Fibre Patch Lead Choice with FCIP

p-matthewson
Level 1
Level 1

I have a solution to implement and connect 2 MDS 9509s. Distances involved in fibre runs are sub 150m. Is there any benefit in me using 50/125 instead of 62.5/125 within these distances. The existing infrastructure would dictate that we run with 62.5/125. We may want to run with up to 10Gb over the Fibre, but as this will be aggregated through port channels I don't see the fibre choice as being an issue so long as we don't interface 62.5 with 50 directly... Can anyone confirm that this is ok?

Thanks

Paul

1 Accepted Solution

Accepted Solutions

pciaccio
Level 4
Level 4

Theoretically the 50um fiber is the better and is primarily used for longer lengths of 500+meters. You can use either type for your application. It will work fine. The only benfit the 50um offers is a smaller diameter that allows for less dispersion loss and goes a longer distance. Yes, I would stay with one type of fibr. Do not mix and match...Please rate..Good Luck...

View solution in original post

2 Replies 2

pciaccio
Level 4
Level 4

Theoretically the 50um fiber is the better and is primarily used for longer lengths of 500+meters. You can use either type for your application. It will work fine. The only benfit the 50um offers is a smaller diameter that allows for less dispersion loss and goes a longer distance. Yes, I would stay with one type of fibr. Do not mix and match...Please rate..Good Luck...

Thanks for your response - I will go with 50um in the solution. Cheers, Paul