what diffirent between vertical 6509 and horizontal 6509?
i can't find from web site.
thank you very much?
Solved! Go to Solution.
04-28-2006 09:00 PM
Vertical 6509 are NEB compliant and they are called 6509-NEB. 6509 Horizontal are not NEB compliant.
This switch complies with Network Equipment Building Systems (NEBS) (Zone 4 per GR-63-Core) in the following areas:
Earthquake environment and criteria
Office vibration and criteria
Transportation vibration and criteria
Shock
Operational5 G 30 ms, half-sine (IEC 68-2-27)
Non-operational20 G, 7.5 ms, trapezoidal
Vibration
Operational3 Hz to 500 Hz,
Power Spectral Density (PSD)-0.0005 G2/Hz at 10 Hz and 200 Hz. 5 dB/octave roll off at each end. 0.5 hours per axis (1.12 Grms).
The Catalyst 6509-NEB switch chassis is designed to install in standard 19-inch equipment racks that meet ANSI/EIA 310-D, IEC 60297, and ETS 300-119 standards.
The 6509 Horizontal is not NEB compliant and therefore does not adhere to the standards above. Other than that they both do the same funtionality.
http://www.cisco.com/univercd/cc/td/doc/product/lan/cat6000/6000hw/6500_ins/01over.htm#wp1079450
Please rate helpful posts.
04-28-2006 09:00 PM
Vertical 6509 are NEB compliant and they are called 6509-NEB. 6509 Horizontal are not NEB compliant.
This switch complies with Network Equipment Building Systems (NEBS) (Zone 4 per GR-63-Core) in the following areas:
Earthquake environment and criteria
Office vibration and criteria
Transportation vibration and criteria
Shock
Operational5 G 30 ms, half-sine (IEC 68-2-27)
Non-operational20 G, 7.5 ms, trapezoidal
Vibration
Operational3 Hz to 500 Hz,
Power Spectral Density (PSD)-0.0005 G2/Hz at 10 Hz and 200 Hz. 5 dB/octave roll off at each end. 0.5 hours per axis (1.12 Grms).
The Catalyst 6509-NEB switch chassis is designed to install in standard 19-inch equipment racks that meet ANSI/EIA 310-D, IEC 60297, and ETS 300-119 standards.
The 6509 Horizontal is not NEB compliant and therefore does not adhere to the standards above. Other than that they both do the same funtionality.
http://www.cisco.com/univercd/cc/td/doc/product/lan/cat6000/6000hw/6500_ins/01over.htm#wp1079450
Please rate helpful posts.