad username is also retriable.
If you are using ACS 5 you can turn down the number of PEAP retries to 1 in which case you would need to fail login 6 times with a bad password to hit the auth-fail VLAN.
--Jesse
10-07-2010 12:57 PM
Ferderico,
--Jesse
10-07-2010 01:18 PM
Jesse,
Thank you very much.
I changed the
to
dot1x auth-fail max-attempts 1
and now it works!
The weird thing is that it still prompts me twice for authentication, gives me auth fail error, but I check the switch and port F0/3 is now on VLAN 30 (as expected).
If I change it back to dot1x auth-fail max-attempts 2, it prompts me twice for authentication, auth fails, but the switch will keep F0/3 on VLAN 11.
It is working, however it's strange isn't it?
Yes.. I am making the test using bad user/pass.
Federico.
10-07-2010 01:23 PM
Great,
This is the retriable error I was mentioning. The password can be retried inside the TLS tunnel without an Access-Reject being sent fromt the RADIUS server. So while you are failing on the supplicant side twice the switch only sees this as a single failure.
--Jesse
10-07-2010 01:39 PM
Great stuff!
Thank you Jesse.
Federico.