Fault error Code on UCS 6140 Cluster
Hi all,
I'm running a UCS 6140 Cluster with 1.4(3q) UCSM Version.
I've a Critical Fault.
The fault code is F999590. This fault code have no correspondance in the "Cisco UCS Faults and Error Messages Reference" doc.
By searching with fault description, i found:
fsmFailSwFcSanBorderDeploy
Fault Code:F999789
Message
[FSM:FAILED]: sam:dme:SwFcSanBorderDeploy
Explanation
None set.
Recommended Action
Copy the message exactly as it appears on the console or in the system log. Research and attempt to
resolve the issue using the tools and utilities provided at http://www.cisco.com/tac. Also refer to the
Release Notes for Cisco UCS Manager and the Cisco UCS Troubleshooting Guide. If you cannot resolve
the issue, execute the show tech-support command and contact Cisco Technical Support.
Fault Details
Severity: critical
Cause: fsm-failed
mibFaultCode: 999789
mibFaultName: fsmFailSwFcSanBorderDeploy
moClass: sw:FcSanBorder
Type: fsm
How can i investigate more ?
Thanks a lot.
Florent
1 ACCEPTED SOLUTION
Hello Florent,
We need more logs and so I would suggest you to open a TAC service request to further investigate the following fault message for FI B FC links.
Code: F999590
Description: [FSM:FAILED]: Uplink fc port configuration on B(FSM:sam:dme:SwFcSanBorderDeploy)
Affected Object: sys/switch-B/border-fc
Creation Time: 2011-10-10T09:56:12.953
Following information would also help the investigation
Were there any VSAN mismatch between FI and upstream FC switch ?
Is FI running End host or switching FC mode ?
Is FC trunking enabled on these links ?
If the FC ports are up and active, it could be also where the fault condition got cleared but fault message stayed on.
Padma
Hello Florent,
Are you aware of any changes that triggered this fault ?
Can you please provide the output of " show vsan usage " from nxos cli mode ?
Padma
hi Padma,
Thanks you for responding.
The fault is appeared during implementation.
Below, you will find outputs.
fi1-A(nxos)# sh vsan usage
2 vsan configured
configured vsans:1,100
vsans available for configuration:2-99,101-4078,4080-4093
fi1-B(nxos)# sh vsan usage
2 vsan configured
configured vsans:1,200
vsans available for configuration:2-199,201-4078,4080-4093
no issue for me
Florent
Re: Fault error Code on UCS 6140 Cluster
I found a difference in VSAN configuration.
Fabric A:
Port Type: aggregation
Transport type: FC
Port Channel Admin Speed is "Auto"
Operational Speed (Gbps): 32
Fabric B:
Transport type: FC
Port Channel Admin Speed is "8 Gbps"
is this could be the problem ?
If i change, port channel admin speed, what are the consequences ?
Florent
Hello Florent,
Were you trying to implement FC port channel ?
Can you please share related fault messages for this event from " show fault detail " output ?
scope fc-uplink
show interface
connect nxos ( from both FI )
show san-port-channel summary
Is it for both FIs ?
Padma
Hi all,
Here, you will find console output:
fi1-A# sh fault detail
Severity: Critical
Code: F999590
Last Transition Time: 2011-10-10T09:56:12.953
Status: None
Name: Fsm Deploy Fsm Fail
Cause: Fsm Failed
Type: Fsm
Acknowledged: Yes
Occurrences: 1
Original Severity: Critical
Previous Severity: Critical
Highest Severity: Critical
fi1-A /fc-uplink # sh int
Interface:
Fabric ID  Slot  Port  Admin State  Oper State    State Reason
A              2     5 Enabled      Sfp Not Present
                                                  SFP not present
A              2     6 Enabled      Sfp Not Present
                                                  SFP not present
B              2     5 Enabled      Sfp Not Present
                                                  SFP not present
B              2     6 Enabled      Sfp Not Present
                                                  SFP not present
fi1-A(nxos)# sh san-port-channel summary
U-Up D-Down B-Hot-standby S-Suspended I-Individual link
summary header
Group  Port-      Type     Protocol  Member Ports
       Channel
100    Spo100               FC      PCP      (U)  FC       fc2/1(P)  fc2/2(P)  fc2/3(P)  fc2/4(P)
fi1-A(nxos)#
fi1-B(nxos)# sh san-port-channel summary
summary header
       Channel
200    Spo200               FC      PCP      (U)  FC       fc2/1(P)  fc2/2(P)  fc2/3(P) fc2/4(P)
fi1-B(nxos)#
Thanks for helping
Florent
Hello Florent,
Code: F999590
Padma
Hello Padma and thanks for helping,
I'll open a TAC request on new week.
Florent
Hi all,
Good news, the fault has been cleared when i disable unused port.
So , i don't need to open a TAC request for the moment.
Thnaks for helping.
Florent