Power state is redundancy failed?

Hello Experts!

I have a UCS-system with two 6120XP and a single 5108 chassi. The chassi have two 2500W power supplies that feeds power to three B200-M1 half width servers. The power supplies are located in slot 1 and 3 as per the hardware installation guide (http://www.cisco.com/en/US/docs/unified_computing/ucs/hw/chassis/install/FRU.html#wp1028655) and the system is configured for N+1 redundancy. The power supplies are working perfectly and their status i OK/Operable.

So to the problem, I have a what appears to be a stale major alarm "Power state on chassis 1 is redundancy failed" that I cannot get rid of. The Last Transition was over a month and a half ago. As this alarm appears to be a old and stale alarm and I have tried to clear the log via UCS Manager but no joy, so how to I forcibly remove it?

Have any ideas?

Regards,

Fredrik

9 REPLIES
Community Member

Re: Power state is redundancy failed?

Hi there,

I'm experiencing exactly the same problem in a B-200M1 with UCSM 1.4

Anyone has a solution for this not really important, but quite anoying problem?

Thanks a lot,

Re: Power state is redundancy failed?

With only 2 power supplies in the chassis the power redundancy fault will always be there. The reason is because UCSM doesn't take into account the actual power the chassis needs to power the blades, it is assuming a full chassis.

To clear the fault you have to have at least 3 power supplies and the chassis power policy has to be set to N+1. If you have 4 power supplies you can set it to either N+1 or Grid if you have 2 PSU going to one PDU and then the other 2 going to a different PDU.

With 4 blades or less you could probably run on 1 power supply so you do have redundancy you just can't clear the fault. Power supplies are cheap though, I always recommend 4 PSUs.

Cisco Employee

Re: Power state is redundancy failed?

Jeremy is right except with there has been a small change since we introduced the B230.  We do check the blades to see what blades are populated to determine the power requirements. However you will never be able to get Redundancy with 2 power supplies only 3.

The B230 can drive the allocated power per slot to 600W. This will exced the 3 power supply requirements for Redundancy. Thus if we see a B230 in a slot on the chassis you need 4 power supplies for Redundancy. This is called High Density Mode. The chances of a blade ever driving 600W is small but it since it is possible we have to allocate for that in the redundancy modes.

louis

Community Member

Re: Power state is redundancy failed?

Sorry, I missed the "2 power supply" part. My problem is not with 2 but with 3 PS. I do have 3 PS's in UCS, and still warns me about this redundancy fail problem. I only have 4 B-200 M1 (with 24 GB each) and 1 B-250 M1 with 160 GB.

Any inputs will be appreciated,

Thanks

Re: Power state is redundancy failed?

Do you have your Power Policy set to n+1?

Community Member

Re: Power state is redundancy failed?

Yes I do. Any more clues?

Thanks,

Re: Power state is redundancy failed?

Try re-acknowledging your chassis, this will disrupt I/O for a bit though.

Community Member

Re: Power state is redundancy failed?

Jeremy, I just did it, but the fault is still there

Cisco Employee

Re: Power state is redundancy failed?

It's a bug. I just checked and it's a known bug and will be fixed in an upcoming maintenance release.

**Update***

Here is the bug-id CSCtl92106