10-13-2010 09:23 AM
Hi, I have a MDS9506 v 3.3(1c) that is denying power to the 4th module. I did a show environment power cmd and got the following:
Each of the 2 modules has 1019.34 power (watts) but it is set in redundant mode. The Power (Amp @42V) is 24.27 for each module.
Here is what I have for each module
Mod Power Requested (Watts) Power Requested (Amp @42V) Power Allocated (Watts) Power Allocated (Amp @42v)
1 190.68 4.54 190.68 4.54
2 190.68 4.54 190.68 4.54
3 147.00 3.50 147.00 3.50
4 147.00 3.50 0.00 0.00
5 126.00 3.00 126.00 3.00
6 126.00 3.00 126.00 3.00
Power Usage Summary:
Power Supply redundancy mode: redundant
Total Power Capacity 1019.34 W
Power reserved for Supervisor(s) 252.00 W
Power reserved for Fan Modules 126.00 W
Power currently used by Modules 528.36 W
Total Power Available 112.98 W
Since it takes 147 Watts to power up the 4th module, I can't because I have 112.98 W available. Are there any other solutions other than changing the redundancy mode? Is the MDS switch only capable of 1019.34 power capacity?
10-22-2010 04:42 AM
Hi Raymond,
could you post the full output of 'show environment power' please?
thanks,
Kris
10-22-2010 05:07 AM
Hi Raymond,
as per the specs found on http://www.cisco.com/en/US/docs/storage/san_switches/mds9000/hw/9500series/installation/guide/techspec.html#wp1010749
Output capacity | 1050 W maximum (at input of 100 to 120 VAC). |
This means you have a theoretical 30W more than the 1019.34W you are getting. Still this isn't enough.
So you have 2 options:
* Connect it to a 200-240VAC outlet
* Run the power supplies in combined mode